Hi Spiros!

I attached output of my ups.
I hope it will be usefull for you.
I sent correct values earlier for you.

2010/4/30 Spiros Ioannou <[email protected]>

> As I'm trying to find the correct values for other UPS models and I
> only see correct values, please use the attached driver while
> compiling nut and please give me an output from upsc.
>
> I would like you to give me the output from upsc along with the
> correct values you get from Multilink or the LCD.
> The only thing that must be wrong are the multipliers.
> Thanks for your effort,
> -Spiros
>



-- 
Best Regards,

Robert
battery.current: 0.00
battery.runtime: 10740
battery.runtime.low: 120
battery.temperature: 0.0
battery.voltage: 54.9
battery.voltage.nominal: 55.2
device.mfr: Liebert
device.model: GXT2-1000RT230                
device.serial: 0428100126AF041     
device.type: ups
driver.name: liebert-esp2
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.version: 2.4.3-2447M
driver.version.internal: 0.02
input.bypass.current: 0.0
input.bypass.frequency: 5.0
input.bypass.voltage: 231.8
input.frequency: 5.0
input.frequency.nominal: 5.0
input.phases: 1
input.voltage: 231.8
output.current: 0.7
output.frequency: 5.0
output.frequency.nominal: 5.0
output.phases: 1
output.voltage: 230.4
ups.delay.start: 0
ups.firmware: GXT2MR15D       
ups.load: 17
ups.mfr: Liebert
ups.mfr.date: 12OCT04 
ups.model: GXT2-1000RT230                
ups.power: 178
ups.power.nominal: 100000
ups.realpower: 83
ups.serial: 0428100126AF041     
ups.status: OL
ups.temperature: 30.5
ups.type: online
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev