Hi,
I tried all commands on
https://github.com/networkupstools/nut/wiki/Building-NUT-for-in%E2%80%90place-upgrades-or-non%E2%80%90disruptive-tests
but i don't know what i'm supposed to do next, it seams to download some
things on my /tmp/nut/ but i don't know what is it.
My kernel is Linux 5.4.0-162-generic x86_64 and i don't have
huawei-ups2000 driver.
I have "/lib/nut$ ls
al175 blazer_usb metasys riello_ser
apcsmart clone mge-shut riello_usb
apcsmart-old clone-outlet mge-utalk safenet
apcupsd-ups dummy-ups microdowell solis
bcmxcp etapro nutdrv_atcl_usb tripplite
bcmxcp_usb everups nutdrv_qx tripplitesu
belkin gamatronic oldmge-shut tripplite_usb
belkinunv genericups oneac upscode2
bestfcom isbmex optiups upsd
bestfortress ivtscd powercom upsmon
bestuferrups liebert powerpanel usbhid-ups
bestups liebert-esp2 rhino victronups
blazer_ser masterguard richcomm_usb
"
My lsusb is showing "Bus 001 Device 008: ID 04e2:1410 Exar Corp.
XR21V1410 USB-UART IC"
And i don't know what to do next.
Fatgear
Le 13/09/2023 à 23:13, [email protected] a écrit :
Send Nut-upsdev mailing list submissions to
[email protected]
To subscribe or unsubscribe via the World Wide Web, visit
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev
or, via email, send a message with subject or body 'help' to
[email protected]
You can reach the person managing the list at
[email protected]
When replying, please edit your Subject line so it is more specific
than "Re: Contents of Nut-upsdev digest..."
Today's Topics:
1. Re: [Nut-upsuser] PR to test for users of Qx devices (blazer
and nutdrv_qx) (d tbsky)
----------------------------------------------------------------------
Message: 1
Date: Wed, 13 Sep 2023 21:26:16 +0800
From: d tbsky <[email protected]>
To: Jim Klimov <[email protected]>
Cc: nut-upsuser Mailing List <[email protected]>,
nut-upsdev <[email protected]>
Subject: Re: [Nut-upsdev] [Nut-upsuser] PR to test for users of Qx
devices (blazer and nutdrv_qx)
Message-ID:
<CAC6SzHJ3KO80Fb0Bb46cErJYO+7ogpuL84o6mc0=punhnez...@mail.gmail.com>
Content-Type: text/plain; charset="UTF-8"
jim Klimov <[email protected]>
Hello all,
Had another hard look at the PR for QX device voltage/charge/runtime fixes
for some broken use-cases (AND hoping to not introduce problems for cases that
were not broken), and hopefully found and rolled back the change which in fact
introduced the strangeness found in our winter round of tests. Then the year
was busy...
As before, the context for this is:
* issue https://github.com/networkupstools/nut/issues/1279
* PR https://github.com/networkupstools/nut/pull/1652
* PR source git branch (code to build for tests)
https://github.com/jimklimov/nut/tree/issue-1279
*
https://github.com/networkupstools/nut/wiki/Building-NUT-for-in%E2%80%90place-upgrades-or-non%E2%80%90disruptive-tests
suggests how to quickly build and
Hi:
one of our voltronic ups caught fire last year. so we abandoned
them and bought APC. now I have only one 10KV ups to test. It's sad
because I like nutdrv_qx driver. APC microlink is too bad since nut
doesn't support it. there is only modbus with apcupsd driver.
BTW I saw an APC ups discussion at nut-upsdev about "SRVS1KI"(can
not reply, not subscribed to that list) . I have that easy-ups series.
nut can support them well with apcsmart driver. normally we should
attach it via serial cable. if you attach the ups with usb cable, you
will see "XR21V1410" which is a usb-serial converter. linux kernel
5.15 seems include the driver. or you will need to compile the
driver(xr_usb_serial_common) yourself and get "/dev/ttyXRUSB0" to use
as an serial port. I do that because we lost serial cable at a remote
site and forced to use the usb cable.
