Morning all..

I've encountered an odd MIB that I could use some insight on. My implementation (using mibble-2.9.3) is correctly only finding one OID from this MIB since the there is no true RootSymbol here.. Being void of a MODULE-IDENTITY mibble seems to target the first OBJECT in the MIB 'pbtBatMeasurementInterval' as the RootSymbol. Since this OBJECT has no children, my code only finds the one entry..

Is it standard to have OIDs out there without MODULE-IDENTITY?

If so, I'm curious what code is used to parse them when there is no hierarchy from which to build an OID tree?

Much thanks and here is the vendor's MIB that I'm trying to parse.

The MIB Browser shows them all under a 'VALUES' node - so I think my code is perhaps not adapting well..

-Matthew
-- ****************************************************************************
-- *
-- * Module Name:   BatteryAgentMIB
-- *
-- *
-- * Description:   This MIB provides access to the battery information 
collected by
-- *                the Phoenix Battery Monitoring products. The MIB supports 
an arbitrary 
-- *                number of Strings and Jars (Batteries).
-- *                Devices of this type are not presently supported by the HMS 
MIBs.
-- *                    This MIB is intended to be used in conjunction with the 
HMS 
-- *                property, alarms, and common MIBs.   
-- *
-- * Created: 09/26/2005 by Mike Quelly, Phoenix Broadband Technologies. 
-- * Revised: 12/16/2005 by Mike Quelly, Added additional objects.
-- * Revised: 12/20/2005 by Mike Quelly, Added sensor firmware version.
-- * Revised: 12/27/2005 by Mike Quelly, Relocated some objects.
-- * Revised: 12/29/2005 by Mike Quelly, Minor cleanup.         
-- * Revised: 04/13/2006 by Mike Quelly, Added pbtBatStringCurrent, 
-- *                                     and pbtBatStringConnectionAdmittance
-- *                                    Added Units where required.     
-- * Revised: 05/09/2006 by Mike Quelly Added values 8 and 9 to 
pbtBatStringStatus,
-- *                                    Corrected units in pbtBatStringVoltage 
description,
-- *                                    Added value 6 to 
pbtBatBatterySensorStatus,
-- *                                    Changed the resolution 
ofpbtBatteryVoltage to 0.01. 
-- *                                    Changed from Battery to Cell Admittance.
-- * Revised: 05/18/2006 by Mike Quelly Revised description for 
pbtBatStringCurrent and added
-- *                                    range.
-- * Revised: 12/27/2006 by Mike Quelly Added pbtBatLocation.
-- * Revised: 01/25/2007 by Mike Quelly Added value 7 to 
pbtBatBatterySensorStatus.  
-- * Revised: 01/29/2007 by Mike Quelly Changed the units of 
pbtBatMeasurementInterval from 
-- *                                    seconds to hours.
-- * Revised: 06/15/2007 by Mike Quely  Revised object descriptions.
-- * Revised: 06/20/2007 by Mike Quelly Added StringStatus state 10.
-- * Revised: 03/17/2008 by Mike Quelly Added pbtBatBatteryElectrolyteLevel. 
-- * Revised: 07/22/2008 by Mike Quelly Changed Conductance to Admittance. 
-- * Revised: 02/17/2009 by Mike Quelly Added pbtBatStringEqualizationControl. 
-- *                                    Changed Battery to Jar where 
appropriate in Object
-- *                                    names.  The OIDs were not changed. 
Other minor edits.
-- * Revised: 01/19/2010 by Mike Quelly Renamed pbtBatStringCurrent to 
pbtBatStringFloatCurrent.
-- *                                    Added pbtBatStringDischargeStatus, 
-- *                                    pbtBatStringRippleVoltage,
-- *                                    pbtBatStringJarVoltageDelta, and 
-- *                                    pbtBatStringDischargeCurrent.
-- *              
-- * Revised: 03/25/2010 by Mike Quelly Changed the max value of 
pbtBatJarNumber from 24 to 40.
-- *                                    Modified pbtBatStringFloatCurrent 
scaling from 0.1 to 0.001 Amps,
-- *                                    and range from (-1000..100) to 
(-10000..10000).
-- * Revised: 04/01/2010 by Mike Quelly Added pbtBatStringSensorComStatus, 
-- *                                    pbtBatStringDischargeEvents,
-- *                                                                    
pbtBatStringDischargeSeconds, and
-- *                                                                    
pbtBatStringDischargeSecondsTotal.
-- * Revised: 04/14/2010 by Mike Quelly Added pbtBatJarVoltageHiRes. 
-- * Revised: 09/29/2010 by Mike Quelly Added VirtualStringTable. 
-- * Revised: 09/30/2010 by Mike Quelly Added VirtualJarTable.
-- *                                    Added pbtBatJarPhysicalStringNumber and
-- *                                            pbtBatJarPhysicalJarNumber.
-- ****************************************************************************

