Sorry, I think I made a mistake in my interpretation of what R1-2 means
when CZ=3.  I think it is just the losses in the actual short-circuit test,
in which the applied voltage is very low, certainly NOT the nominal
voltage. The voltage is applied until one gets the nominal current, I=1 in
pu.  Then the calculation of R in the Siemens paper I cited is correct.

The corrected code would be then:

   R(cz3) = 1.0e-6 * ( R(cz3) ./ trans2(cz3,23) );
   X(cz3) = sqrt(X(cz3).^2 - R(cz3).^2);
   % now change to pu of system units (also with a possible correction
due to nominal bus voltages)
   R(cz3) = R(cz3) .* Zb(cz3) ./ Zbs(fbus(cz3));
   X(cz3) = X(cz3) .* Zb(cz3) ./ Zbs(fbus(cz3));

(and similarly for R,X of 3-winding transformers; note also that line 0107
has to stay for cz2 transformers).


-- 
Jose L. Marin
Gridquant España SL
Grupo AIA



On Thu, Oct 22, 2015 at 2:52 PM, Jose Luis Marin <mari...@gridquant.com>
wrote:

> Hello Ray,
>
>
> I think I may have found a bug in *psse2mpc*, which concerns the
> calculation of R,X for transformers when these are specified with *"Impedance
> Code" CZ=3*.  The PSS/E docs decribing the RAW format specify that, when
> CZ=3, the values in the file are:
>
>    - R1-2 is the transformer load loss in watts (to be precise:
>    short-circuit test three-phase full-load winding copper losses, in Watts)
>    - X1-2 is impedance magnitude in pu, on a specified base MVA
>    (SBASE1-2) and winding base voltage (NOMV1)
>
> The conversion code is in lines L0107-L0108 for 2W transformers and
> L0180-L0185 for 3W transformers, in module psse_convert_xfmr
> <http://www.pserc.cornell.edu//matpower/docs/ref/matpower5.1/psse_convert_xfmr.html>
> .
>
> By my account, this is how the conversion should be done, conceptually
> (see if you agree):
>
>    - The value X1-2 given in the file is actually the modulus of Z, i.e.
>    the complex impedance of the "copper" part of the transformer. Use this to
>    obtain the modulus of the intensity I in the short-circuit test (using
>    V=NOMV1, i.e 1 in pu), and then from P=I^2 R one can obtain the per-unit
>    resistance. The value P (in pu) is just the value R1-2 divided by SBASE1-2
>    * 1.0e+6.
>    - Now that we've got R in pu, and we know |Z|, calculate X = sqrt (
>    |Z|^2 - R^2).
>    - Up to here all quantities are pu on SBASE1-2 and NOMV1.  Change to
>    the pu of the system base and the bus terminals base voltages (these may be
>    different than the transformers' sometimes).  This last bit was correctly
>    done in the code.
>
>
> But this is how it appears in the code now:
>
> 0107     X(cz23) = X(cz23) .* Zb(cz23) ./ Zbs(fbus(cz23));
> 0108     R(cz3)  = trans2(cz3,25).^2 ./ trans2(cz3,21) ./ Zbs(fbus(cz3));
>
>
> The correction, if my conversion procedure above is correct, would be as
> follows (showing the code only for 2-winding cz3 transformers):
>
>    R(cz3) = 1.0e-6 * ( R(cz3) ./ trans2(cz3,23) ) .* X(cz3).^2;
>    X(cz3) = sqrt(X(cz3).^2 - R(cz3).^2);
>    % now change to pu of system units (also with a possible correction due to 
> nominal bus voltages)
>    R(cz3) = R(cz3) .* Zb(cz3) ./ Zbs(fbus(cz3));
>    X(cz3) = X(cz3) .* Zb(cz3) ./ Zbs(fbus(cz3));
>
> (and similarly for R,X of 3-winding transformers; note also that line 0107
> has to stay for cz2 transformers).
>
> Now, keep in mind that there's a document by Siemens here
> <http://w3.usa.siemens.com/datapool/us/SmartGrid/docs/pti/2009July/PDFs/Modeling_of_two_winding_voltage_regulating_transformers.pdf>
> in which they work out the math of this conversion, but I think they get it
> wrong for R, because they are forgetting the factor |Z|^2.  Unfortunately,
> I don't have PSS/E to test what the program really does internally, but my
> take is that if R1-2 and X1-2 are what the specs say they are, then the
> formulas I gave here are the correct ones.
>
>
> --
> Jose L. Marin
> Gridquant España SL
> Grupo AIA
>
> <http://www.gridquant.com/>
>