It is a planning case 2020 WECC system

On Tue, Apr 3, 2018 at 12:25 PM, Jovan Ilic <[email protected]> wrote:

>
> Vikram,
>
> For what year is this WECC system?
>
> Jovan
>
>
> On Tue, Apr 3, 2018 at 11:54 AM, vikram reddy <[email protected]>
> wrote:
>
>> I have a 20000 bus WECC system in PSSE raw format. I am trying to run the
>> DC power flow, but the total of the power injections that I got from
>> MATPOWER does not equal to zero. Are the voltage angles obtained in this
>> case wrong?
>>
>> Thanks,
>> Vikram
>>
>> On Tue, Apr 3, 2018 at 6:46 AM, Ray Zimmerman <[email protected]> wrote:
>>
>>> There is no need to check. The slack bus active power will be adjusted
>>> to make the injections sum to zero. And the DC power flow in MATPOWER is a
>>> lossless approximation. That is, it assumes the losses are zero.
>>>
>>>    Ray
>>>
>>>
>>> On Mar 28, 2018, at 2:28 PM, vikram reddy <[email protected]>
>>> wrote:
>>>
>>> Hi,
>>>
>>> I am working on a 20000 bus system and running a DC load flow. Now, the
>>> power injection vector computed as
>>>
>>>   Pbus = real(makeSbus(baseMVA, bus, gen)) - Pbusinj - bus(:, GS) /
>>> baseMVA;
>>>
>>> In general, the total of the power injection vector should be zero
>>> implying generation=load+losses. MATPOWER does not do the checking if the
>>> total of injection vector is zero.
>>>
>>> 1. Why does MATPOWER not check if the total of injection vector goes to
>>> zero? Is it not important?
>>> 2.  What happens if the injection vector is not zero and running the DC
>>> load flow? I assume the voltage angles thus obtained will have an error.
>>> 3. Assuming losses is the total sum of Pbus vector, how should the
>>> losses be distributed?
>>>
>>> Thanks,
>>> Vikram
>>>
>>>
>>>
>>>
>>
>

Reply via email to