Dear Professor Zimmerman,
Thank you so much for your help.
Kind Regard,
Naime

On Wed, Apr 21, 2021 at 7:23 AM Ray Daniel Zimmerman <r...@cornell.edu>
wrote:

> Sorry, the ‘halved" and “doubled” language was confusing, except in the
> context of identical parallel lines.
>
> For lines with parameters r1, x1, b1 and r2, x2, b2, the equivalent values
> for the parallel set would be rt, xt, bt, where …
>
> rt = 1 / (1/r1 + 1/r2)
> xt = 1 / (1/x1 + 1/x2)
> bt = b1 + b2
>
> So I think the first alternative in your example is correct, except for
> multiplying b by 2.
>
> You can also easily check by running a power flow before and after
> consolidating the lines. You should get *exactly* the same solution if
> you did it correctly.
>
> Hope this clarifies,
>
>    Ray
>
> On Apr 19, 2021, at 11:37 AM, naime ahmadi <naimeahm...@gmail.com> wrote:
>
> Dear Professor Zimmerman,
> Thank you for your time.
> Please confirm if my understanding is correct.
> For this duplicate branch
> 77 80 0.017 0.0485 0.0472 0 0 0 0 0 1 -360 360;
> 77 80 0.0294 0.105 0.0228 0 0 0 0 0 1 -360 360;
>
> 1/r_t =1/ 0.017 +1/ 0.0294 ---> r_t=0.0108   *OR*  r_t = (0.017 +
> 0.0294)/2 ---> r_t=0.0232
> 1/x_t =1/ 0.0485 +1/ 0.105 ---> x_t=0.0332  *OR* x_t =(0.0485 + 0.105)/2
> ---> x_t=0.07675
> b_t= (0.0472 + 0.0228)*2  ---> b_t=0.14
> so the equivalent branch is
> 77 80  0.0108  0.0332  0.14 0 0 0 0 0 1 -360 360;360;
> *OR*
> 77 80   0.0232    0.07675   0.14 0 0 0 0 0 1 -360 360;360;
> Kind Regards,
> Naime
>
> On Tue, Apr 20, 2021 at 1:09 AM Ray Daniel Zimmerman <r...@cornell.edu>
> wrote:
>
>> In general, the line ratings RATE_A, etc, would also equal the sum of the
>> individual line ratings, but in this case the capacity limit is not given
>> (interpreted as unlimited) so no change.
>>
>> However, a quick correction … while the total impedance (*r* and *x*)
>> are halved, the total line charging (*b*) is doubled.
>>
>>     Ray
>>
>>
>> On Apr 19, 2021, at 9:59 AM, naime ahmadi <naimeahm...@gmail.com> wrote:
>>
>> Hello Matpower users,
>>
>> I want to remove duplicate branches in IEEE 118 bus system and put an
>> equivalent one. For example:
>> fbus tbus   r    x    b rateA rateB rateC ratio angle status angmin angmax
>>
>> duplicate branches:
>>  42   49   0.0715 0.323 0.086 0 0 0 0 0 1 -360 360;
>>  42   49   0.0715 0.323 0.086 0 0 0 0 0 1 -360 360;
>>
>> equivalent branch:
>> 42 49 0.0357 0.1615 0.0430 0 0 0 0 0 1 -360 360;
>>
>> Is it sufficient to only change r, x and b to equivalent one or do I need
>> to have more changes?
>>
>> Thanks,
>> Naime
>>
>>
>>
>

Reply via email to