./nutdrv_qx -a ftups -u root -DDDDDD -d1
Network UPS Tools - Generic Q* USB/Serial driver 0.35 (2.8.0-2359-g6c0032e52)
USB communication driver (libusb 1.0) 0.45
0.000000 [D1] Network UPS Tools version 2.8.0-2359-g6c0032e52
(release/snapshot of 2.8.0.1) built with gcc (GCC) 11.3.1 20221121
(Red Hat 11.3.1-4) and configured with flags: --enable-Wcolor
--enable-keep_nut_report_featu
re --with-all=auto --with-cgi=auto
--with-serial=auto --with-dev=auto --with-doc=skip
--with-nut_monitor=auto --with-pynut=auto
--disable-force-nut-version-header --enable-check-NIT
--enable-maintainer-mode
0.000011 [D1] debug level is '6'
0.000014 [D5] send_to_all: SETINFO driver.debug "6"
0.000018 [D5] send_to_all: SETFLAGS driver.debug RW NUMBER
0.000815 [D1] Succeeded to become_user(root): now UID=0 GID=0
0.000822 [D5] send_to_all: SETINFO device.type "ups"
0.000825 [D5] send_to_all: SETINFO driver.state "init.device"
0.000827 [D1] upsdrv_initups...
0.003147 [D2] Checking device 1 of 11 (8087/8000)
0.057855 [D2] - VendorID: 8087
0.057861 [D2] - ProductID: 8000
0.057862 [D2] - Manufacturer: unknown
0.057864 [D2] - Product: unknown
0.057865 [D2] - Serial Number: unknown
0.057867 [D2] - Bus: 002
0.057868 [D2] - Device: 002
0.057870 [D2] - Device release number: 0005
0.057873 [D2] Trying to match device
0.057875 [D3] match_function_regex: matching a device...
0.057888 [D2] Device does not match - skipping
0.071830 [D2] Checking device 2 of 11 (1D6B/0002)
0.078881 [D2] - VendorID: 1d6b
0.078885 [D2] - ProductID: 0002
0.078887 [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64
ehci_hcd
0.078888 [D2] - Product: EHCI Host Controller
0.078890 [D2] - Serial Number: 0000:00:1d.0
0.078891 [D2] - Bus: 002
0.078893 [D2] - Device: 001
0.078894 [D2] - Device release number: 0514
0.078897 [D2] Trying to match device
0.078898 [D3] match_function_regex: matching a device...
0.078912 [D2] Device does not match - skipping
0.091359 [D2] Checking device 3 of 11 (8087/8008)
0.145626 [D2] - VendorID: 8087
0.145635 [D2] - ProductID: 8008
0.145637 [D2] - Manufacturer: unknown
0.145638 [D2] - Product: unknown
0.145640 [D2] - Serial Number: unknown
0.145641 [D2] - Bus: 001
0.145643 [D2] - Device: 002
0.145645 [D2] - Device release number: 0005
0.145648 [D2] Trying to match device
0.145661 [D3] match_function_regex: matching a device...
0.145664 [D2] Device does not match - skipping
0.159837 [D2] Checking device 4 of 11 (1D6B/0002)
0.166862 [D2] - VendorID: 1d6b
0.166867 [D2] - ProductID: 0002
0.166868 [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64
ehci_hcd
0.166870 [D2] - Product: EHCI Host Controller
0.166871 [D2] - Serial Number: 0000:00:1a.0
0.166873 [D2] - Bus: 001
0.166874 [D2] - Device: 001
0.166876 [D2] - Device release number: 0514
0.166878 [D2] Trying to match device
0.166880 [D3] match_function_regex: matching a device...
0.166894 [D2] Device does not match - skipping
0.179366 [D2] Checking device 5 of 11 (1D6B/0003)
0.200847 [D2] - VendorID: 1d6b
0.200851 [D2] - ProductID: 0003
0.200853 [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64
xhci-hcd
0.200854 [D2] - Product: xHCI Host Controller
0.200856 [D2] - Serial Number: 0000:00:14.0
0.200857 [D2] - Bus: 004
0.200858 [D2] - Device: 001
0.200860 [D2] - Device release number: 0514
0.200862 [D2] Trying to match device
0.200864 [D3] match_function_regex: matching a device...
0.200877 [D2] Device does not match - skipping
0.200931 [D2] Checking device 6 of 11 (9966/0202)
0.202237 [D2] - VendorID: 9966
0.202254 [D2] - ProductID: 0202
0.202256 [D2] - Manufacturer: PSTEK
0.202268 [D2] - Product: PSTEK Combo KVM 8/16 V:2.00
0.202269 [D2] - Serial Number: unknown
0.202271 [D2] - Bus: 003
0.202272 [D2] - Device: 003
0.202274 [D2] - Device release number: 0000
0.202275 [D2] Trying to match device
0.202276 [D3] match_function_regex: matching a device...
