The power flow does not enforce any limits (generator, voltage or branch flow 
limits). The only exception is that it will attempt to enforce generator 
reactive limits if the pf.enforce_q_lims option is true, which it does by 
relaxing the voltage setpoint at the generator when the reactive limit is 
reached.

If you want a solution that respects all limits, you will need to use the OPF.

   Ray




> On Aug 28, 2018, at 4:03 AM, Mariusz Drabecki <[email protected]> wrote:
> 
> Dear All,
>  
> I ran Power Flow on slightly changed case Illinois 200 (PD of each node 
> augmented by 8%). The success flag is 1 and the PF fully converged. However, 
> when I look at the results I get situation shown below i.e.  PG output is 
> higher than its upper constraint PMAX of the slack bus. I know that the slack 
> bus’ power injection results from the situation in the grid, yet shouldn’t it 
> still be within acceptable limits? If not then what would you suggest to 
> force the PMAX limit?
>  
>  
> GEN_BUS           PG          QG         QMAX  QMIN   VG         MBASE        
>          GEN_STATUS    PMAX                   PMIN
> 189                         598,10 150,31   209,45   -46,67   1,07       
> 682,98                   1                             569,15                 
>   170,75
>  
> Best,
> Mariusz