PBT-BATTERYAGENT-MIB DEFINITIONS ::= BEGIN

IMPORTS
     OBJECT-TYPE     FROM RFC-1212
     DisplayString,DateAndTime   FROM SNMPv2-TC
     pbtBatteryAgent FROM PBT-ROOT-MIB
     
    ;

pbtBatMeasurementInterval OBJECT-TYPE
     SYNTAX INTEGER (0..32000)  
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
          "Time interval between autonomous admittance measurements, 
          in hours. Default value is 8 hours."
     ::= { pbtBatteryAgent 1 }

pbtBatStrings OBJECT-TYPE
     SYNTAX INTEGER ( 0..6 )
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Number of battery strings connected to this device."
     ::= { pbtBatteryAgent 2 }

pbtBatStringTable OBJECT-TYPE
     SYNTAX SEQUENCE OF PbtBatStringEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Table containing information about each String." 
     ::= { pbtBatteryAgent 3 }

pbtBatJarTable OBJECT-TYPE
     SYNTAX SEQUENCE OF PbtBatJarEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Table containing information about each jar (battery)." 
     ::= { pbtBatteryAgent 4 }

pbtBatLocation OBJECT-TYPE
     SYNTAX DisplayString (SIZE(32))
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
                "String describing the location.
                This object is nonvolatile as specified in the HMS MIBs.
                The default value of this object is 'Default Site Location'."
     ::= { pbtBatteryAgent 5 } 

pbtBatVirtualStringTable OBJECT-TYPE
     SYNTAX SEQUENCE OF PbtBatVirtualStringEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Table containing information about each Virtual String." 
     ::= { pbtBatteryAgent 6 }


pbtBatVirtualJarTable OBJECT-TYPE
     SYNTAX SEQUENCE OF PbtBatVirtualJarEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Table containing information about each jar (battery) 
          on a Virtual String." 
     ::= { pbtBatteryAgent 7 }


pbtBatStringEntry OBJECT-TYPE
     SYNTAX PbtBatStringEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "List of information about each String."
     INDEX { pbtBatStringNumber }
     ::= { pbtBatStringTable 1 }

PbtBatStringEntry ::=
     SEQUENCE
     {
          pbtBatStringNumber
               INTEGER,
          pbtBatStringJars
               INTEGER,
          pbtBatStringStatus
                   INTEGER,
          pbtBatStringControl
                   INTEGER,
          pbtBatStringName
               DisplayString,
          pbtBatStringVoltage
                   INTEGER,                  
          pbtBatStringFloatCurrent
                   INTEGER,                        
          pbtBatStringConnectionAdmittance
                   INTEGER,                    
          pbtBatStringEqualizationControl
               INTEGER,
          pbtBatStringJarVoltageDelta
               INTEGER,    
          pbtBatStringDischargeCurrent
               INTEGER,   
              pbtBatStringDischargeStatus
               INTEGER,
          pbtBatStringRippleCurrent
               INTEGER,
          pbtBatStringSensorComStatus
               INTEGER,
          pbtBatStringDischargeEvents                      
               INTEGER,
          pbtBatStringDischargeSeconds                             
               INTEGER,
          pbtBatStringDischargeSecondsTotal                        
               INTEGER
     }

pbtBatStringNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..6 )
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Index into the Table. Specifies the String number."
     ::= { pbtBatStringEntry 1 }

pbtBatStringJars OBJECT-TYPE
     SYNTAX INTEGER ( 1..40 )
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Number of Jars (batteries) in this string."
     ::= { pbtBatStringEntry 2 }

pbtBatStringStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),disabled(2),shorted(3),missingSensor(4),
                         tooManySensors(5),sensorFault(6),alarms(7),
                         initializing(8), sensorDisabled(9), 
stringDisconnected(10),
                         noSensorCom(11)}   
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Status of this String."
     ::= { pbtBatStringEntry 3 }
                      
pbtBatStringControl OBJECT-TYPE
     SYNTAX INTEGER {enabled(1),disabled(2)}
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
       "Control the String measurements.
        This object is nonvolatile. The default value is 1."
     ::= { pbtBatStringEntry 4 } 

                      
pbtBatStringName OBJECT-TYPE
     SYNTAX DisplayString (SIZE(32))
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
          "String describing the battery string.
           This object is nonvolatile as specified in the HMS MIBs.
           The default value of this object is 'String n'."
     ::= { pbtBatStringEntry 5 } 

pbtBatStringVoltage OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Total String Voltage.
        Units  = 0.0 Volts DC
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatStringEntry 6 }

pbtBatStringFloatCurrent OBJECT-TYPE
     SYNTAX INTEGER ( -10000..10000 )
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "String Current. Positive charge, negative discharge.
        Units = milliamps DC. 
        This object is read-write so that the management system can 
        provide the nominal current where it cannot be measured.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatStringEntry 7 }

pbtBatStringConnectionAdmittance OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "Typical connductance of the connection between the sensor and
        the battery.  Units = Mho."
     ::= { pbtBatStringEntry 8 }
                  
pbtBatStringEqualizationControl OBJECT-TYPE
     SYNTAX INTEGER     {enabled(1),disabled(2)} 
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "Enables or Disables battery equalization on this string. This
        object is nonvolatile.  The default value is disabled(2)."
     ::= { pbtBatStringEntry 9 }

pbtBatStringJarVoltageDelta OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "The difference between the highest and lowest jar voltage.
        This object is only available in the SC3 version of the 
        Site Controller.
        Units = 0.001 Volt (1 mV). 
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatStringEntry 10 }

pbtBatStringDischargeCurrent OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "String Discharge Current. 
        Units = Amps DC. 
        This object is only available in the SC3 version of the 
        Site Controller.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatStringEntry 11 }

 pbtBatStringDischargeStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),discharge(2)} 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the presence of a discharge event.  
        This object must provide for alarm management capabilities 
        with a coresponding entry in the discreteTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatStringEntry 12 }

pbtBatStringRippleCurrent OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "String AC Ripple Current. 
        Units = 0.1 AC Amps. (100 mA resolution)
        This object is only available in the SC3 version of the 
        Site Controller when the current sensor is installed.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatStringEntry 13 }

pbtBatStringSensorComStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),faultedSensor(2)} 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates that the site controller has 
        lost communications with one or more sensors on this string.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the discreteTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatStringEntry 14 }

pbtBatStringDischargeEvents OBJECT-TYPE
     SYNTAX INTEGER  
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the number of discharge events 
        that have occured.  The counter is reset by writting zero to
        this object.  Other values may not be written."  
     ::= { pbtBatStringEntry 15 }

pbtBatStringDischargeSeconds OBJECT-TYPE
     SYNTAX INTEGER  
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the duration of the present or 
        previous (if over) discharge event. 
        The counter is reset when a new discharge event begins."  
     ::= { pbtBatStringEntry 16 }

pbtBatStringDischargeSecondsTotal OBJECT-TYPE
     SYNTAX INTEGER  
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the total discharge time. 
        The counter is reset by writting zero to
        this object.  Other values may not be written."  
     ::= { pbtBatStringEntry 17 }


pbtBatJarEntry OBJECT-TYPE
     SYNTAX PbtBatJarEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "List of information about each jar (battery)."
     INDEX { pbtBatJarStringNumber, pbtBatJarNumber }
     ::= { pbtBatJarTable 1 }