0.202279 [D2] Device does not match - skipping
0.202300 [D2] Checking device 7 of 11 (0557/2419)
0.202309 [D2] - VendorID: 0557
0.202327 [D2] - ProductID: 2419
0.202329 [D2] - Manufacturer: unknown
0.202331 [D2] - Product: unknown
0.202334 [D2] - Serial Number: unknown
0.202346 [D2] - Bus: 003
0.202348 [D2] - Device: 004
0.202350 [D2] - Device release number: 0100
0.202353 [D2] Trying to match device
0.202365 [D3] match_function_regex: matching a device...
0.202367 [D2] Device does not match - skipping
0.202371 [D2] Checking device 8 of 11 (0557/7000)
0.202377 [D2] - VendorID: 0557
0.202379 [D2] - ProductID: 7000
0.202380 [D2] - Manufacturer: unknown
0.202382 [D2] - Product: unknown
0.202384 [D2] - Serial Number: unknown
0.202386 [D2] - Bus: 003
0.202389 [D2] - Device: 002
0.202391 [D2] - Device release number: 0000
0.202393 [D2] Trying to match device
0.202395 [D3] match_function_regex: matching a device...
0.202398 [D2] Device does not match - skipping
0.202402 [D2] Checking device 9 of 11 (0665/5161)
0.204923 [D1] nut_libusb_open get iManufacturer failed, retrying...
0.207280 [D1] nut_libusb_open get iManufacturer failed, retrying...
0.209669 [D1] nut_libusb_open get iManufacturer failed, retrying...
0.212022 [D1] nut_libusb_open get iProduct failed, retrying...
0.214338 [D1] nut_libusb_open get iProduct failed, retrying...
0.216830 [D1] nut_libusb_open get iProduct failed, retrying...
0.216846 [D2] - VendorID: 0665
0.216847 [D2] - ProductID: 5161
0.216849 [D2] - Manufacturer: unknown
0.216850 [D2] - Product: unknown
0.216852 [D2] - Serial Number: unknown
0.216864 [D2] - Bus: 003
0.216866 [D2] - Device: 006
0.216868 [D2] - Device release number: 0001
0.216870 [D2] Trying to match device
0.216872 [D3] match_function_regex: matching a device...
0.216885 [D2] Device matches
0.216886 [D2] Reading first configuration descriptor
0.216896 [D3] libusb_kernel_driver_active() returned 0: Success
0.216926 [D2] Claimed interface 0 successfully
0.216929 [D3] nut_usb_set_altinterface: skipped
libusb_set_interface_alt_setting(udev, 0, 0)
0.216946 [D5] send_to_all: SETINFO ups.vendorid "0665"
0.216950 [D5] send_to_all: SETINFO ups.productid "5161"
0.218318 [D3] send: QGS
0.278886 [D5] read [ 0]: (8 bytes) => 28 32 32 31 2e 33 20 35
0.310887 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 39 2e
0.342884 [D5] read [ 16]: (8 bytes) => 35 20 35 39 2e 39 20 30
0.382879 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
0.414887 [D5] read [ 32]: (8 bytes) => 20 33 36 32 2e 33 20 33
0.454888 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
0.486869 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
0.518892 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
0.558896 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
0.574889 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
0.574909 [D3] read: (221.3 59.9 219.5 59.9 002.8 007 362.3
361.8 272.9 ---.- 022.9 100000000010
0.574928 [D5] send_to_all: SETINFO input.voltage "221.3"
0.576176 [D3] send: QPI
0.622874 [D5] read [ 0]: (8 bytes) => 28 50 49 30 32 0d 00 00
0.622880 [D3] read: (PI02
0.622937 [D5] send_to_all: SETINFO ups.firmware.aux "P02"
0.622940 Using protocol: Voltronic 0.08
0.622942 [D5] send_to_all: SETINFO driver.state "init.quiet"
0.622956 [D5] send_to_all: SETINFO driver.version
"2.8.0-2359-g6c0032e52"
0.622959 [D5] send_to_all: SETINFO driver.version.internal "0.35"
0.622963 [D5] send_to_all: SETINFO driver.name "nutdrv_qx"
0.622965 [D5] send_to_all: SETINFO driver.state "init.info"
0.622967 [D1] upsdrv_initinfo...
0.622980 [D5] send_to_all: SETINFO driver.version.data "Voltronic 0.08"
0.624104 [D3] send: QRI
0.678874 [D5] read [ 0]: (8 bytes) => 28 32 32 30 2e 30 20 30
0.718855 [D5] read [ 8]: (8 bytes) => 34 35 20 32 34 30 2e 30
0.742898 [D5] read [ 16]: (8 bytes) => 20 36 30 2e 30 0d 00 00
0.742910 [D3] read: (220.0 045 240.0 60.0
0.742946 [D5] send_to_all: SETINFO output.voltage.nominal "220.0"
0.742952 [D5] send_to_all: SETINFO output.current.nominal "45"
0.742958 [D5] send_to_all: SETINFO battery.voltage.nominal "240.0"
0.742964 [D5] send_to_all: SETINFO output.frequency.nominal "60.0"
0.744242 [D3] send: QMD
0.798887 [D5] read [ 0]: (8 bytes) => 28 23 23 23 23 23 23 23
0.838882 [D5] read [ 8]: (8 bytes) => 23 23 23 23 47 31 30 4b
0.870886 [D5] read [ 16]: (8 bytes) => 20 23 23 31 30 30 30 30
0.910884 [D5] read [ 24]: (8 bytes) => 20 38 30 20 31 2f 31 20
0.942903 [D5] read [ 32]: (8 bytes) => 32 33 30 20 32 33 30 20
0.974868 [D5] read [ 40]: (8 bytes) => 32 30 20 31 32 2e 30 0d
0.974873 [D3] read: (###########G10K ##10000 80 1/1 230 230 20 12.0
0.974882 [D5] send_to_all: SETINFO device.model "G10K"
0.974887 [D5] send_to_all: SETINFO ups.power.nominal "10000"
0.974893 [D5] send_to_all: SETINFO output.powerfactor "0.8"
0.974903 [D5] send_to_all: SETINFO input.phases "1"
0.974907 [D5] send_to_all: SETINFO output.phases "1"
0.974911 [D5] send_to_all: SETINFO input.voltage.nominal "230.0"
0.976111 [D3] send: F
1.022870 [D5] read [ 0]: (8 bytes) => 23 32 32 30 2e 30 20 30
1.062876 [D5] read [ 8]: (8 bytes) => 34 35 20 32 34 30 2e 30
1.086867 [D5] read [ 16]: (8 bytes) => 20 36 30 2e 30 0d 00 00
1.086872 [D3] read: #220.0 045 240.0 60.0
1.086881 [D5] send_to_all: SETINFO input.current.nominal "45.0"
1.086901 [D5] send_to_all: SETINFO input.frequency.nominal "60.0"
1.088234 [D3] send: QMF
1.134884 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
1.134903 [D3] read: (NAK
1.134905 [D2] qx_process_answer: query rejected by the UPS (device.mfr)
1.136185 [D3] send: QVFW
1.198873 [D5] read [ 0]: (8 bytes) => 28 56 45 52 46 57 3a 30
1.230865 [D5] read [ 8]: (8 bytes) => 30 30 37 37 2e 31 33 0d
1.230870 [D3] read: (VERFW:00077.13
1.230874 [D5] send_to_all: SETINFO ups.firmware "00077.13"
1.232171 [D3] send: QID
1.278886 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
1.278896 [D3] read: (NAK
1.278909 [D2] qx_process_answer: query rejected by the UPS
(device.serial)
1.280047 [D3] send: I
1.326866 [D5] read [ 0]: (8 bytes) => 20 20 20 20 20 20 20 20
1.334901 [D5] read [ 8]: (8 bytes) => 0d 00 00 00 00 00 00 00
1.334906 [D3] read:
1.334908 [D2] qx_process_answer: short reply (device.mfr)
1.336115 [D3] send: QGS
1.390871 [D5] read [ 0]: (8 bytes) => 28 32 31 39 2e 35 20 35
1.430868 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 32 30 2e
1.462877 [D5] read [ 16]: (8 bytes) => 34 20 36 30 2e 30 20 30
1.502865 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
1.534867 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
1.566867 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
1.606862 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
1.638861 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
1.678883 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
1.694864 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
1.694884 [D3] read: (219.5 59.9 220.4 60.0 002.8 007 361.8
361.8 272.9 ---.- 022.9 100000000010
1.694914 [D5] send_to_all: SETINFO input.frequency "59.9"
1.694921 [D5] send_to_all: SETINFO output.voltage "220.4"
1.694926 [D5] send_to_all: SETINFO output.frequency "60.0"
