Well, that would only be true if it were a completely ideal transformer with no 
impedance. Even at the nominal tap ratio of 1.0 the voltages magnitudes will 
not be identical (as with a transmission line).

   Ray


> On Oct 17, 2017, at 12:19 PM, Ahmad Sadiq Abubakar 
> <ahmad.abuba...@futminna.edu.ng> wrote:
> 
> Dear Ray,
> Thanks for your response. In my case, V1 is a generator bus with 1.025 p.u. 
> and V2 is a known PQ bus with 1 p.u.
> This implied Tap is 1.02? 
> 
> On Oct 17, 2017 4:27 PM, "Ray Zimmerman" <r...@cornell.edu 
> <mailto:r...@cornell.edu>> wrote:
> The tap ratio is the off-nominal tap ratio, relating per-unit voltages, not 
> kV voltages. So if both voltages are at their nominal values (i.e. both at 1 
> p.u.) then the TAP should be 1 and SHIFT should be 0.
> 
>    Ray
> 
> 
>> On Oct 17, 2017, at 6:23 AM, Ahmad Sadiq Abubakar 
>> <ahmad.abuba...@futminna.edu.ng <mailto:ahmad.abuba...@futminna.edu.ng>> 
>> wrote:
>> 
>> Hi, all
>> For a given case branch data r, x, b, assuming the branch is a transformer, 
>> between bus1 and bus2, with voltages V1 and V2 KV respectively. How do I 
>> obtain the Tap ration (column 9) and shift (column 10) of the branch matrix?
>> 
>> I have simply used V1/V2 as the Tap ration while the shift is zero, however, 
>> the power flow did not converged. Am I missing something?
>> 
>> Kindly assist
>> 
>> best regrads 
>> A. A. Sadiq
>> 
> 

Reply via email to