Yes, internally, it is converted to a p.u. value. The susceptance is specified 
as the MVAr injected at a voltage of 1 p.u., so simply dividing that number by 
the MVA base gives the appropriate p.u. susceptance.

   Ray


> On Mar 21, 2019, at 4:16 PM, Jubeyer Rahman <[email protected]> wrote:
> 
> I have one confusion, on page 145 (Matpower manual for 7.0b1) in Table B-1, 
> it says the shunt susceptance is in MVAR , is that correct? If yes, so is 
> there any internal conversion for that for running power flow?
> 
> On Thu, Mar 21, 2019 at 9:09 AM Ray Zimmerman <[email protected] 
> <mailto:[email protected]>> wrote:
> Voltages and impedances are specified in p.u. in the case file data, but 
> powers in MW and MVAr. That is, the conversion done internally, is simply to 
> divide all of the powers by the baseMVA.
> 
> If you were to specify the powers in p.u. and set the baseMVA to 1, you 
> should get the same solution, with the solution powers also expressed in 
> per-unit, of course. Internally, it would be solving everything with the same 
> values.
> 
>    Ray
> 
> > On Mar 20, 2019, at 9:36 PM, Jubeyer Rahman <[email protected] 
> > <mailto:[email protected]>> wrote:
> > 
> > Hi,
> > 
> > Is there any chance for wrong results, if I convert every parameters(Pg,Qg, 
> > Pmax, Qmax, etc.; every possible power flow data) that could be transformed 
> > into per unit and call the runpf in matpower?
> > 
> > My point of confusion is, in usual case data file, only the voltages are 
> > given in per unit and all other parameters are usually given in actual 
> > units, and runpf is applied on that type of case file; is there really an 
> > internal conversion of the given data?
> > 
> > Regards,
> > Jubeyer
> 
> 
> 