Dear Chixin Xiao,
if you have executed it already, the avoid this message. Otherwise i have
attached corrected case30 combined with case33.
*Regards,*

*Aamir Nawaz*

On Mon, Sep 2, 2019 at 12:33 PM 赤心 肖 <chixinx...@hotmail.com> wrote:

> Hi Prof.Ray,
>      I found the mistake that I forgot to transfer the W to KW while
> combining two systems. Thanks.
> Regards,
> Chixin
> ------------------------------
> *From:* bounce-123871453-44420...@list.cornell.edu <
> bounce-123871453-44420...@list.cornell.edu> on behalf of
> chixinx...@hotmail.com <chixinx...@hotmail.com>
> *Sent:* 02 September 2019 14:01
> *To:* 'MATPOWER discussion forum' <matpowe...@list.cornell.edu>
> *Subject:* Power flow while involving radial systems
>
> Dear Prof.Ray,
>    The runpf and the runopf did not converge while handling a revised
> system (i.e., IEEE 30 and IEEE 33).  The revised system is attached.  Could
> you give me some suggestions when you feel convenient? Thanks.
>    The revising details:  a standard IEEE 30 bus system [] is revised by
> connecting the bus 2 to the bus 1 of an IEEE 33-bus radial system [] which
> consists of 33 buses, 32 lines,  a  voltage  of  12.66kV,  load  size  of
>  3.715MW  and 2.3MVar.
>      In the new combined system, the original bus-index  of the IEEE
> 33-bus has increased 30 (i.e., the original bus-index 1 corresponds the new
> index 31, and so on). The resistance and reactance between bus 1 and bus 31
> are 0.2030 (p.u.) and 0.1034 (p.u.) respectively.
> Regards,
> Chixin
>

Attachment: case30_RS33_XIAO.m
Description: Binary data