PbtBatJarEntry ::=
     SEQUENCE
     {
          pbtBatJarStringNumber
                   INTEGER,  
          pbtBatJarNumber
               INTEGER,
          pbtBatJarSensorStatus
                   INTEGER,
          pbtBatJarSensorControl
                   INTEGER,
          pbtBatJarSensorLedControl
               INTEGER,    
          pbtBatJarName
                   DisplayString,
          pbtBatJarVoltage
               INTEGER,
          pbtBatJarTemperature
               INTEGER,
          pbtBatJarCellAdmittance
               INTEGER,
          pbtBatJarAdmittanceTime
                   DateAndTime,
          pbtBatJarCellInitialAdmittance
                   INTEGER,
          pbtBatJarInitialAdmittanceTime
                   DateAndTime,
          pbtBatJarCellAdmittanceChange
                   INTEGER,                  
          pbtBatJarSensorVersion
                   INTEGER,                  
          pbtBatJarElectrolyteLevel
                   INTEGER,
          pbtBatJarVoltageHiRes
               INTEGER,
          pbtBatJarPhysicalStringNumber
                   INTEGER,  
              pbtBatJarPhysicalJarNumber
               INTEGER
     }

pbtBatJarStringNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..6 )
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Index into the Table. Specifies the String number."
     ::= { pbtBatJarEntry 1 }


pbtBatJarNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..40 )
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Index into the Table. Specifies the Jar (Battery) number."
     ::= { pbtBatJarEntry 2 }

pbtBatJarSensorStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),fault(2),measuring(3),sensorDisabled(4),
                     stringDisabled(5),missing(6),measurementFailed(7)}
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "The present status of the sensor on this Jar."
     ::= { pbtBatJarEntry 3 }

pbtBatJarSensorControl OBJECT-TYPE
     SYNTAX INTEGER {enable(1),measureNow(2),disable(3),resetAdmittance(4)}
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
       "Control the admittance measurements.
          1 = Autonoumous admittance measurements on this Jar at
              the specified Interval.
          2 = Measure admittance now (ASAP), reverts to 1 after the measurement.
          3 = Admittance measurements are disabled.
          4 = Set the Jar initial admittance values and time to the present 
              admittance and time.
          This object is nonvolatile. The default value is 1."

     ::= { pbtBatJarEntry 4 } 
                      
pbtBatJarSensorLedControl OBJECT-TYPE
     SYNTAX INTEGER 
{normal(1),ledGreen(2),ledRed(3),flashGreen(4),flashRed(5),greenRed(6)}
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
          "Sensor LED Control.
          This object is nonvolatile. The default value is 1."
     ::= { pbtBatJarEntry 5 }

pbtBatJarName OBJECT-TYPE
     SYNTAX DisplayString (SIZE(32))
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
       "String describing the Jar.
           This object is nonvolatile as specified in the HMS MIBs.
           The default value of this object is 'String n, Jar m' for 
           12 volt Jars and 'String n, Cell m' for 2 volt cells."
     ::= { pbtBatJarEntry 6 } 

pbtBatJarVoltage OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Present jar voltage, Units = 0.01 Volts DC.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatJarEntry 7 }

pbtBatJarTemperature OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Present jar Temperature in degrees C.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatJarEntry 8 }

pbtBatJarCellAdmittance OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Present Cell Admittance,  in Siemens (mhos).
          For a 2V Cell CellAdmittance = JarAdmittance.
          For a 12V Jar CellAdmittance = 6 * JarAdmittance."  
     ::= { pbtBatJarEntry 9 }

pbtBatJarAdmittanceTime OBJECT-TYPE
     SYNTAX DateAndTime 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Time the admittance was measured."  
     ::= { pbtBatJarEntry 10 }

pbtBatJarCellInitialAdmittance OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
          "Initial value of the cell admittance."  
     ::= { pbtBatJarEntry 11 }

pbtBatJarInitialAdmittanceTime OBJECT-TYPE
     SYNTAX DateAndTime 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Date and time the initial admittance was recorded 
          for this jar."  
     ::= { pbtBatJarEntry 12 }

pbtBatJarCellAdmittanceChange OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Change in cell admittance in percent.  
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatJarEntry 13 }

pbtBatJarSensorVersion OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Sensor Firmware Version.  
        Encoded as 4 BCD digits in an integer.
        example; 0x0110 = version 1.10 "  
     ::= { pbtBatJarEntry 14 }

pbtBatJarElectrolyteLevel OBJECT-TYPE
     SYNTAX INTEGER {notAvailable(1),normal(2),low(3)} 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "If the electrolyte sensor is not supported by the Sensor
        this object will report notAvailable. If the electrolyte level is
        supported (Sensors with Model Numbers containing -ES) this
        object will report normal or low.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the discreteTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatJarEntry 15 }

