Hello, I have completed and tested a new generic modbus driver for UPS devices with contact signaling. I have also posted the corresponding pull request:
(https://github.com/networkupstools/nut/pull/1052) kind regards, Dimitris Economou --- This is a generic modbus driver expected to work with contact (direct) signal UPS devices, connected via modbus RIO (remote I/O) either serial or TCP/IP. The driver has been tested against PULS UPS (model UB40.241) via MOXA ioLogikR1212 (RS485) and ioLogikE1212 (TCP/IP). The PULS UPS UB40.241 supports the following signals: Ready contact (DO) <--> HB Buffering contact (DO) <--> OL | OB Battery-low (DO) <--> LB Replace Battery (DO) <--> RB Inhibit (DI) <--> FSD DO and DI assumes device perspective The driver's concept is to map the UPS states (as defined in nut) onto UPS contacts' states The driver has an extended configuration interface implemented using variables defined in ups.conf. [generic_modbus] # info parameters driver = generic_modbus port = /dev/ttyUSB0 # port = 192.168.2.104 # port = 192.168.2.104:1502 desc = "generic ups driver" # device info device_mfr = "PULS" device_model = "UB40.241" # serial settings ser_baud_rate = 9600 ser_parity = N ser_data_bit = 8 ser_stop_bit = 1 modbus slave id rio_slave_id = 5 # UPS signal state attributes OB_addr = 0x0 OB_regtype = 1 OB_noro = 0 LB_addr = 0x1 LB_regtype = 1 HB_addr = 0x2 HB_regtype = 1 RB_addr = 0x3 RB_regtype = 1 # CHRG_addr = 0x0 # CHRG_regtype = 1 # CHRG_noro = 1 DISCHRG_addr = 0x0 DISCHRG_regtype = 1 DISCHRG_noro = 0 FSD_addr = 0x140 FSD_regtype = 0 FSD_pulse_duration = 180 *XXX_addr* denotes the modbus address of RIO where the XXX UPS signal is connected *XXX_regtype* is the type of modbus register (0:COIL, 1:INPUT_B, 2:INPUT_R, 3:HOLDING) *XXX_noro* is the configuration for NO/NC (normally open, normally closed contact) *FSD_pulse_duration* defines the duration in ms of the inhibit pulse. if it's not defined, the signal has only one transition depending on noro configuration.
_______________________________________________ Nut-upsdev mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev