Morning all..
I've encountered an odd MIB that I could use some insight on. My
implementation (using mibble-2.9.3) is correctly only finding one OID
from this MIB since the there is no true RootSymbol here.. Being void of
a MODULE-IDENTITY mibble seems to target the first OBJECT in the MIB
'pbtBatMeasurementInterval' as the RootSymbol. Since this OBJECT has no
children, my code only finds the one entry..
Is it standard to have OIDs out there without MODULE-IDENTITY?
If so, I'm curious what code is used to parse them when there is no
hierarchy from which to build an OID tree?
Much thanks and here is the vendor's MIB that I'm trying to parse.
The MIB Browser shows them all under a 'VALUES' node - so I think my
code is perhaps not adapting well..
-Matthew
-- ****************************************************************************
-- *
-- * Module Name: BatteryAgentMIB
-- *
-- *
-- * Description: This MIB provides access to the battery information
collected by
-- * the Phoenix Battery Monitoring products. The MIB supports
an arbitrary
-- * number of Strings and Jars (Batteries).
-- * Devices of this type are not presently supported by the HMS
MIBs.
-- * This MIB is intended to be used in conjunction with the
HMS
-- * property, alarms, and common MIBs.
-- *
-- * Created: 09/26/2005 by Mike Quelly, Phoenix Broadband Technologies.
-- * Revised: 12/16/2005 by Mike Quelly, Added additional objects.
-- * Revised: 12/20/2005 by Mike Quelly, Added sensor firmware version.
-- * Revised: 12/27/2005 by Mike Quelly, Relocated some objects.
-- * Revised: 12/29/2005 by Mike Quelly, Minor cleanup.
-- * Revised: 04/13/2006 by Mike Quelly, Added pbtBatStringCurrent,
-- * and pbtBatStringConnectionAdmittance
-- * Added Units where required.
-- * Revised: 05/09/2006 by Mike Quelly Added values 8 and 9 to
pbtBatStringStatus,
-- * Corrected units in pbtBatStringVoltage
description,
-- * Added value 6 to
pbtBatBatterySensorStatus,
-- * Changed the resolution
ofpbtBatteryVoltage to 0.01.
-- * Changed from Battery to Cell Admittance.
-- * Revised: 05/18/2006 by Mike Quelly Revised description for
pbtBatStringCurrent and added
-- * range.
-- * Revised: 12/27/2006 by Mike Quelly Added pbtBatLocation.
-- * Revised: 01/25/2007 by Mike Quelly Added value 7 to
pbtBatBatterySensorStatus.
-- * Revised: 01/29/2007 by Mike Quelly Changed the units of
pbtBatMeasurementInterval from
-- * seconds to hours.
-- * Revised: 06/15/2007 by Mike Quely Revised object descriptions.
-- * Revised: 06/20/2007 by Mike Quelly Added StringStatus state 10.
-- * Revised: 03/17/2008 by Mike Quelly Added pbtBatBatteryElectrolyteLevel.
-- * Revised: 07/22/2008 by Mike Quelly Changed Conductance to Admittance.
-- * Revised: 02/17/2009 by Mike Quelly Added pbtBatStringEqualizationControl.
-- * Changed Battery to Jar where
appropriate in Object
-- * names. The OIDs were not changed.
Other minor edits.
-- * Revised: 01/19/2010 by Mike Quelly Renamed pbtBatStringCurrent to
pbtBatStringFloatCurrent.
-- * Added pbtBatStringDischargeStatus,
-- * pbtBatStringRippleVoltage,
-- * pbtBatStringJarVoltageDelta, and
-- * pbtBatStringDischargeCurrent.
-- *
-- * Revised: 03/25/2010 by Mike Quelly Changed the max value of
pbtBatJarNumber from 24 to 40.
-- * Modified pbtBatStringFloatCurrent
scaling from 0.1 to 0.001 Amps,
-- * and range from (-1000..100) to
(-10000..10000).
