It is true that when a lower generation limit is binding, as in this example, 
the LMP at the bus will be lower than the generator’s marginal cost (or offer 
in a market context). So, in a market you can’t get away with paying such a 
generator only the LMP, you typically also pay them an “uplift” payment equal 
to the shadow price on the lower generation limit in order to make them whole 
financially.

     Ray


> On Nov 19, 2015, at 1:19 PM, Victor Hugo Hinojosa M. <victor.hinoj...@usm.cl> 
> wrote:
> 
> Thank you so much for the information Prof. Zimmerman.
> I’d like your explanation about the simulation for the 6-bus system (Wood & 
> Wollemberg). When I run a DCOPF with the original case (rundcopf(case6ww)), 
> the LMP shown for Matpower are the same (11.899 $/MWh) for all buses because 
> there isn’t congestion in the transmission lines. Despite of the fact that 
> the Lagrange multiplier for generator 1 is active (0.303 $/MWh), the LMP are 
> the same. In my opinion, the LPM from bus 1 should be 12.202 $/MWh.
> I’ll wait for your comments.
> Regards,
> Vh
>  
>  
> MATPOWER Version 5.1, 20-Mar-2015 -- DC Optimal Power Flow
> Gurobi Version 6.0.4 -- automatic QP solver
>  
> Converged in 0.16 seconds
> Objective Function Value = 3046.41 $/hr
> ================================================================================
> |     System Summary                                                          
>  |
> ================================================================================
>  
> How many?                How much?              P (MW)            Q (MVAr)
> ---------------------    -------------------  -------------  -----------------
> Buses              6     Total Gen Capacity     530.0           0.0 to 0.0
> Generators         3     On-line Capacity       530.0           0.0 to 0.0
> Committed Gens     3     Generation (actual)    210.0               0.0
> Loads              3     Load                   210.0               0.0
>   Fixed            3       Fixed                210.0               0.0
>   Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
> Shunts             0     Shunt (inj)             -0.0               0.0
> Branches          11     Losses (I^2 * Z)         0.00              0.00
> Transformers       0     Branch Charging (inj)     -                0.0
> Inter-ties         0     Total Inter-tie Flow     0.0               0.0
> Areas              1
>  
>                           Minimum                      Maximum
>                  -------------------------  --------------------------------
> Voltage Magnitude   1.000 p.u. @ bus 1          1.000 p.u. @ bus 1  
> Voltage Angle      -3.67 deg   @ bus 5          0.00 deg   @ bus 1  
> Lambda P           11.90 $/MWh @ bus 3         11.90 $/MWh @ bus 4  
> Lambda Q            0.00 $/MWh @ bus 1          0.00 $/MWh @ bus 1  
>  
> ================================================================================
> |     Bus Data                                                                
>  |
> ================================================================================
> Bus      Voltage          Generation             Load          
> Lambda($/MVA-hr)
>   #   Mag(pu) Ang(deg)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)     P        Q 
>  
> ----- ------- --------  --------  --------  --------  --------  -------  
> -------
>     1  1.000    0.000*    50.00      0.00       -         -      11.899     -
>     2  1.000   -0.299     88.07      0.00       -         -      11.899     -
>     3  1.000   -0.278     71.93      0.00       -         -      11.899     -
>     4  1.000   -2.986       -         -       70.00      0.00    11.899     -
>     5  1.000   -3.666       -         -       70.00      0.00    11.899     -
>     6  1.000   -3.087       -         -       70.00      0.00    11.899     -
>                         --------  --------  --------  --------
>                Total:    210.00      0.00    210.00      0.00
>  
> ================================================================================
> |     Branch Data                                                             
>  |
> ================================================================================
> Brnch   From   To    From Bus Injection   To Bus Injection     Loss (I^2 * Z) 
>   #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q 
> (MVAr)
> -----  -----  -----  --------  --------  --------  --------  --------  
> --------
>    1      1      2      2.61      0.00     -2.61      0.00     0.000      0.00
>    2      1      4     26.06      0.00    -26.06      0.00     0.000      0.00
>    3      1      5     21.33      0.00    -21.33      0.00     0.000      0.00
>    4      2      3     -0.15      0.00      0.15      0.00     0.000      0.00
>    5      2      4     46.91      0.00    -46.91      0.00     0.000      0.00
>    6      2      5     19.59      0.00    -19.59      0.00     0.000      0.00
>    7      2      6     24.33      0.00    -24.33      0.00     0.000      0.00
>    8      3      5     22.75      0.00    -22.75      0.00     0.000      0.00
>    9      3      6     49.03      0.00    -49.03      0.00     0.000      0.00
>   10      4      5      2.97      0.00     -2.97      0.00     0.000      0.00
>   11      5      6     -3.37      0.00      3.37      0.00     0.000      0.00
>                                                              --------  
> --------
>                                                     Total:     0.000      0.00
>  
> ================================================================================
> |     Generation Constraints                                                  
>  |
> ================================================================================
> Gen   Bus                  Active Power Limits
>   #     #     Pmin mu     Pmin       Pg       Pmax    Pmax mu
> ----  -----   -------   --------  --------  --------  -------
>    1     1      0.303     50.00     50.00    200.00      -  
>  
> De: bounce-119913926-12657...@list.cornell.edu 
> [mailto:bounce-119913926-12657...@list.cornell.edu] En nombre de Ray Zimmerman
> Enviado el: jueves, 19 de noviembre de 2015 12:03
> Para: MATPOWER discussion forum
> Asunto: Re: Question about LMP
>  
> The LMPs for a DC OPF problem do incorporate any generator limits as well as 
> generation cost. Consider the case with no congestion, where the LMPs are 
> uniform at all nodes. For nodes with generators that are dispatched between 
> their lower and upper limits, the LMP equals their marginal cost of 
> generation. For a node with a generator at a binding upper (lower) limit, the 
> LMP will equal the marginal cost of generation plus (minus) the shadow price 
> on the binding upper (lower) generation constraint.
>  
>    Ray
>  
>> On Nov 19, 2015, at 8:27 AM, Victor Hugo Hinojosa M. <victor.hinoj...@usm.cl 
>> <mailto:victor.hinoj...@usm.cl>> wrote:
>>  
>> Dear Jovan and Sarmad,
>> I agree with your comments about LMP. In this analysis I’m not considered 
>> the congestion. If the generation inequality constraints aren’t active, 
>> Matpower prints this information correctly, and It’s possible to realize 
>> different prices when the lines is congested. Sarmad, I’ve verified your 
>> idea. Despite the fact that the shadow price for the minimum or maximum is 
>> active, the LMP shown are the same for all buses.
>> My question is about why LMP doesn’t include the Lagrange multipliers 
>> related to generation inequality constraints. I did a model using the dual 
>> problem for the DCOPF, and I realized that dual constraints are the prices 
>> for each buses. It’s very clear in those constraints that those “prices” 
>> take into account the marginal cost, the congestion cost through the partial 
>> transmission distribution factors (PTDF) and the generation constraints.
>> In the technical literature for the DCOPF (losses are neglected), the LPM 
>> are modeled considering energy cost and congestion cost. However, in the 
>> book “Spot pricing of electricity” from F. Schweppe et all, authors include 
>> these shadow prices in order to compute the spot prices.
>> I’d like to know your feedback about these comments.
>> Regards,
>> Vh
>>  
>> De: bounce-119912654-12657...@list.cornell.edu 
>> <mailto:bounce-119912654-12657...@list.cornell.edu> 
>> [mailto:bounce-119912654-12657...@list.co 
>> <mailto:bounce-119912654-12657...@list.co>rnell.edu <http://rnell.edu/>] En 
>> nombre de Jovan Ilic
>> Enviado el: jueves, 19 de noviembre de 2015 1:13
>> Para: MATPOWER discussion forum
>> Asunto: Re: Question about LMP
>>  
>>  
>> Dear Victor,
>>  
>> If there is no congestion in the network, there is the same LMP at all the 
>> nodes. 
>> The LMP consists of loss, congestion, and energy costs. DCOPF has no 
>> losses, and if there is no congestion only the energy cost is accounted for. 
>> You can think of it as if since there is no congestion or loss cost the 
>> energy can
>> be distributed to all nodes at the same price. 
>>  
>> Regards, 
>> Jovan Ilic
>>  
>> On Wed, Nov 18, 2015 at 4:37 PM, Victor Hugo Hinojosa M. 
>> <victor.hinoj...@usm.cl <mailto:victor.hinoj...@usm.cl>> wrote:
>> Dear Prof. Zimmerman,
>> 
>> I have a question about Local Marginal Prices (LMP) that are shown in
>> Matpower.
>> 
>> The definition of the LMP is the marginal cost of supplying, at least cost,
>> the next increment of electric demand at a specific location (node) on the
>> electric power network, taking into account both supply (generation/import)
>> bids and demand (load/export) offers and the physical aspects of the
>> transmission system including transmission and other operational
>> constraints.
>> 
>> When it is performed a DCOPF, Matpower shows LMP for each bus considering
>> the marginal cost (energy cost) and the congestion cost so that I'd like to
>> know why the generation constraints (maximum and minimum power) aren't
>> considered in the LMP.
>> 
>> Thank you so much for your ideas and comments.
>> 
>> Regards,
>> 
>> Vh
>> 
>> 
>> 
>>  
> 
>  

Reply via email to