This is a modeling issue (not really a MATPOWER issue). You’ll need to use the 
nominal voltage to convert your current rating to an MVA rating.

    Ray


> On Feb 14, 2019, at 1:34 AM, amir ali Hosseini <[email protected]> wrote:
> 
> Hello 
> and thanks a lot
> I can make net work .
> and now 
> I need rateA,B,C 
> my cable is 
> 
> 
> <image.png>
> 
> 
> i found rating current 
> 698
> 483 
> 230
> 156 ampere
> but I do nt how get rate A,B,C
> thank you
> 
> On Tue, Feb 12, 2019 at 7:08 PM Ray Zimmerman <[email protected] 
> <mailto:[email protected]>> wrote:
> Oops … sorry for the repeat, Carlos, didn’t see this until after I’d sent my 
> reply.
> 
>    Ray
> 
> 
> > On Feb 11, 2019, at 11:10 AM, Carlos E Murillo-Sanchez 
> > <[email protected] <mailto:[email protected]>> wrote:
> > 
> > amir ali Hosseini wrote:
> >> Dear Sir,
> >> i trying make a new network. 37 bus
> >> but ! after runpf  .i have warning!
> >> can you help me ?
> >> thanks a lot.
> >> my warning is :
> >> Warning: Matrix is singular to working precision.
> >> > In newtonpf (line 89)
> >>   In runpf (line 204)
> >> find attachment .
> >> new network with 37 node.
> >> 
> > This is the output of case_info.m applied to your case file:
> > 
> > >> case_info(mpc)
> > Checking connectivity ... single connected network, plus 1 isolated bus
> > Elapsed time is 0.245606 seconds.
> > ================================================================================
> >                         Full       Island     Isolated
> >                        System         1         Buses
> > Number of:           ----------  ----------  ----------
> >   buses                    37          36           1
> >   loads                    36          35           1
> >     on                     36          35           1
> >     off                     -           -           -
> >     fixed                  36          35           1
> >     dispatchable            -           -           -
> >       on                    -           -           -
> >       off                   -           -           -
> >   generators                1           1           -
> >     on                      1           1           -
> >     off                     -           -           -
> >   shunt elements            -           -           -
> >   branches                 36          36           -
> >     on                     36          36           -
> >     off                     -           -           -
> >     ties (off)              -           -           -
> > 
> > Load
> >   active (MW)
> >     dispatched              9.6         9.5         0.1
> >       fixed                 9.6         9.5         0.1
> >       dispatchable          -           -           -
> >     curtailed               -           -           -
> >     nominal                 9.6         9.5         0.1
> >       on                    9.6         9.5         0.1
> >       off                   -           -           -
> >       fixed                 9.6         9.5         0.1
> >       dispatchable          -           -           -
> >         on                  -           -           -
> >         off                 -           -           -
> >   reactive (MVAr)
> >     dispatched              4.6         4.6         0.0
> >       fixed                 4.6         4.6         0.0
> >       dispatchable          -           -           -
> >     curtailed               -           -           -
> >     nominal                 4.6         4.6         0.0
> >       on                    4.6         4.6         0.0
> >       off                   -           -           -
> >       fixed                 4.6         4.6         0.0
> >       dispatchable          -           -           -
> >         on                  -           -           -
> >         off                 -           -           -
> > 
> > Generation
> >   active (MW)
> >     dispatched             11.5        11.5         -
> >     max capacity           10.0        10.0         -
> >       on                   10.0        10.0         -
> >       off                   -           -           -
> >     min capacity            -           -           -
> >       on                    -           -           -
> >       off                   -           -           -
> >   reactive (MVAr)
> >     dispatched              -           -           -
> >     max capacity            1.5         1.5         -
> >       on                    1.5         1.5         -
> >       off                   -           -           -
> >     min capacity           -0.2        -0.2         -
> >       on                   -0.2        -0.2         -
> >       off                   -           -           -
> > 
> > Shunt Injections
> >     active (MW)             -           -           -
> >     reactive (MVAr)         -           -           -
> > 
> > Branch Losses
> >     active (MW)             -           -           -
> >     reactive (MVAr)         -           -           -
> > 
> > DC line
> >   export (MW)
> >     dispatch                -           -           -
> >     max capacity            -           -           -
> >       on                    -           -           -
> >       off                   -           -           -
> >     min capacity            -           -           -
> >       on                    -           -           -
> >       off                   -           -           -
> > 
> > Reference Buses
> >   num of ref buses          1           1           0
> >   ref bus numbers           1           1
> > >>
> > 
> > It seems that you have an isolated bus; is this what you intend in your 
> > case file?
> > 
> > carlos.
> > 
> > 
> 
> 
> 