-- * Revised: 04/01/2010 by Mike Quelly Added pbtBatStringSensorComStatus,
-- * pbtBatStringDischargeEvents,
-- *
pbtBatStringDischargeSeconds, and
-- *
pbtBatStringDischargeSecondsTotal.
-- * Revised: 04/14/2010 by Mike Quelly Added pbtBatJarVoltageHiRes.
-- * Revised: 09/29/2010 by Mike Quelly Added VirtualStringTable.
-- * Revised: 09/30/2010 by Mike Quelly Added VirtualJarTable.
-- * Added pbtBatJarPhysicalStringNumber and
-- * pbtBatJarPhysicalJarNumber.
-- ****************************************************************************
PBT-BATTERYAGENT-MIB DEFINITIONS ::= BEGIN
IMPORTS
OBJECT-TYPE FROM RFC-1212
DisplayString,DateAndTime FROM SNMPv2-TC
pbtBatteryAgent FROM PBT-ROOT-MIB
;
pbtBatMeasurementInterval OBJECT-TYPE
SYNTAX INTEGER (0..32000)
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Time interval between autonomous admittance measurements,
in hours. Default value is 8 hours."
::= { pbtBatteryAgent 1 }
pbtBatStrings OBJECT-TYPE
SYNTAX INTEGER ( 0..6 )
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Number of battery strings connected to this device."
::= { pbtBatteryAgent 2 }
pbtBatStringTable OBJECT-TYPE
SYNTAX SEQUENCE OF PbtBatStringEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Table containing information about each String."
::= { pbtBatteryAgent 3 }
pbtBatJarTable OBJECT-TYPE
SYNTAX SEQUENCE OF PbtBatJarEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Table containing information about each jar (battery)."
::= { pbtBatteryAgent 4 }
pbtBatLocation OBJECT-TYPE
SYNTAX DisplayString (SIZE(32))
ACCESS read-write
STATUS mandatory
DESCRIPTION
"String describing the location.
This object is nonvolatile as specified in the HMS MIBs.
The default value of this object is 'Default Site Location'."
::= { pbtBatteryAgent 5 }
pbtBatVirtualStringTable OBJECT-TYPE
SYNTAX SEQUENCE OF PbtBatVirtualStringEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Table containing information about each Virtual String."
::= { pbtBatteryAgent 6 }
pbtBatVirtualJarTable OBJECT-TYPE
SYNTAX SEQUENCE OF PbtBatVirtualJarEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Table containing information about each jar (battery)
on a Virtual String."
::= { pbtBatteryAgent 7 }
pbtBatStringEntry OBJECT-TYPE
SYNTAX PbtBatStringEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"List of information about each String."
INDEX { pbtBatStringNumber }
::= { pbtBatStringTable 1 }
PbtBatStringEntry ::=
SEQUENCE
{
pbtBatStringNumber
INTEGER,
pbtBatStringJars
INTEGER,
pbtBatStringStatus
INTEGER,
pbtBatStringControl
INTEGER,
pbtBatStringName
DisplayString,
pbtBatStringVoltage
INTEGER,
pbtBatStringFloatCurrent
INTEGER,
pbtBatStringConnectionAdmittance
INTEGER,
pbtBatStringEqualizationControl
INTEGER,
pbtBatStringJarVoltageDelta
INTEGER,
pbtBatStringDischargeCurrent
INTEGER,
pbtBatStringDischargeStatus
INTEGER,
pbtBatStringRippleCurrent
INTEGER,
pbtBatStringSensorComStatus
INTEGER,
pbtBatStringDischargeEvents
INTEGER,
pbtBatStringDischargeSeconds
INTEGER,
pbtBatStringDischargeSecondsTotal
INTEGER
}
pbtBatStringNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..6 )
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Index into the Table. Specifies the String number."
::= { pbtBatStringEntry 1 }
pbtBatStringJars OBJECT-TYPE
SYNTAX INTEGER ( 1..40 )
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Number of Jars (batteries) in this string."
