Good day! Here are the results with OpenMediaVault 8.1.2-1 running on a 
Raspberry Pi 4 and the UPS BE900G3 from APC using the usbhid-ups driver. This 
model is not listed yet in the compatibility list.
  *
Device manufacturer and name: APC model BE900G3
  *
shutdown 
sequence<https://networkupstools.org/docs/user-manual.chunked/ar01s06.html#Shutdown_design>
 testing results: Tested with a 60 seconds countdown after unplugging from the 
wall, device turned off as expected.
  *
a link to the manufacturer’s online description of the device is also 
appreciated.<https://www.se.com/us/en/product/BE900G3/apc-backups-900va-540w-floor-wall-mount-120v-8x-nema-515r-outlets-usb-type-a-+-c-ports/>
 
https://www.se.com/us/en/product/BE900G3/apc-backups-900va-540w-floor-wall-mount-120v-8x-nema-515r-outlets-usb-type-a-+-c-ports/
upsc output:

battery.charge: 97
battery.charge.low: 10
battery.mfr.date: 2001/01/01
battery.runtime: 4357
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 14.4
battery.voltage.nominal: 12.0
device.mfr: American Power Conversion
device.model: Back-UPS BE900G3
device.serial: 0B2528P00742
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: auto
driver.state: quiet
driver.version: 2.8.1
driver.version.data: APC HID 0.100
driver.version.internal: 0.52
driver.version.usb: libusb-1.0.28 (API: 0x100010a)
input.sensitivity: medium
input.transfer.high: 139
input.transfer.low: 92
input.transfer.reason: input voltage out of range
input.voltage: 116.0
input.voltage.nominal: 115
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 464401G -495900G
ups.load: 0
ups.mfr: American Power Conversion
ups.mfr.date: 2025/07/08
ups.model: Back-UPS BE900G3
ups.productid: 0002
ups.realpower.nominal: 540
ups.serial: 0B2528P00742
ups.status: OL CHRG
ups.test.result: Done and passed
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d

Cheers!

Simon
_______________________________________________
Nut-upsdev mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to