On Mon, Dec 8, 2014 at 3:45 PM, David Higgs <hig...@gmail.com> wrote:
> On Mon, Dec 8, 2014 at 3:37 PM, trondd <tro...@gmail.com> wrote:
>> On Mon, Dec 8, 2014 at 3:23 PM, trondd <tro...@gmail.com> wrote:
>>> On Mon, Dec 8, 2014 at 11:47 AM, David Higgs <hig...@gmail.com> wrote:
>>>>
>>>>
>>>> sysctl(8) will display Off if the value is zero, and On for nonzero.
>>>> So, using the "closed interval" rule above, you should use "high=0"
>>>> for indicators that you consider in "good" state when Off (i.e.
>>>> ShutdownImminent), and "low=1" for indicators that you consider in
>>>> "good" state when On (i.e. ACPresent).
>>>>
>>>
>>> Isn't saying high=0 kind of the same thing as saying low=1?
>>
>>
>> Oh, I think I get this.  Since the sensor doesn't trigger if it is on the
>> limit, only outside the limit, you have to set up which is the OK state.
>>
>> Still a little confusing but I guess there is no way to automatically know
>> if an indicator is supposed to be Off or On when it's in it's good state?
>>
>
> Kind of.  The high/low difference is what values you consider "within"
> normal operating parameters (and the output of %l).  The upd(4) code
> hasn't yet been taught how to map specific indicator values to OK /
> WARN / CRITICAL status.  Currently any value successfully read is
> marked OK.
>
> I'm working with tech@ and slowly writing diffs to improve these things.
>
> --david

Resurrecting an old thread since I just ran into the same problem in
5.8. To summarize, upd(4) exposes some SENSOR_INDICATOR-type sensors
for attached UPSes, such as ACPresent = On/Off, and it's not clear how
to configure sensorsd(8) to execute a command when this value changes.
Also, upd always sets sensor status to "OK," so sensorsd never
triggers commands for status changes; we have to use low/high limits
until this is fixed. One proposed hack was to use "low=1:high=2" in
sensorsd.conf, but this doesn't seem to work for everybody.

Has anyone tried using "low=0:high=0"? I'm pretty sure that should
solve the problem in all cases.

The low/high range is inclusive at both ends. Off is 0, but On can be
any other int64 value, including negative. For my UPS, ACPresent = On
is actually a value of -1. I know this because when I set
"low=-1:high=-1" sensorsd reports "upd0.indicator2: within limits:
On". That being the case, "low=1:high=2" would not work because the
value changes from -1 (On) to 0 (Off), and is always below the lower
limit.

Using "low=0:high=0" should always work for On -> Off -> On
transitions, but it will show On as outside (below or above) the
limits. If you want On to be within limits, then just play with the
values until you figure out whether On is 1, -1, or something else
entirely. That may not be as reliable. I'm not actually sure whether
this value is UPS-specific or something that upd determines.

-Max