Ok.
Will check that.

On Tue, 22 Nov, 2022, 1:08 am Ray Daniel Zimmerman, <r...@cornell.edu>
wrote:

> If you convert everything into per-unit correctly, using a different
> voltage base for the different buses, it shouldn’t be a problem. I suggest
> finding a good textbook on converting parameters to per-unit to make sure
> you get it right, especially for the transformer.
>
>     Ray
>
>
> > On Nov 7, 2022, at 12:56 PM, Irfan Mujawar <irfanbudhg...@gmail.com>
> wrote:
> >
> > I want to use the MATPOWER for load flow analysis of the practical
> radial distribution system.
> > In the system two voltage levels are there.
> > First is 11 kV bus (Bus 1) which is slack bus.
> > All other buses are of 440V bus.
> > There is a transformer of 11kV/440V  between bus 1 and 2.
> > From bus 2 onwards are load bus.
> > At some buses load is present at some buses no load is present.
> > I know the values of R and X of line in ohm.
> > How to perform the load flow analysis of this system having two voltage
> levels with transformer?
> > How to proceed.
> >
> >  I am able to perform the load flow analysis of the system from 440V and
> downstream buses i.e. with one voltage level.
> > I am facing the problem when I make bus 1 as slack bus with 11 kV.
> >
> > When I have added the 11 kV line and performed the load flow total
> losses are less than that of load flow when only 440V line and downstream
> loads are present.
> >
> > I am not getting what is wrong.
> > Please help.
> > Thank you.
>
>

Reply via email to