I suspect that CPF diverged after passing the nose point. Can you please send 
us the case (offline) and the commands you used for running the continuation 
power flow. As I mentioned before, the voltages and the load scaling parameter 
lambda at each continuation step are stored in the ‘cpf’ field of the 
outresults struct where outresults = runcpf(mpcbase,mpctarget). The easiest way 
would be to use the values stored in outresults.cpf for your voltage versus 
reactive power load plot.

For example, to plot the voltage magnitude versus the reactive power load at 
bus 5, I would do

plot(mpcbase.bus(5,QD)*(1+outresults.cpf.lam_c),abs(outresults.cpf.V_c(5,:)))

Shri

From: Hiranya Seneviratne 
<hiranya.seneviratn...@gmail.com<mailto:hiranya.seneviratn...@gmail.com>>
Reply-To: MATPOWER discussion forum 
<matpowe...@list.cornell.edu<mailto:matpowe...@list.cornell.edu>>
Date: Monday, May 25, 2015 at 2:54 AM
To: MATPOWER discussion forum 
<matpowe...@list.cornell.edu<mailto:matpowe...@list.cornell.edu>>
Subject: Re: increasing Reactive power load by a load factor

Dear Shri,

Thank you for your email. I tried this method, however it says that it does not 
converge.
I am also looking to plot the voltage against the reactive power load. Is it 
possible to do this using the continuation power flow method?
Thank you
Hiranya
On 24 May 2015, at 23:28, Abhyankar, Shrirang G. 
<abhy...@anl.gov<mailto:abhy...@anl.gov>> wrote:

Hi,
  You might want to try MATPOWER’s continuation power flow feature instead of 
rolling out your own load increment loop. The reason is that as you increase 
the load the Jacobian matrix conditioning worsens and running a simple power 
flow may yield a divergent solution. For your case, I would run the 
continuation power flow as follows:

mpcbase = loadcase(‘case95’);
mpctarget = mpcbase;
mpctarget.bus(5,[PD,QD]) = mpctarget.bus(5,[PD,QD])*3.0;

outresults = runcpf(mpcbase,mpctarget);

The results of the continuation power flow can be found in the cpf field of the 
outresults struct.

You can further customize continuation power flow based on your needs (for e.g. 
vary the step-size, add custom monitors, stop at a given loading, and others). 
Read the MATPOWER manual to know more.

Shri


From: Hiranya Seneviratne 
<hiranya.seneviratn...@gmail.com<mailto:hiranya.seneviratn...@gmail.com>>
Reply-To: MATPOWER discussion forum 
<matpowe...@list.cornell.edu<mailto:matpowe...@list.cornell.edu>>
Date: Saturday, May 23, 2015 at 7:57 AM
To: MATPOWER discussion forum 
<matpowe...@list.cornell.edu<mailto:matpowe...@list.cornell.edu>>
Subject: Fwd: increasing Reactive power load by a load factor



Dear Ray,

I am trying to implement a code in matpower, that increases the reactive power 
load by a factor and then see what happens to the voltage.
I have written this code, however the value of y and q don’t seem to change 
appropriately. will you be please able to let me know how i can implement this?



clear all
close all
define_constants;
results = loadcase('case95');

for i = 1:10
    define_constants;

  y = results.bus(5,[PD QD]);
  results.bus(5,[PD QD]) = y + 0.2*y;

  x = runpf(results);

v(i) = x.bus(5,VM)
q(i) = x.bus(5,QD)
p(i) = x.bus(5,PD)




end