::= { pbtBatStringEntry 2 }
pbtBatStringStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),disabled(2),shorted(3),missingSensor(4),
tooManySensors(5),sensorFault(6),alarms(7),
initializing(8), sensorDisabled(9),
stringDisconnected(10),
noSensorCom(11)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Status of this String."
::= { pbtBatStringEntry 3 }
pbtBatStringControl OBJECT-TYPE
SYNTAX INTEGER {enabled(1),disabled(2)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Control the String measurements.
This object is nonvolatile. The default value is 1."
::= { pbtBatStringEntry 4 }
pbtBatStringName OBJECT-TYPE
SYNTAX DisplayString (SIZE(32))
ACCESS read-write
STATUS mandatory
DESCRIPTION
"String describing the battery string.
This object is nonvolatile as specified in the HMS MIBs.
The default value of this object is 'String n'."
::= { pbtBatStringEntry 5 }
pbtBatStringVoltage OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Total String Voltage.
Units = 0.0 Volts DC
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatStringEntry 6 }
pbtBatStringFloatCurrent OBJECT-TYPE
SYNTAX INTEGER ( -10000..10000 )
ACCESS read-write
STATUS mandatory
DESCRIPTION
"String Current. Positive charge, negative discharge.
Units = milliamps DC.
This object is read-write so that the management system can
provide the nominal current where it cannot be measured.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatStringEntry 7 }
pbtBatStringConnectionAdmittance OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Typical connductance of the connection between the sensor and
the battery. Units = Mho."
::= { pbtBatStringEntry 8 }
pbtBatStringEqualizationControl OBJECT-TYPE
SYNTAX INTEGER {enabled(1),disabled(2)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Enables or Disables battery equalization on this string. This
object is nonvolatile. The default value is disabled(2)."
::= { pbtBatStringEntry 9 }
pbtBatStringJarVoltageDelta OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"The difference between the highest and lowest jar voltage.
This object is only available in the SC3 version of the
Site Controller.
Units = 0.001 Volt (1 mV).
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatStringEntry 10 }
pbtBatStringDischargeCurrent OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"String Discharge Current.
Units = Amps DC.
This object is only available in the SC3 version of the
Site Controller.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatStringEntry 11 }
pbtBatStringDischargeStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),discharge(2)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the presence of a discharge event.
This object must provide for alarm management capabilities
with a coresponding entry in the discreteTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatStringEntry 12 }
pbtBatStringRippleCurrent OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"String AC Ripple Current.
Units = 0.1 AC Amps. (100 mA resolution)
This object is only available in the SC3 version of the
Site Controller when the current sensor is installed.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatStringEntry 13 }
pbtBatStringSensorComStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),faultedSensor(2)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates that the site controller has
lost communications with one or more sensors on this string.
This object must provide for alarm management capabilities
with a coresponding entry in the discreteTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatStringEntry 14 }
pbtBatStringDischargeEvents OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-write
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the number of discharge events
that have occured. The counter is reset by writting zero to
this object. Other values may not be written."
::= { pbtBatStringEntry 15 }
pbtBatStringDischargeSeconds OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the duration of the present or
previous (if over) discharge event.
The counter is reset when a new discharge event begins."
::= { pbtBatStringEntry 16 }
pbtBatStringDischargeSecondsTotal OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-write
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the total discharge time.
The counter is reset by writting zero to
this object. Other values may not be written."
::= { pbtBatStringEntry 17 }
pbtBatJarEntry OBJECT-TYPE
SYNTAX PbtBatJarEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"List of information about each jar (battery)."
INDEX { pbtBatJarStringNumber, pbtBatJarNumber }
::= { pbtBatJarTable 1 }
PbtBatJarEntry ::=
SEQUENCE
{
pbtBatJarStringNumber
INTEGER,
pbtBatJarNumber
INTEGER,
pbtBatJarSensorStatus
INTEGER,
pbtBatJarSensorControl
INTEGER,
pbtBatJarSensorLedControl
INTEGER,
pbtBatJarName
DisplayString,
pbtBatJarVoltage
INTEGER,
pbtBatJarTemperature
INTEGER,
pbtBatJarCellAdmittance
INTEGER,
pbtBatJarAdmittanceTime
DateAndTime,
pbtBatJarCellInitialAdmittance
INTEGER,
pbtBatJarInitialAdmittanceTime
DateAndTime,
pbtBatJarCellAdmittanceChange
INTEGER,
pbtBatJarSensorVersion
INTEGER,
pbtBatJarElectrolyteLevel
INTEGER,
pbtBatJarVoltageHiRes
INTEGER,
pbtBatJarPhysicalStringNumber
INTEGER,
pbtBatJarPhysicalJarNumber
INTEGER
}
pbtBatJarStringNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..6 )
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Index into the Table. Specifies the String number."
::= { pbtBatJarEntry 1 }
pbtBatJarNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..40 )
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Index into the Table. Specifies the Jar (Battery) number."
::= { pbtBatJarEntry 2 }
pbtBatJarSensorStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),fault(2),measuring(3),sensorDisabled(4),
stringDisabled(5),missing(6),measurementFailed(7)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"The present status of the sensor on this Jar."
::= { pbtBatJarEntry 3 }
pbtBatJarSensorControl OBJECT-TYPE
SYNTAX INTEGER {enable(1),measureNow(2),disable(3),resetAdmittance(4)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Control the admittance measurements.
1 = Autonoumous admittance measurements on this Jar at
the specified Interval.
2 = Measure admittance now (ASAP), reverts to 1 after the measurement.
3 = Admittance measurements are disabled.
4 = Set the Jar initial admittance values and time to the present
admittance and time.
This object is nonvolatile. The default value is 1."
::= { pbtBatJarEntry 4 }
pbtBatJarSensorLedControl OBJECT-TYPE
SYNTAX INTEGER
{normal(1),ledGreen(2),ledRed(3),flashGreen(4),flashRed(5),greenRed(6)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Sensor LED Control.
This object is nonvolatile. The default value is 1."
::= { pbtBatJarEntry 5 }
pbtBatJarName OBJECT-TYPE
SYNTAX DisplayString (SIZE(32))
ACCESS read-write
STATUS mandatory
DESCRIPTION
"String describing the Jar.
This object is nonvolatile as specified in the HMS MIBs.
The default value of this object is 'String n, Jar m' for
12 volt Jars and 'String n, Cell m' for 2 volt cells."
::= { pbtBatJarEntry 6 }
pbtBatJarVoltage OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Present jar voltage, Units = 0.01 Volts DC.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatJarEntry 7 }
pbtBatJarTemperature OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Present jar Temperature in degrees C.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatJarEntry 8 }
pbtBatJarCellAdmittance OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Present Cell Admittance, in Siemens (mhos).
For a 2V Cell CellAdmittance = JarAdmittance.
For a 12V Jar CellAdmittance = 6 * JarAdmittance."
::= { pbtBatJarEntry 9 }
pbtBatJarAdmittanceTime OBJECT-TYPE
SYNTAX DateAndTime
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Time the admittance was measured."
::= { pbtBatJarEntry 10 }
pbtBatJarCellInitialAdmittance OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Initial value of the cell admittance."
::= { pbtBatJarEntry 11 }
pbtBatJarInitialAdmittanceTime OBJECT-TYPE
SYNTAX DateAndTime
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Date and time the initial admittance was recorded
for this jar."
::= { pbtBatJarEntry 12 }
pbtBatJarCellAdmittanceChange OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Change in cell admittance in percent.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatJarEntry 13 }
pbtBatJarSensorVersion OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Sensor Firmware Version.
Encoded as 4 BCD digits in an integer.
example; 0x0110 = version 1.10 "
::= { pbtBatJarEntry 14 }
pbtBatJarElectrolyteLevel OBJECT-TYPE
SYNTAX INTEGER {notAvailable(1),normal(2),low(3)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"If the electrolyte sensor is not supported by the Sensor
this object will report notAvailable. If the electrolyte level is
supported (Sensors with Model Numbers containing -ES) this
object will report normal or low.