pbtBatJarVoltageHiRes OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Present jar voltage, Units = 0.001 Volts DC.
        Use object pbtBatJarVoltage for traps."   
     ::= { pbtBatJarEntry 16 }

pbtBatJarPhysicalStringNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..6 )
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Specifies the Physical String number for this Jar.
          This is the same value as the string index and is
          included here to maintain consistency between the 
          physical jar and the virtual jar MIBS."
     ::= { pbtBatJarEntry 17 }

pbtBatJarPhysicalJarNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..40 )
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Specifies the Physical Jar number for this Jar.          
          This is the same value as the jar index and is
          included here to maintain consistency between the 
          physical jar and the virtual jar MIBS."
     ::= { pbtBatJarEntry 18 }




PbtBatVirtualStringEntry ::=
     SEQUENCE
     {
          pbtBatVirtualStringNumber
               INTEGER,
          pbtBatVirtualStringJars
               INTEGER,
          pbtBatVirtualStringStatus
                   INTEGER,
          pbtBatVirtualStringControl
                   INTEGER,
          pbtBatVirtualStringName
               DisplayString,
          pbtBatVirtualStringVoltage
                   INTEGER,                  
          pbtBatVirtualStringFloatCurrent
                   INTEGER,                        
          pbtBatVirtualStringEqualizationControl
               INTEGER,
          pbtBatVirtualStringJarVoltageDelta
               INTEGER,    
          pbtBatVirtualStringDischargeCurrent
               INTEGER,   
              pbtBatVirtualStringDischargeStatus
               INTEGER,
          pbtBatVirtualStringRippleCurrent
               INTEGER,
          pbtBatVirtualStringSensorComStatus
               INTEGER,
          pbtBatVirtualStringDischargeEvents                       
               INTEGER,
          pbtBatVirtualStringDischargeSeconds                      
               INTEGER,
          pbtBatVirtualStringDischargeSecondsTotal                         
               INTEGER,
          pbtBatVirtualJarTable                            
               SEQUENCE OF PbtBatJarEntry
     }

pbtBatVirtualStringEntry OBJECT-TYPE
     SYNTAX PbtBatVirtualStringEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "List of information about each String."
     INDEX { pbtBatVirtualStringNumber }
     ::= { pbtBatVirtualStringTable 1 }


pbtBatVirtualStringNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..6 )
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Index into the Table. Specifies the String number."
     ::= { pbtBatVirtualStringEntry 1 }

pbtBatVirtualStringJars OBJECT-TYPE
     SYNTAX INTEGER ( 1..40 )
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Number of Jars (batteries) in this string."
     ::= { pbtBatVirtualStringEntry 2 }

pbtBatVirtualStringStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),disabled(2),shorted(3),missingSensor(4),
                         tooManySensors(5),sensorFault(6),alarms(7),
                         initializing(8), sensorDisabled(9), 
stringDisconnected(10),
                         noSensorCom(11)}   
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Status of this String."
     ::= { pbtBatVirtualStringEntry 3 }
                      
pbtBatVirtualStringControl OBJECT-TYPE
     SYNTAX INTEGER {enabled(1),disabled(2)}
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
       "Control the String measurements.
        This object is nonvolatile. The default value is 1."
     ::= { pbtBatVirtualStringEntry 4 } 

                      
pbtBatVirtualStringName OBJECT-TYPE
     SYNTAX DisplayString (SIZE(32))
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
          "String describing the battery string.
           This object is nonvolatile as specified in the HMS MIBs.
           The default value of this object is 'String n'."
     ::= { pbtBatVirtualStringEntry 5 } 

pbtBatVirtualStringVoltage OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Total String Voltage.
        Units  = 0.0 Volts DC
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatVirtualStringEntry 6 }

pbtBatVirtualStringFloatCurrent OBJECT-TYPE
     SYNTAX INTEGER ( -10000..10000 )
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "String Current. Positive charge, negative discharge.
        Units = milliamps DC. 
        This object is read-write so that the management system can 
        provide the nominal current where it cannot be measured.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatVirtualStringEntry 7 }

pbtBatVirtualStringEqualizationControl OBJECT-TYPE
     SYNTAX INTEGER     {enabled(1),disabled(2)} 
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "Enables or Disables battery equalization on this string. This
        object is nonvolatile.  The default value is disabled(2)."
     ::= { pbtBatVirtualStringEntry 9 }

