Forgive if this is duplicate.  Too many posts in the various forks of
this thread to dig through them all.

http://www.troxaitcs.com/aitcs/products/co2_mcc/index.jsp
http://www.modbs.co.uk/news/fullstory.php/aid/1735/The_next_generation_of_cooling__for_computer_rooms.html

"CO2 has the additional benefit that should a leak occur, it is
electrically benign. Imagine the consequences of a leak of water or
refrigerant. While a leak of CO2 could be a health-and-safety hazard,
the risk is minimised by CO2 detection as part of the system."

> On Thu, Apr 3, 2008 at 11:58 PM, Patrick Giagnocavo <[EMAIL PROTECTED]> wrote:
>
> >
> > First, I would like to thank everyone who responded to my initial query.
> >
> > It seems that power and how to remove the resulting heat, is certainly on a 
> > lot of people's minds.
> >
> > Clearly the days of "including" power are past in all but sales and 
> > marketing materials.
> >
> > There is a cost to each component and markup is applied (if internally and 
> > not broken out to the customer) on each rack, each power circuit, etc. with 
> > covering the overhead of UPS, diesel generator, chillers, etc.  being a big 
> > priority.
> >
> > After some thought, I believe, to coin a term, that "DHR" or direct heat 
> > removal, in some fashion will be the "new" thing for the datacenter.
> >
> > Somewhat counter-intuitively, the focus will be to remove the heat that 
> > comes out the back of the rack rather than worrying so much about the 
> > temperature of the air going in the front as long as it falls in a 
> > generally acceptable range of say, 68-75F.
> >
> > My guess is that someone will come up with an inexpensive, reliable way to 
> > put a heat collector, which will basically look like a car radiator the 
> > size of a rear rack door, directly behind the hot air coming from the 
> > systems in the rack.
> >
> > Hot air flows past the cooling fins and is quickly cooled back to 68F; the 
> > heated refrigerant is immediately piped away, out of the room and to the 
> > chiller, so that the evil BTUs do not spread out and contaminate other 
> > areas of the room.
> >
> > It might involve a phase change material, or might involve a more 
> > traditional refrigerant.
> >
> > My money would be on R744, also known as CO2, as it is not polluting and 
> > can serve double duty as fire suppression (provided you have enough on hand 
> > to flood the area/room).
> >
> > Detectors for leaks are very inexpensive and the technology  for the 
> > closed-loop of the refrigerant cycle is already here.
> >
> > It is not caustic the way any of the salts-based variants would be, is not 
> > explosive, and is heavier than regular air, meaning it will sink below the 
> > area that most people breathe at should there be a small leak.
> >
> > With the heat being removed within a few inches of where it is generated, 
> > less CRAC units will be needed to keep the rest of the air cooled; and 
> > possibly, no separate unit would be needed if enough heat can be removed to 
> > drop the temperature below 68F.
> >
> > For fire suppression, an alarm would sound and only when it can in some 
> > fashion be "proven" that no humans are inside the area, CO2 is flooded into 
> > the area and the fire goes out.  Some form of ducting which mixes the CO2 
> > with regular air and exhausts it is needed after the fire is out.  Firemen 
> > go in with oxygen if they need to enter before this is done.  (obviously 
> > there would be an entire tested procedure for how this is done, probably 
> > including a small oxygen mask with ~4 minutes of O2 placed beside each fire 
> > extinguisher and within easy reach).
> >
> > (For racks with less than say 4KW of power use, network and power is fed 
> > from overhead with a few feet of slack in the cables, as well as a portion 
> > of the DHR piping being flexible tubing.  This allows them to be  placed 
> > more closely together than normal, almost front to back to front to back, 
> > with enough slack to pulled the wheeled racks "out" from the stack so it 
> > can be worked on (sort of like pulling a book out of a bookshelf). They use 
> > far less space and are sold a little cheaper by the colo facility.)
> >
> > Surely there is a limit as to how much air can be moved around, even with 
> > the use of best practices, there are hot spots.
> >
> > Simple physics dictates that this is a less energy intensive cooling method 
> > as a) moving a lot of air around requires a lot of energy b) air is a lousy 
> > way to transfer heat away from where you want it to be compared to other 
> > materials.
> >
> > Cordially
> >
> > Patrick Giagnocavo
> > [EMAIL PROTECTED]
> >
>
>