1.694932 [D5] send_to_all: SETINFO output.current "2.8"
1.694936 [D5] send_to_all: SETINFO ups.load "7"
1.694940 [D5] send_to_all: SETINFO battery.voltage "272.9"
1.694945 [D5] send_to_all: SETINFO ups.temperature "22.9"
1.694962 [D5] send_to_all: SETINFO ups.type "online"
1.694967 [D5] update_status: OL
1.694970 [D5] update_status: !LB
1.694988 [D5] update_status: !CAL
1.695003 [D5] update_status: !FSD
1.695007 [D5] send_to_all: SETINFO ups.beeper.status "enabled"
1.696295 [D3] send: QMOD
1.734859 [D5] read [ 0]: (8 bytes) => 28 4c 0d 00 00 00 00 00
1.734878 [D3] read: (L
1.734891 [D5] update_status: OL
1.736229 [D3] send: QWS
1.790912 [D5] read [ 0]: (8 bytes) => 28 30 30 30 30 30 30 30
1.830878 [D5] read [ 8]: (8 bytes) => 30 30 30 30 30 30 30 30
1.862874 [D5] read [ 16]: (8 bytes) => 30 30 30 30 30 30 30 30
1.894869 [D5] read [ 24]: (8 bytes) => 30 30 30 30 30 30 30 30
1.934865 [D5] read [ 32]: (8 bytes) => 30 30 30 30 30 30 30 30
1.966853 [D5] read [ 40]: (8 bytes) => 30 30 30 30 30 30 30 30
2.006871 [D5] read [ 48]: (8 bytes) => 30 30 30 30 30 30 30 30
2.038858 [D5] read [ 56]: (8 bytes) => 30 30 30 30 30 30 30 30
2.046851 [D5] read [ 64]: (8 bytes) => 30 0d 30 30 30 30 30 30
2.046870 [D3] read:
(0000000000000000000000000000000000000000000000000000000000000000
2.048166 [D3] send: QBV
2.102862 [D5] read [ 0]: (8 bytes) => 28 32 37 33 2e 32 20 32
2.142871 [D5] read [ 8]: (8 bytes) => 30 20 30 31 20 31 30 30
2.158875 [D5] read [ 16]: (8 bytes) => 20 30 31 30 0d 00 00 00
2.158880 [D3] read: (273.2 20 01 100 010
2.158886 battery_number: 20
2.158895 battery_number, settable range: 1..9
2.158904 [D5] send_to_all: SETINFO battery.packs "1"
2.158907 [D5] send_to_all: SETFLAGS battery.packs RW
2.158911 [D5] send_to_all: ADDRANGE battery.packs 1 99
2.158914 [D5] send_to_all: SETFLAGS battery.packs RW NUMBER
2.158919 [D5] send_to_all: SETINFO battery.charge "100"
2.158924 [D5] send_to_all: SETINFO battery.runtime "600"
2.160228 [D3] send: QLDL
2.206859 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
2.206874 [D3] read: (NAK
2.206880 [D2] qx_process_answer: query rejected by the UPS
(output.power.minimum.percent)
2.206894 [D2] qx_process_answer: query rejected by the UPS
(output.power.maximum.percent)
2.208167 [D3] send: QFLAG
2.270872 [D5] read [ 0]: (8 bytes) => 28 45 70 62 72 61 73 64
2.310890 [D5] read [ 8]: (8 bytes) => 74 69 44 6f 76 65 66 6a
2.318849 [D5] read [ 16]: (8 bytes) => 6d 0d 00 00 00 00 00 00
2.318867 [D3] read: (EpbrasdtiDovefjm
2.318910 [D5] send_to_all: SETINFO ups.start.auto "yes"
2.318915 [D5] send_to_all: SETFLAGS ups.start.auto RW
2.318928 [D5] send_to_all: ADDENUM ups.start.auto "no"
2.318930 [D5] send_to_all: ADDENUM ups.start.auto "yes"
2.318945 [D5] send_to_all: SETINFO battery.protection "yes"
2.318948 [D5] send_to_all: SETFLAGS battery.protection RW
2.318951 [D5] send_to_all: ADDENUM battery.protection "no"
2.318964 [D5] send_to_all: ADDENUM battery.protection "yes"
2.318969 [D4] ups_infoval_set: failed to preprocess value
[battery.energysave: EpbrasdtiDovefjm]
2.318973 [D4] ups_infoval_set: failed to preprocess value
[ups.start.battery: EpbrasdtiDovefjm]
2.318989 [D5] send_to_all: SETINFO outlet.0.switchable "no"
2.318992 [D5] send_to_all: SETFLAGS outlet.0.switchable RW
2.318994 [D5] send_to_all: ADDENUM outlet.0.switchable "no"
2.318996 [D5] send_to_all: ADDENUM outlet.0.switchable "yes"
2.319001 bypass_alarm: enabled
2.319020 battery_alarm: enabled
2.319036 bypass_when_off: disabled
2.319055 alarm_control: enabled