pbtBatVirtualStringJarVoltageDelta OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "The difference between the highest and lowest jar voltage.
        This object is only available in the SC3 version of the 
        Site Controller.
        Units = 0.001 Volt (1 mV). 
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatVirtualStringEntry 10 }

pbtBatVirtualStringDischargeCurrent OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "String Discharge Current. 
        Units = Amps DC. 
        This object is only available in the SC3 version of the 
        Site Controller.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatVirtualStringEntry 11 }

 pbtBatVirtualStringDischargeStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),discharge(2)} 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the presence of a discharge event.  
        This object must provide for alarm management capabilities 
        with a coresponding entry in the discreteTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatVirtualStringEntry 12 }

pbtBatVirtualStringRippleCurrent OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "String AC Ripple Current. 
        Units = 0.1 AC Amps. (100 mA resolution)
        This object is only available in the SC3 version of the 
        Site Controller when the current sensor is installed.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the propertyTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."
     ::= { pbtBatVirtualStringEntry 13 }

pbtBatVirtualStringSensorComStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),faultedSensor(2)} 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates that the site controller has 
        lost communications with one or more sensors on this string.
        This object must provide for alarm management capabilities 
        with a coresponding entry in the discreteTable of
        SCTE-HMS-PROPERTY-MIB (HMS026).
        An alarm shall be recorder as an entry in the currentAlarmTable
        of SCTE-HMS-PROPERTY-MIB (HMS026).
        A log record shall be added as an entry in the heCommonLogTable
        of SCTE-HMS-HE-COMMON-MIB."  
     ::= { pbtBatVirtualStringEntry 14 }

pbtBatVirtualStringDischargeEvents OBJECT-TYPE
     SYNTAX INTEGER  
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the number of discharge events 
        that have occured.  The counter is reset by writting zero to
        this object.  Other values may not be written."  
     ::= { pbtBatVirtualStringEntry 15 }

pbtBatVirtualStringDischargeSeconds OBJECT-TYPE
     SYNTAX INTEGER  
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the duration of the present or 
        previous (if over) discharge event. 
        The counter is reset when a new discharge event begins."  
     ::= { pbtBatVirtualStringEntry 16 }

pbtBatVirtualStringDischargeSecondsTotal OBJECT-TYPE
     SYNTAX INTEGER  
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
        "This object is only available in the SC3 version of the 
        Site Controller and indicates the total discharge time. 
        The counter is reset by writting zero to
        this object.  Other values may not be written."  
     ::= { pbtBatVirtualStringEntry 17 }

 
 pbtBatVirtualJarEntry OBJECT-TYPE
     SYNTAX PbtBatVirtualJarEntry
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "List of information about each jar (battery)."
     INDEX { pbtBatVirtualJarStringNumber, pbtBatVirtualJarNumber }
     ::= { pbtBatVirtualJarTable 1 }

PbtBatVirtualJarEntry ::=
     SEQUENCE
     {
          pbtBatVirtualJarStringNumber
                   INTEGER,  
              pbtBatVirtualJarNumber
               INTEGER,
          pbtBatVirtualJarSensorStatus
                   INTEGER,
          pbtBatVirtualJarSensorControl
                   INTEGER,
          pbtBatVirtualJarSensorLedControl
               INTEGER,    
          pbtBatVirtualJarName
                   DisplayString,
          pbtBatVirtualJarVoltage
               INTEGER,
          pbtBatVirtualJarTemperature
               INTEGER,
          pbtBatVirtualJarCellAdmittance
               INTEGER,
          pbtBatVirtualJarAdmittanceTime
                   DateAndTime,
          pbtBatVirtualJarCellInitialAdmittance
                   INTEGER,
          pbtBatVirtualJarInitialAdmittanceTime
                   DateAndTime,
          pbtBatVirtualJarCellAdmittanceChange
                   INTEGER,                  
          pbtBatVirtualJarSensorVersion
                   INTEGER,                  
          pbtBatVirtualJarElectrolyteLevel
                   INTEGER,
          pbtBatVirtualJarVoltageHiRes
               INTEGER,
          pbtBatVirtualJarPhysicalStringNumber
                   INTEGER,  
              pbtBatVirtualJarPhysicalJarNumber
               INTEGER
     }

pbtBatVirtualJarStringNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..3 )
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatJarStringNumber."
     ::= { pbtBatVirtualJarEntry 1 }


pbtBatVirtualJarNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..240 )
     ACCESS not-accessible
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatVirtualJarNumber."
     ::= { pbtBatVirtualJarEntry 2 }

pbtBatVirtualJarSensorStatus OBJECT-TYPE
     SYNTAX INTEGER {normal(1),fault(2),measuring(3),sensorDisabled(4),
                     stringDisabled(5),missing(6),measurementFailed(7)}
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatVirtualJarSensorStatus."
     ::= { pbtBatVirtualJarEntry 3 }

pbtBatVirtualJarSensorControl OBJECT-TYPE
     SYNTAX INTEGER {enable(1),measureNow(2),disable(3),resetAdmittance(4)}
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
       "Same as pbtBatVirtualJarSensorControl."
     ::= { pbtBatVirtualJarEntry 4 } 
                      
pbtBatVirtualJarSensorLedControl OBJECT-TYPE
     SYNTAX INTEGER 
{normal(1),ledGreen(2),ledRed(3),flashGreen(4),flashRed(5),greenRed(6)}
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatVirtualJarSensorLedControl."
     ::= { pbtBatVirtualJarEntry 5 }

pbtBatVirtualJarName OBJECT-TYPE
     SYNTAX DisplayString (SIZE(32))
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
       "Same as pbtBatVirtualJarName."
     ::= { pbtBatVirtualJarEntry 6 } 

pbtBatVirtualJarVoltage OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Same as pbtBatJarVoltage. 
        Configure the alarm using pbtBatJarVoltage."  
     ::= { pbtBatVirtualJarEntry 7 }

pbtBatVirtualJarTemperature OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatJarTemperature.
          Configure the alarm using pbtBatJarTemperature."  
     ::= { pbtBatVirtualJarEntry 8 }

pbtBatVirtualJarCellAdmittance OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatJarCellAdmittance"  
     ::= { pbtBatVirtualJarEntry 9 }

pbtBatVirtualJarAdmittanceTime OBJECT-TYPE
     SYNTAX DateAndTime 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatVirtualJarAdmittanceTime."  
     ::= { pbtBatVirtualJarEntry 10 }

pbtBatVirtualJarCellInitialAdmittance OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-write
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatJarCellInitialAdmittance."  
     ::= { pbtBatVirtualJarEntry 11 }

pbtBatVirtualJarInitialAdmittanceTime OBJECT-TYPE
     SYNTAX DateAndTime 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Same as pbtBatJarInitialAdmittanceTime."  
     ::= { pbtBatVirtualJarEntry 12 }

pbtBatVirtualJarCellAdmittanceChange OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Same as pbtBatJarCellAdmittanceChange.
        Configure the alarm using pbtBatJarCellAdmittanceChange."
     ::= { pbtBatVirtualJarEntry 13 }

pbtBatVirtualJarSensorVersion OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Same as pbtBatVirtualJarSensorVersion."
     ::= { pbtBatVirtualJarEntry 14 }

pbtBatVirtualJarElectrolyteLevel OBJECT-TYPE
     SYNTAX INTEGER {notAvailable(1),normal(2),low(3)} 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "Same as pbtBatVirtualJarElectrolyteLevel.
        Configure the alarm using pbtBatVirtualJarElectrolyteLevel."
     ::= { pbtBatVirtualJarEntry 15 }

pbtBatVirtualJarVoltageHiRes OBJECT-TYPE
     SYNTAX INTEGER 
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
        "pbtBatVirtualJarVoltageHiRes."   
     ::= { pbtBatVirtualJarEntry 16 }

pbtBatVirtualJarPhysicalStringNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..6 )
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Specifies the Physical String number for this Virtual Jar."
     ::= { pbtBatVirtualJarEntry 17 }


pbtBatVirtualJarPhysicalJarNumber OBJECT-TYPE
     SYNTAX INTEGER ( 1..40 )
     ACCESS read-only
     STATUS mandatory
     DESCRIPTION
          "Specifies the Physical Jar number for this Virtual Jar."
     ::= { pbtBatVirtualJarEntry 18 }



END