Dear Sir/Madam,
         I have a question with the AC power flow calculation. In Matpower 5.1, 
when AC power flow is calculated, if the q_limt is used, as the manual states 
that "If any generator has a violated reactive power limit, its reactive 
injection is fixed at the limit, the corresponding bus is converted to a PQ bus 
and the power flow is solved again. This procedure is repeated until there are 
no more violations". Obviously, we can find that all generators violating the 
reactive power limit will be regared as PQ bus, then the power flow will be 
recalculated. However, when I opened the file runpf.m,  I fund that the states 
of all generators violating the reactive power limit are set to be zero, that 
is, "gen(mx, GEN_STATUS) = 0";. That means the generation is turned off in the 
next power flow re-calculation. This isn't included in the manual. It seems 
unreasonable. So I want to know the reason why turn off all these generators.