Hello Houssem,

I don't know the reason why line Q-losses are reported that way in
MATPOWER, but heuristically, if voltages are kept within reasonable bounds
(say 0.9 to 1.10 in pu) then you can see that Q injections from line
Bshunts will remain also bounded, as they are equal to Bs·V^2.  By
contrast, the transmission part of Q-losses (I^2·X) can vary orders of
magnitude, depending on the load on the transmission network.

-- 
Jose L. Marin
Grupo AIA


On Mon, Apr 4, 2016 at 3:22 AM, Houssem <bouchekara.hous...@gmail.com>
wrote:

>
> Thanks Gang for your answer. This confirms my thoughts because it is
> written I^2*Z above losses. Therefore, these losses are power loss in the
> series portion of the pi-model of the transmission line.
> However, in an OPF problem where the objective is to minimize reactive
> power transmission losses, reactive losses are computed taking into account
> both portions of the transmission line (i.e. line charging capacitance
> portions of the pi-model are also included). So what is the goal of
> calculating losses in matpower including only the series portion? Is there
> any advantages of doing so?
>
> Regards
>
> Houssem
>
>
>
> On 03/04/2016 11:59 PM, Gang Huang wrote:
>
> Dear Houssem,
>
>
>
> Please note that transmission lines have charging susceptance (i.e.,
> mpc.branch(:, BR_B)), and its contribution to the reactive power is not
> listed in the pretty-printed output.
>
>
>
> Best regards,
>
>
>
> Gang
>
>
>
> *From:* bounce-120330262-73377...@list.cornell.edu [
> mailto:bounce-120330262-73377...@list.cornell.edu
> <bounce-120330262-73377...@list.cornell.edu>] *On Behalf Of *Houssem
> *Sent:* Sunday, April 03, 2016 11:29 AM
> *To:* MATPOWER discussion forum
> *Subject:* question about losses
>
>
>
> Dear All
> I have a small question about losses in matpower .
> I have run a small program with 3 buses in matpower 4.1.
> The obtained results are:
>
> ================================================================================
> |     Branch
> Data                                                              |
>
> ================================================================================
> Brnch   From   To    From Bus Injection   To Bus Injection     Loss (I^2 *
> Z)
>   #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q
> (MVAr)
> -----  -----  -----  --------  --------  --------  --------  --------
> --------
>    1      1      2          179.33     116.79     -170.96
> -102.71       8.369       16.74
>    *2      1      3          39.03        20.69      -38.85
> -22.98        0.183        0.55*
>    3      2      3        -229.04     -147.29      238.85      166.92
>    9.813       19.63
>                                                              --------
> --------
>                                                     Total:    18.365
> 36.91
>
> my question is, in line 2 Qlosses should be (20.69)+(-22.98) =-2.29 MVar.
> However matpower displays 0.55MVar !!! is there any explanation to that?
> same for branch 1.
> Regards
> Houssem
>
>
>