Hi,

I want the driver report the battery status from ABM charging controllers 
-patch attached- :

http://www.google.de/url?sa=t&rct=j&q=advanced+battery+management+floating&source=web&cd=1&ved=0CDMQxQEwAA&url=http%3A%2F%2Fdocs.google.com%2Fviewer%3Fa%3Dv%26q%3Dcache%3AH0Fy9-ZmujgJ%3Alit.powerware.com%2Fll_download.asp%253Ffile%253DABM_datasheet_rev_A_re_working.pdf%2Badvanced%2Bbattery%2Bmanagement%2Bfloating%26hl%3Dde%26gl%3Dde%26pid%3Dbl%26srcid%3DADGEESj_h5zp2cVwCOSCZP0BgmzG3jNOC9cq_54FStVvgWoYVD6lauUNAqYpMSoVxYMf3dcNF2_9x_ZGCPNGnnlm6OVZuvi8VzKvbVfwVdNISlcSrdzqaeS3b8I2WApj9E_Yh38CGIww%26sig%3DAHIEtbRE44qDSR4VtSuK7qOOLZSRVz7XYA&ei=ytUvT6XyBILKtAbJk4ndDA&usg=AFQjCNH0GuqrYphp6h9t1jtWcAu0LzGsBw

battery.capacity.nominal: 17.00
battery.charge: 74.4
battery.runtime: 1620
battery.status.abm: RS (New)
battery.voltage: 26.10*
battery.voltage.maximum: 28.20
battery.voltage.minimum: 20.00
battery.voltage.nominal: 24.00

Since my ancient Compaq T1000h got it, response STBM should be widely 
implemented:
http://webcache.googleusercontent.com/search?q=cache:Pt8WJTtgaW0J:old.networkupstools.org/protocols/eaton/UC2concept-1002889j.odt+upscode+II+pdf&cd=1&hl=de&ct=clnk&gl=de

BTW, possible bug: Wether my new lead AGM batteries are broken (Cold weather 
storage damage in GLS logistics transport?)
http://media.rotek.at/a000/000/007/000000007_V000000_HAB_HIG_00_RT_A_de.pdf

*or the charge estimation calculator of the driver is broken:

battery.capacity.nominal: 17.00
battery.charge: 93.9
battery.runtime: 1620
battery.status.abm: FT
battery.voltage: 27.70
battery.voltage.maximum: 28.20
battery.voltage.minimum: 20.00
battery.voltage.nominal: 24.00
device.mfr: Compaq
device.model: UPS 1000 VA FW -0026
device.serial: E00230050

My UPS does not support UPBS cmd, but its responses are not very useful anyway.

y
tom






--- nut-2.6.2/drivers/upscode2.c	2011-09-15 13:30:45.000000000 +0200
+++ nut-2.6.2/drivers/upscode2.c	2012-02-05 18:14:42.000000000 +0100
@@ -32,7 +32,7 @@
  * Powerware 9305
  *
  * Also tested against
- * Compaq T1500h (Per J?nsson <[email protected]>)
+ * Compaq T1000h/T1500h (T.Schorpp, <[email protected]>, Per J?nsson <[email protected]>)
  * Powerware 9120 (Gorm J. Siiger <[email protected]>)
  * Fiskars PowerServer 10 (Per Larsson <[email protected]>)
  */
@@ -45,7 +45,7 @@
 #include <math.h>
 
 #define DRIVER_NAME	"UPScode II UPS driver"
-#define DRIVER_VERSION	"0.87"
+#define DRIVER_VERSION	"0.88"
 
 /* driver description structure */
 upsdrv_info_t	upsdrv_info = {
@@ -54,7 +54,7 @@
 	"H K Lygre, <[email protected]>\n" \
 	"Niels Baggesen <[email protected]>\n" \
 	"Niklas Edmundsson <[email protected]>",
-	DRV_EXPERIMENTAL,
+	DRV_BETA,
 	{ NULL }
 };
 
@@ -262,7 +262,7 @@
 	{ "STAT", t_list,   NULL, 0, 0, att },
 	{ "STBO", t_status, NULL, UPSC_STAT_ONBATT },
 	{ "STBL", t_status, NULL, UPSC_STAT_LOBATT },
-	{ "STBM", t_ignore },
+	{ "STBM", t_string, "battery.status.abm" },
 	{ "STBP", t_status, NULL, UPSC_STAT_BYPASS },
 	{ "STEA", t_list,   NULL, 0, 0, env },
 	{ "STEM", t_list,   NULL, 0, 0, env },
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to