2.319060 converter_mode: disabled
2.319072 eco_mode: disabled
2.319075 battery_open_status_check: enabled
2.319078 bypass_forbidding: disabled
2.319083 [D4] ups_infoval_set: failed to preprocess value
[site_fault_detection: EpbrasdtiDovefjm]
2.319087 [D4] ups_infoval_set: failed to preprocess value
[advanced_eco_mode: EpbrasdtiDovefjm]
2.319091 [D4] ups_infoval_set: failed to preprocess value
[constant_phase_angle: EpbrasdtiDovefjm]
2.319096 [D4] ups_infoval_set: failed to preprocess value
[limited_runtime_on_battery: EpbrasdtiDovefjm]
2.319101 setvar(bypass_when_off, disabled)
2.319104 bypass_when_off is already disabled
2.319106 setvar: FAILED
2.320434 [D3] send: QHE
2.374864 [D5] read [ 0]: (8 bytes) => 28 32 33 31 20 32 30 39
2.382868 [D5] read [ 8]: (8 bytes) => 20 0d 00 00 00 00 00 00
2.382883 [D3] read: (231 209
2.382916 [D5] send_to_all: SETINFO input.transfer.high "231"
2.382929 [D5] send_to_all: SETFLAGS input.transfer.high RW
2.382932 [D5] send_to_all: ADDRANGE input.transfer.high 231 244
2.382934 [D5] send_to_all: SETFLAGS input.transfer.high RW NUMBER
2.382950 [D5] send_to_all: SETINFO input.transfer.low "209"
2.382953 [D5] send_to_all: SETFLAGS input.transfer.low RW
2.382955 [D5] send_to_all: ADDRANGE input.transfer.low 196 209
2.382957 [D5] send_to_all: SETFLAGS input.transfer.low RW NUMBER
2.382962 [D5] send_to_all: SETINFO input.transfer.low.min "196"
2.382966 [D5] send_to_all: SETINFO input.transfer.low.max "209"
2.382970 [D5] send_to_all: SETINFO input.transfer.high.min "231"
2.382975 [D5] send_to_all: SETINFO input.transfer.high.max "244"
2.384206 [D3] send: QFRE
2.430854 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
2.430859 [D3] read: (NAK
2.430861 [D2] qx_process_answer: query rejected by the UPS
(input.frequency.high)
2.430864 [D2] qx_process_answer: query rejected by the UPS
(input.frequency.low)
2.432092 [D3] send: QBYV
2.494864 [D5] read [ 0]: (8 bytes) => 28 32 36 34 20 31 31 30
2.502857 [D5] read [ 8]: (8 bytes) => 0d 00 00 00 00 00 00 00
2.502875 [D3] read: (264 110
2.502891 max_bypass_volt: 264
2.502896 max_bypass_volt, settable range: 231..276
2.502899 min_bypass_volt: 110
2.502903 min_bypass_volt, settable range: 110..209
2.504103 [D3] send: QBYF
2.566858 [D5] read [ 0]: (8 bytes) => 28 36 34 2e 30 20 35 36
2.574855 [D5] read [ 8]: (8 bytes) => 2e 30 0d 00 00 00 00 00
2.574870 [D3] read: (64.0 56.0
2.574876 max_bypass_freq: 64.0
2.574891 max_bypass_freq, settable range: 61.0..64.0
2.574895 min_bypass_freq: 56.0
2.574909 min_bypass_freq, settable range: 56.0..59.0
2.574915 [D2] setvar: nothing to do... [battery_number]
2.576110 [D3] send: RE0
2.798865 [D5] read [ 0]: (8 bytes) => 00 00 00 00 00 00 00 00
3.801004 [D3] read: Operation timed out (-7)
3.801025 [D4] qx_process: failed to preprocess answer
[battery.voltage.low]
3.802276 [D3] send: QPD
3.846839 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
3.846844 [D3] read: (NAK
3.846855 [D2] qx_process_answer: query rejected by the UPS
(input_phase_angle)
3.846872 [D2] qx_process_answer: query rejected by the UPS
(output_phase_angle)
3.848203 [D3] send: QPAR
3.894852 [D5] read [ 0]: (8 bytes) => 28 30 31 0d 00 00 00 00
3.894870 [D3] read: (01
] 3.894874 [D2] voltronic_parallel: non numerical value
[voltronic_parallel: 01
] 3.894875 [D4] ups_infoval_set: failed to preprocess value
[voltronic_parallel: 01
3.894883 [D5] send_to_all: ADDCMD load.off
3.894898 [D5] send_to_all: ADDCMD load.on
3.894900 [D5] send_to_all: ADDCMD shutdown.return
3.894902 [D5] send_to_all: ADDCMD shutdown.stayoff
