You’ve got the right idea. You can simply set the branch status to 0 and then 
use find_islands() and to find the isolated buses and set their BUS_TYPE  to 
NONE (4). You may then be left with multiple islands, also found via 
find_islands() or extract_islands(). To solve a power flow, each island needs 
its own reference bus (which may have been eliminated even for the main 
system). The load / generation mismatch could also be potential very large in 
some islands, and that would show up in the slack generation (negative, or 
unreasonably large positive).

So I think the main challenge in automating everything is in selecting a new 
reference bus for islands without one. I’d probably go with the first PV bus, 
and if there are no PV buses, then that whole island blacks out and you can set 
all its buses to type NONE.

Hope this helps,

   Ray



On Dec 4, 2021, at 12:58 PM, prem panigrahi 
<prempanigr...@outlook.com<mailto:prempanigr...@outlook.com>> wrote:

Dear Ray sir, is their any direct process to remove bus along with their 
branches . I am using mpc.branch method to remove a bus with its branches. But 
I am facing difficulties when I have to remove more than 100 buses.
mpc.branch([6161;7479;7480;7488;7489;7490], BR_STATUS) = 0;
results=rundcpf(mpc,opt)
[groups, isolated] = find_islands(mpc)
mpc_list = extract_islands(mpc)
[GROUPS, ISOLATED] = case_info(mpc)
mpc.bus([ISOLATED],BUS_TYPE)=4
results=rundcpf(mpc,opt)

Sent from Mail<https://go.microsoft.com/fwlink/?LinkId=550986> for Windows