This object must provide for alarm management capabilities
with a coresponding entry in the discreteTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatJarEntry 15 }
pbtBatJarVoltageHiRes OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Present jar voltage, Units = 0.001 Volts DC.
Use object pbtBatJarVoltage for traps."
::= { pbtBatJarEntry 16 }
pbtBatJarPhysicalStringNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..6 )
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Specifies the Physical String number for this Jar.
This is the same value as the string index and is
included here to maintain consistency between the
physical jar and the virtual jar MIBS."
::= { pbtBatJarEntry 17 }
pbtBatJarPhysicalJarNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..40 )
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Specifies the Physical Jar number for this Jar.
This is the same value as the jar index and is
included here to maintain consistency between the
physical jar and the virtual jar MIBS."
::= { pbtBatJarEntry 18 }
PbtBatVirtualStringEntry ::=
SEQUENCE
{
pbtBatVirtualStringNumber
INTEGER,
pbtBatVirtualStringJars
INTEGER,
pbtBatVirtualStringStatus
INTEGER,
pbtBatVirtualStringControl
INTEGER,
pbtBatVirtualStringName
DisplayString,
pbtBatVirtualStringVoltage
INTEGER,
pbtBatVirtualStringFloatCurrent
INTEGER,
pbtBatVirtualStringEqualizationControl
INTEGER,
pbtBatVirtualStringJarVoltageDelta
INTEGER,
pbtBatVirtualStringDischargeCurrent
INTEGER,
pbtBatVirtualStringDischargeStatus
INTEGER,
pbtBatVirtualStringRippleCurrent
INTEGER,
pbtBatVirtualStringSensorComStatus
INTEGER,
pbtBatVirtualStringDischargeEvents
INTEGER,
pbtBatVirtualStringDischargeSeconds
INTEGER,
pbtBatVirtualStringDischargeSecondsTotal
INTEGER,
pbtBatVirtualJarTable
SEQUENCE OF PbtBatJarEntry
}
pbtBatVirtualStringEntry OBJECT-TYPE
SYNTAX PbtBatVirtualStringEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"List of information about each String."
INDEX { pbtBatVirtualStringNumber }
::= { pbtBatVirtualStringTable 1 }
pbtBatVirtualStringNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..6 )
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Index into the Table. Specifies the String number."
::= { pbtBatVirtualStringEntry 1 }
pbtBatVirtualStringJars OBJECT-TYPE
SYNTAX INTEGER ( 1..40 )
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Number of Jars (batteries) in this string."
::= { pbtBatVirtualStringEntry 2 }
pbtBatVirtualStringStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),disabled(2),shorted(3),missingSensor(4),
tooManySensors(5),sensorFault(6),alarms(7),
initializing(8), sensorDisabled(9),
stringDisconnected(10),
noSensorCom(11)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Status of this String."
::= { pbtBatVirtualStringEntry 3 }
pbtBatVirtualStringControl OBJECT-TYPE
SYNTAX INTEGER {enabled(1),disabled(2)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Control the String measurements.
This object is nonvolatile. The default value is 1."
::= { pbtBatVirtualStringEntry 4 }
pbtBatVirtualStringName OBJECT-TYPE
SYNTAX DisplayString (SIZE(32))
ACCESS read-write
STATUS mandatory
DESCRIPTION
"String describing the battery string.
This object is nonvolatile as specified in the HMS MIBs.
The default value of this object is 'String n'."
::= { pbtBatVirtualStringEntry 5 }
pbtBatVirtualStringVoltage OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Total String Voltage.
Units = 0.0 Volts DC
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatVirtualStringEntry 6 }
pbtBatVirtualStringFloatCurrent OBJECT-TYPE
SYNTAX INTEGER ( -10000..10000 )
ACCESS read-write
STATUS mandatory
DESCRIPTION
"String Current. Positive charge, negative discharge.
Units = milliamps DC.