3.894904 [D5] send_to_all: ADDCMD shutdown.stop
3.894916 [D5] send_to_all: ADDCMD test.battery.start
3.894918 [D5] send_to_all: ADDCMD test.battery.start.deep
3.894920 [D5] send_to_all: ADDCMD test.battery.start.quick
3.894922 [D5] send_to_all: ADDCMD test.battery.stop
3.894934 [D5] send_to_all: ADDCMD beeper.toggle
3.894937 [D5] send_to_all: ADDCMD beeper.enable
3.894940 [D5] send_to_all: ADDCMD beeper.disable
3.894942 [D5] send_to_all: ADDCMD bypass.start
3.894956 [D5] send_to_all: ADDCMD bypass.stop
3.894960 [D5] send_to_all: SETINFO ups.delay.start "180"
3.894963 [D5] send_to_all: SETFLAGS ups.delay.start RW
3.894978 [D5] send_to_all: ADDRANGE ups.delay.start 0 599940
3.894981 [D5] send_to_all: SETFLAGS ups.delay.start RW NUMBER
3.894983 [D5] send_to_all: SETINFO ups.delay.shutdown "30"
3.894985 [D5] send_to_all: SETFLAGS ups.delay.shutdown RW
3.894989 [D5] send_to_all: ADDRANGE ups.delay.shutdown 12 5940
3.895001 [D5] send_to_all: SETFLAGS ups.delay.shutdown RW NUMBER
3.895005 No values for battery high/low voltages
3.895010 [D5] send_to_all: SETINFO battery.voltage.low "208.00"
3.895023 [D5] send_to_all: SETINFO battery.voltage.high "260.00"
3.895026 Using 'guesstimation' (low: 208.000000, high: 260.000000)!
3.895037 setvar(ups.delay.start, 60)
3.895041 [D2] setvar: setting server side variable ups.delay.start
3.895044 [D5] send_to_all: SETINFO ups.delay.start "60"
3.895046 setvar: SUCCEED
3.895049 setvar(ups.delay.shutdown, 30)
3.895051 setvar: nothing to do... [ups.delay.shutdown]
3.895057 [D5] send_to_all: SETINFO driver.parameter.pollfreq "30"
3.895065 [D5] send_to_all: SETINFO driver.state "init.updateinfo"
3.895068 [D1] upsdrv_updateinfo...
3.895071 [D1] Quick update...
3.896659 [D3] send: QGS
3.950819 [D5] read [ 0]: (8 bytes) => 28 32 32 30 2e 34 20 35
3.990855 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 38 2e
4.022858 [D5] read [ 16]: (8 bytes) => 37 20 35 39 2e 39 20 30
4.062843 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
4.094844 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
4.126840 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 33
4.166841 [D5] read [ 48]: (8 bytes) => 2e 32 20 2d 2d 2d 2e 2d
4.198838 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
4.238833 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
4.254852 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 33
4.254868 [D3] read: (220.4 59.9 218.7 59.9 002.8 007 361.8
361.8 273.2 ---.- 022.9 100000000010
4.254872 [D5] update_status: OL
4.254875 [D5] update_status: !LB
4.254879 [D5] update_status: !CAL
4.254896 [D5] update_status: !FSD
4.254918 [D5] send_to_all: SETINFO ups.status "OL"
4.254921 [D5] send_to_all: DATAOK
4.254924 [D5] send_to_all: SETINFO driver.state "init.quiet"
4.254938 [D5] send_to_all: SETINFO driver.parameter.pollinterval "10"
4.254941 [D5] send_to_all: SETINFO driver.parameter.synchronous "yes"
4.254943 Running as foreground process, not saving a PID file
4.254956 [D5] send_to_all: SETINFO driver.flag.allow_killpower "0"
4.254960 [D5] send_to_all: SETFLAGS driver.flag.allow_killpower RW
NUMBER
4.254963 [D5] send_to_all: ADDCMD driver.killpower
4.254976 [D5] send_to_all: ADDCMD driver.reload
4.254979 [D5] send_to_all: ADDCMD driver.reload-or-exit
4.254981 [D5] send_to_all: ADDCMD driver.reload-or-error
4.254984 [D5] send_to_all: SETINFO driver.state "quiet"
4.254986 [D1] Driver initialization completed, beginning data
dump (1 loops)
4.254990 [D5] send_to_all: SETINFO driver.state "updateinfo"
4.254993 [D1] upsdrv_updateinfo...
