I don't think this is a power factor problem. My guess is that that the generator is "seeing" some of the switching as on-off, particularly at the lower power outputs while the batteries are topping off. The repeated intermittent "load drops" may be creating voltage spikes, "frying" the voltage regulator on the generator.
I would try wiring up a load of say 300 watts of light bulbs and put them online as a base load for the generator while it is running, so it will never see a no load situation. There will still be plenty of watts for battery charging. Oso --- In [email protected], [EMAIL PROTECTED] wrote: > > I agree with Graeme regarding the hash the switched-mode/pwm power supplies > make of many generator outputs. The caps are a appropriate solution to the > problem. If the generator is oversized by about 75-100% the generator generally > manages to overcome the problem through brute force. Thus if you are using a > 2500 watt generator to provide, say 6 amps/240V worst-case reactive power to > the charger then I think something else may be amiss as well. For instance, are > you sure you do not have other loads running at the same time? Washing machine, > fridge, pump? > > Rob > > > > > Quoting Frank Leslie <[EMAIL PROTECTED]>: > > > > > > > > > > > Graeme, > > > > > > > > Consider the difference between volt-amps that express complex power in > > > > which generators are rated. Driving a resistive load, it will supply the > > > > same number of watts of real power. A reactive load, usually inductive (like > > > > motors or transformers), will require imaginary power at phase right angles > > > > to the real power. The square root of the sum of the squares of real and > > > > reactive powers yields the complex power that the generator must supply. > > > > > > > > If the Truecharge has a low power factor, say 0.7 (1.0 is resistive), then > > > > the generator may be overloaded if it can't supply the complex power. > > > > Capacitors added in parallel with the input can restore the power factor to > > > > near 1.0. > > > > > > > > This is just a guess, as I don't know what the Xantrex power factor value > > > > is. These are sharp guys -- ask them. > > > > > > > > Frank > > > > -----Original Message----- > > > > From: [email protected] [mailto:[EMAIL PROTECTED] > > > > Behalf Of Graeme > > > > Sent: Thursday, December 01, 2005 11:38 PM > > > > To: [email protected] > > > > Subject: [microhydro] petrol generator problem - low voltage > > > > > > > > > > > > I am setting up my micro hydro system. Until I get the generator installed > > > > at > > > > the waterfall and the transmission line in place I am using petrol > > > > generators > > > > to provide power to charge the batteries. > > > > > > > > The only load on the generator is a Xantrex Truecharge 40i+ > > > > > > > > So far I have had a Scorpian DY2500L replaced and the replecement repaired > > > > because of low output voltage (ie less than 200v instead of 230v). I also > > > > have > > > > two GMC 850W units that have the same problem. > > > > > > > > I have contacted Xantrex asking if the Truecharge puts a strange load on > > > > the > > > > generator but they didn't answer the question. > > > > > > > > I can keep having petrol generators replaced / repaired while under > > > > warrenty > > > > but I need to know the likely fault and how to prevent it. > > > > > > > > I do not want to have my hydro generator fail as it is not convienient to > > > > pull > > > > out. > > > > > > > > If any-one has suggestions on likely cause and how to prevent it please > > > > let me > > > > know. > > > > > > > > Cheers > > > > Graeme > > > > > > > > > > > > > > > > ____________________________________________________ > > > > Do you Yahoo!? > > > > Never miss an Instant Message - Yahoo! Messenger for SMS > > > > http://au.mobile.yahoo.com/mweb/index.html > > > > > > > > > > > > > > > > > > > > Does your company feature in the microhydro business directory at > > > > http://microhydropower.net/directory ? If not, please register free of > > > > charge and be exposed to the microhydro community world wide! > > > > > > > > NOTE: The advertisements in this email are added by Yahoogroups who > > > > provides us with free email group services. The microhydro-group does not > > > > endorse products or support the advertisements in any way. > > > > > > > > More information on micro hydropower at http://microhydropower.net > > > > > > > > To unsubscribe: send empty message to > > > > [EMAIL PROTECTED] > > > > > > > > > > > > > > > > ------------------------------------------------------------------ ---------- > > > > -- > > > > YAHOO! GROUPS LINKS > > > > > > > > a.. Visit your group "microhydro" on the web. > > > > > > > > b.. To unsubscribe from this group, send an email to: > > > > [EMAIL PROTECTED] > > > > > > > > c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of > > > > Service. > > > > > > > > > > > > ------------------------------------------------------------------ ---------- > > > > -- > > > > > > > > > > > > > > > > [Non-text portions of this message have been removed] > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Does your company feature in the microhydro business directory at > > http://microhydropower.net/directory ? If not, please register free of charge > > and be exposed to the microhydro community world wide! > > > > > > > > NOTE: The advertisements in this email are added by Yahoogroups who provides > > us with free email group services. The microhydro-group does not endorse > > products or support the advertisements in any way. > > > > > > > > More information on micro hydropower at http://microhydropower.net > > > > > > > > To unsubscribe: send empty message to [EMAIL PROTECTED] > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > SPONSORED LINKS > > > > > > > > > > Energy management > > > > > > Energy gels > > > > > > Energy conservation home > > > > > > > > > > Energy savings > > > > > > Energy > > > > > > Energy efficiency > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > YAHOO! GROUPS LINKS > > > > > > > > > > Visit your group "microhydro" on the web. > > > > To unsubscribe from this group, send an email to: > > [EMAIL PROTECTED] > > > > Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > ------------------------ Yahoo! Groups Sponsor --------------------~--> Get fast access to your favorite Yahoo! Groups. Make Yahoo! your home page http://us.click.yahoo.com/dpRU5A/wUILAA/yQLSAA/FGYolB/TM --------------------------------------------------------------------~-> Does your company feature in the microhydro business directory at http://microhydropower.net/directory ? If not, please register free of charge and be exposed to the microhydro community world wide! NOTE: The advertisements in this email are added by Yahoogroups who provides us with free email group services. The microhydro-group does not endorse products or support the advertisements in any way. More information on micro hydropower at http://microhydropower.net To unsubscribe: send empty message to [EMAIL PROTECTED] Yahoo! Groups Links <*> To visit your group on the web, go to: http://groups.yahoo.com/group/microhydro/ <*> To unsubscribe from this group, send an email to: [EMAIL PROTECTED] <*> Your use of Yahoo! Groups is subject to: http://docs.yahoo.com/info/terms/