This object is read-write so that the management system can
provide the nominal current where it cannot be measured.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatVirtualStringEntry 7 }
pbtBatVirtualStringEqualizationControl OBJECT-TYPE
SYNTAX INTEGER {enabled(1),disabled(2)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Enables or Disables battery equalization on this string. This
object is nonvolatile. The default value is disabled(2)."
::= { pbtBatVirtualStringEntry 9 }
pbtBatVirtualStringJarVoltageDelta OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"The difference between the highest and lowest jar voltage.
This object is only available in the SC3 version of the
Site Controller.
Units = 0.001 Volt (1 mV).
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatVirtualStringEntry 10 }
pbtBatVirtualStringDischargeCurrent OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"String Discharge Current.
Units = Amps DC.
This object is only available in the SC3 version of the
Site Controller.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatVirtualStringEntry 11 }
pbtBatVirtualStringDischargeStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),discharge(2)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the presence of a discharge event.
This object must provide for alarm management capabilities
with a coresponding entry in the discreteTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatVirtualStringEntry 12 }
pbtBatVirtualStringRippleCurrent OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"String AC Ripple Current.
Units = 0.1 AC Amps. (100 mA resolution)
This object is only available in the SC3 version of the
Site Controller when the current sensor is installed.
This object must provide for alarm management capabilities
with a coresponding entry in the propertyTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatVirtualStringEntry 13 }
pbtBatVirtualStringSensorComStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),faultedSensor(2)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates that the site controller has
lost communications with one or more sensors on this string.
This object must provide for alarm management capabilities
with a coresponding entry in the discreteTable of
SCTE-HMS-PROPERTY-MIB (HMS026).
An alarm shall be recorder as an entry in the currentAlarmTable
of SCTE-HMS-PROPERTY-MIB (HMS026).
A log record shall be added as an entry in the heCommonLogTable
of SCTE-HMS-HE-COMMON-MIB."
::= { pbtBatVirtualStringEntry 14 }
pbtBatVirtualStringDischargeEvents OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-write
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the number of discharge events
that have occured. The counter is reset by writting zero to
this object. Other values may not be written."
::= { pbtBatVirtualStringEntry 15 }
pbtBatVirtualStringDischargeSeconds OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the duration of the present or
previous (if over) discharge event.
The counter is reset when a new discharge event begins."
::= { pbtBatVirtualStringEntry 16 }
pbtBatVirtualStringDischargeSecondsTotal OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-write
STATUS mandatory
DESCRIPTION
"This object is only available in the SC3 version of the
Site Controller and indicates the total discharge time.
The counter is reset by writting zero to
this object. Other values may not be written."
::= { pbtBatVirtualStringEntry 17 }
pbtBatVirtualJarEntry OBJECT-TYPE
SYNTAX PbtBatVirtualJarEntry
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"List of information about each jar (battery)."
INDEX { pbtBatVirtualJarStringNumber, pbtBatVirtualJarNumber }
::= { pbtBatVirtualJarTable 1 }
PbtBatVirtualJarEntry ::=
SEQUENCE
{
pbtBatVirtualJarStringNumber
INTEGER,
pbtBatVirtualJarNumber
INTEGER,
pbtBatVirtualJarSensorStatus
INTEGER,
pbtBatVirtualJarSensorControl
INTEGER,
pbtBatVirtualJarSensorLedControl
INTEGER,
pbtBatVirtualJarName
DisplayString,
pbtBatVirtualJarVoltage
INTEGER,
pbtBatVirtualJarTemperature
INTEGER,
pbtBatVirtualJarCellAdmittance
INTEGER,
pbtBatVirtualJarAdmittanceTime
DateAndTime,
pbtBatVirtualJarCellInitialAdmittance
INTEGER,
pbtBatVirtualJarInitialAdmittanceTime
DateAndTime,
pbtBatVirtualJarCellAdmittanceChange
INTEGER,
pbtBatVirtualJarSensorVersion
INTEGER,
pbtBatVirtualJarElectrolyteLevel
INTEGER,
pbtBatVirtualJarVoltageHiRes
INTEGER,
pbtBatVirtualJarPhysicalStringNumber
INTEGER,
pbtBatVirtualJarPhysicalJarNumber
INTEGER
}
pbtBatVirtualJarStringNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..3 )
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Same as pbtBatJarStringNumber."
::= { pbtBatVirtualJarEntry 1 }
pbtBatVirtualJarNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..240 )
ACCESS not-accessible
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarNumber."
::= { pbtBatVirtualJarEntry 2 }
pbtBatVirtualJarSensorStatus OBJECT-TYPE
SYNTAX INTEGER {normal(1),fault(2),measuring(3),sensorDisabled(4),
stringDisabled(5),missing(6),measurementFailed(7)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarSensorStatus."
::= { pbtBatVirtualJarEntry 3 }
pbtBatVirtualJarSensorControl OBJECT-TYPE
SYNTAX INTEGER {enable(1),measureNow(2),disable(3),resetAdmittance(4)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarSensorControl."
::= { pbtBatVirtualJarEntry 4 }
pbtBatVirtualJarSensorLedControl OBJECT-TYPE
SYNTAX INTEGER
{normal(1),ledGreen(2),ledRed(3),flashGreen(4),flashRed(5),greenRed(6)}
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarSensorLedControl."
::= { pbtBatVirtualJarEntry 5 }
pbtBatVirtualJarName OBJECT-TYPE
SYNTAX DisplayString (SIZE(32))
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarName."
::= { pbtBatVirtualJarEntry 6 }
pbtBatVirtualJarVoltage OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatJarVoltage.
Configure the alarm using pbtBatJarVoltage."
::= { pbtBatVirtualJarEntry 7 }
pbtBatVirtualJarTemperature OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatJarTemperature.
Configure the alarm using pbtBatJarTemperature."
::= { pbtBatVirtualJarEntry 8 }
pbtBatVirtualJarCellAdmittance OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatJarCellAdmittance"
::= { pbtBatVirtualJarEntry 9 }
pbtBatVirtualJarAdmittanceTime OBJECT-TYPE
SYNTAX DateAndTime
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarAdmittanceTime."
::= { pbtBatVirtualJarEntry 10 }
pbtBatVirtualJarCellInitialAdmittance OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-write
STATUS mandatory
DESCRIPTION
"Same as pbtBatJarCellInitialAdmittance."
::= { pbtBatVirtualJarEntry 11 }
pbtBatVirtualJarInitialAdmittanceTime OBJECT-TYPE
SYNTAX DateAndTime
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatJarInitialAdmittanceTime."
::= { pbtBatVirtualJarEntry 12 }
pbtBatVirtualJarCellAdmittanceChange OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatJarCellAdmittanceChange.
Configure the alarm using pbtBatJarCellAdmittanceChange."
::= { pbtBatVirtualJarEntry 13 }
pbtBatVirtualJarSensorVersion OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarSensorVersion."
::= { pbtBatVirtualJarEntry 14 }
pbtBatVirtualJarElectrolyteLevel OBJECT-TYPE
SYNTAX INTEGER {notAvailable(1),normal(2),low(3)}
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Same as pbtBatVirtualJarElectrolyteLevel.
Configure the alarm using pbtBatVirtualJarElectrolyteLevel."
::= { pbtBatVirtualJarEntry 15 }
pbtBatVirtualJarVoltageHiRes OBJECT-TYPE
SYNTAX INTEGER
ACCESS read-only
STATUS mandatory
DESCRIPTION
"pbtBatVirtualJarVoltageHiRes."
::= { pbtBatVirtualJarEntry 16 }
pbtBatVirtualJarPhysicalStringNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..6 )
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Specifies the Physical String number for this Virtual Jar."
::= { pbtBatVirtualJarEntry 17 }
pbtBatVirtualJarPhysicalJarNumber OBJECT-TYPE
SYNTAX INTEGER ( 1..40 )
ACCESS read-only
STATUS mandatory
DESCRIPTION
"Specifies the Physical Jar number for this Virtual Jar."
::= { pbtBatVirtualJarEntry 18 }
END