4.254995 [D1] Quick update...
4.256195 [D3] send: QGS
4.310837 [D5] read [ 0]: (8 bytes) => 28 32 31 39 2e 35 20 35
4.350846 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 39 2e
4.390858 [D5] read [ 16]: (8 bytes) => 35 20 36 30 2e 30 20 30
4.422834 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
4.454832 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
4.494848 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
4.526837 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
4.566835 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
4.598847 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
4.614849 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
4.614855 [D3] read: (219.5 59.9 219.5 60.0 002.8 007 361.8
361.8 272.9 ---.- 022.9 100000000010
4.614859 [D5] update_status: OL
4.614862 [D5] update_status: !LB
4.614866 [D5] update_status: !CAL
4.614883 [D5] update_status: !FSD
4.614903 [D5] send_to_all: SETINFO driver.state "quiet"
4.614906 [D5] send_to_all: SETINFO driver.state "updateinfo"
4.614908 [D1] upsdrv_updateinfo...
4.614911 [D1] Quick update...
4.616211 [D3] send: QGS
4.670846 [D5] read [ 0]: (8 bytes) => 28 32 32 31 2e 33 20 35
4.710831 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 38 2e
4.742850 [D5] read [ 16]: (8 bytes) => 37 20 35 39 2e 39 20 30
4.782842 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
4.814822 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
4.846843 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
4.886822 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
4.918833 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
4.958839 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
4.974825 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
4.974829 [D3] read: (221.3 59.9 218.7 59.9 002.8 007 361.8
361.8 272.9 ---.- 022.9 100000000010
4.974833 [D5] update_status: OL
4.974836 [D5] update_status: !LB
4.974839 [D5] update_status: !CAL
4.974855 [D5] update_status: !FSD
4.974864 [D5] send_to_all: SETINFO driver.state "quiet"
4.974878 [D5] send_to_all: SETINFO driver.state "dumping"
4.974881 [D3] Entering dstate_dump
battery.charge: 100
battery.packs: 1
battery.protection: yes
battery.runtime: 600
battery.voltage: 272.9
battery.voltage.high: 260.00
battery.voltage.low: 208.00
battery.voltage.nominal: 240.0
device.model: G10K
device.type: ups
driver.debug: 6
driver.flag.allow_killpower: 0
driver.name: nutdrv_qx
driver.parameter.bypass_when_off: disabled
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 10
driver.parameter.port: auto
driver.parameter.synchronous: yes
driver.state: dumping
driver.version: 2.8.0-2359-g6c0032e52
driver.version.data: Voltronic 0.08
driver.version.internal: 0.35
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.current.nominal: 45.0
input.frequency: 59.9
input.frequency.nominal: 60.0
input.phases: 1
input.transfer.high: 231
input.transfer.high.max: 244
input.transfer.high.min: 231
input.transfer.low: 209
input.transfer.low.max: 209
input.transfer.low.min: 196
input.voltage: 221.3
input.voltage.nominal: 230.0
outlet.0.switchable: no
output.current: 2.8
output.current.nominal: 45
output.frequency: 60.0
output.frequency.nominal: 60.0
output.phases: 1
output.powerfactor: 0.8
output.voltage: 220.4
output.voltage.nominal: 220.0
ups.beeper.status: enabled
ups.delay.shutdown: 30
ups.delay.start: 60
ups.firmware: 00077.13
ups.firmware.aux: P02
ups.load: 7
ups.power.nominal: 10000
ups.productid: 5161
ups.start.auto: yes
ups.status: OL
ups.temperature: 22.9
ups.type: online
ups.vendorid: 0665
4.975010 [D5] send_to_all: SETINFO driver.state "cleanup.upsdrv"
4.975014 [D1] upsdrv_cleanup...
4.975125 [D5] send_to_all: SETINFO driver.state "cleanup.exit
------------------------------
Subject: Digest Footer
_______________________________________________
Nut-upsdev mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev
------------------------------
End of Nut-upsdev Digest, Vol 206, Issue 5
******************************************
_______________________________________________
Nut-upsdev mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev