Alex's point is that 5x density does not mean that the infrastructure costs are less than 5x. At a certain point in time there is a rate of return lower than 1.
We're so stuck thinking that costs are primarily related to square feet, but with powering and cooling costs being the primary factors, we may be better off thinking in terms of costs in relation to amps. Frank -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Robert Boyle Sent: Saturday, March 29, 2008 10:29 PM To: Alex Pilosov; Paul Vixie Cc: nanog@merit.edu Subject: Re: cooling door <snip> I don't disagree with what you have written above, but if you can get 100A into all 5 racks (and cool it!), then you have five times the revenue with the same fixed infrastructure costs (with the exception of a bit more power, GenSet, UPS and cooling, but the rest of my costs stay the same.) >To rephrase vijay, "what is the problem being solved"? For us in our datacenters, the problem being solved is getting as much return out of our investment as possible. -Robert Tellurian Networks - Global Hosting Solutions Since 1995 http://www.tellurian.com | 888-TELLURIAN | 973-300-9211 "Well done is better than well said." - Benjamin Franklin