Hello,
Got PowerCOM BNT-1000AP, usb id 0d9f:00a6, firmware FW4.A6
nut 2.4.3 on debian stable shows only two instant commands:
beeper.toggle - Toggle the UPS beeper -- not working
test.battery.start.quick - Start a quick battery test -- works ok.
No load and shutdown commands.
Trying svn trunk version, with the same results.
Debug output shows the problem:
0.035558 hid_lookup_path: 00840004 -> UPS
0.035569 hid_lookup_path: 00840024 -> PowerSummary
0.035580 hid_lookup_path: 00ff0057 -> not found in lookup table
..skip..
0.036073 hid_lookup_path: 00840004 -> UPS
0.036084 hid_lookup_path: 00840024 -> PowerSummary
0.036095 hid_lookup_path: 00ff0056 -> not found in lookup table
..skip..
0.054472 hid_lookup_usage: UPS -> 00840004
0.054476 hid_lookup_usage: PowerSummary -> 00840024
0.054480 hid_lookup_usage: DelayBeforeStartup -> 00840056
0.054488 string_to_path: depth = 3
0.054494 hid_lookup_usage: UPS -> 00840004
0.054499 hid_lookup_usage: PowerSummary -> 00840024
0.054503 hid_lookup_usage: DelayBeforeShutdown -> 00840057
0.054507 string_to_path: depth = 3
0.054512 hid_lookup_usage: UPS -> 00840004
0.054517 hid_lookup_usage: PowerSummary -> 00840024
0.054521 hid_lookup_usage: DelayBeforeShutdown -> 00840057
0.054525 string_to_path: depth = 3
0.054531 find_nut_info: unknown info type: load.off.delay
0.054535 find_nut_info: unknown info type: load.on.delay
0.054539 find_nut_info: unknown info type: load.off.delay
Appears in firmware FW4.A6 PowerCOM changed DelayBeforeStartup/Shutdown
usage pages to Page 0x00ff.
It's non-standard, "USB Usage Tables for HID Power Devices" says:
"Usage pages xFF00 to xFFFF are reserved by HID for vendor-specific
implementation".
May change again..
Anyway, patch against svn trunk attached.
Beeper.enable/disable also works, but only on battery.
Patched nut upscmd -l output:
Instant commands supported on UPS [pcm]:
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.toggle - Toggle the UPS beeper
load.off - Turn off the load immediately
load.on - Turn on the load immediately
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
test.battery.start.quick - Start a quick battery test
Index: drivers/powercom-hid.c
===================================================================
--- drivers/powercom-hid.c (revision 3857)
+++ drivers/powercom-hid.c (working copy)
@@ -94,6 +94,7 @@
uint16_t val, command;
val = atoi(value ? value : s);
+ val = val ? val : 1; /* 0 sets the maximum delay */
command = ((val % 60) << 8) + (val / 60);
command |= 0x4000; /* AC RESTART NORMAL ENABLE */
upsdebugx(3, "%s: value = %s, command = %04X", __func__, value, command);
@@ -111,6 +112,7 @@
uint16_t val, command;
val = atoi(value ? value : s);
+ val = val ? val : 1; /* 0 sets the maximum delay */
command = ((val % 60) << 8) + (val / 60);
command |= 0x8000; /* AC RESTART NORMAL DISABLE */
upsdebugx(3, "%s: value = %s, command = %04X", __func__, value, command);
@@ -137,6 +139,8 @@
{ "POWERCOM1", 0x0084002f },
{ "POWERCOM2", 0xff860060 },
{ "POWERCOM3", 0xff860080 },
+ { "PCMDelayBeforeStartup", 0x00ff0056 },
+ { "PCMDelayBeforeShutdown", 0x00ff0057 },
{ NULL, 0 }
};
@@ -235,6 +239,8 @@
*/
{ "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 8, "UPS.PowerSummary.DelayBeforeShutdown", NULL, DEFAULT_OFFDELAY, HU_FLAG_ABSENT, NULL },
{ "ups.timer.shutdown", 0, 0, "UPS.PowerSummary.DelayBeforeShutdown", NULL, "%.0f", HU_FLAG_QUICK_POLL, powercom_shutdown_info },
+ { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 8, "UPS.PowerSummary.PCMDelayBeforeShutdown", NULL, DEFAULT_OFFDELAY, HU_FLAG_ABSENT, NULL },
+ { "ups.timer.shutdown", 0, 0, "UPS.PowerSummary.PCMDelayBeforeShutdown", NULL, "%.0f", HU_FLAG_QUICK_POLL, powercom_shutdown_info },
{ "input.voltage", 0, 0, "UPS.Input.Voltage", NULL, "%.1f", 0, NULL },
{ "input.voltage.nominal", 0, 0, "UPS.Input.ConfigVoltage", NULL, "%.0f", HU_FLAG_STATIC, NULL },
@@ -251,10 +257,16 @@
/* instcmds */
{ "beeper.toggle", 0, 0, "UPS.PowerSummary.AudibleAlarmControl", NULL, "1", HU_TYPE_CMD, NULL },
+ { "beeper.enable", 0, 0, "UPS.PowerSummary.AudibleAlarmControl", NULL, "1", HU_TYPE_CMD, NULL },
+ { "beeper.disable", 0, 0, "UPS.PowerSummary.AudibleAlarmControl", NULL, "0", HU_TYPE_CMD, NULL },
{ "test.battery.start.quick", 0, 0, "UPS.Battery.Test", NULL, "1", HU_TYPE_CMD, NULL },
{ "load.on.delay", 0, 0, "UPS.PowerSummary.DelayBeforeStartup", NULL, NULL, HU_TYPE_CMD, powercom_startup_info },
{ "shutdown.return", 0, 0, "UPS.PowerSummary.DelayBeforeShutdown", NULL, NULL, HU_TYPE_CMD, powercom_shutdown_info },
{ "shutdown.stayoff", 0, 0, "UPS.PowerSummary.DelayBeforeShutdown", NULL, NULL, HU_TYPE_CMD, powercom_stayoff_info },
+ { "load.on", 0, 0, "UPS.PowerSummary.PCMDelayBeforeStartup", NULL, "0", HU_TYPE_CMD, powercom_startup_info },
+ { "load.off", 0, 0, "UPS.PowerSummary.PCMDelayBeforeShutdown", NULL, "0", HU_TYPE_CMD, powercom_stayoff_info },
+ { "shutdown.return", 0, 0, "UPS.PowerSummary.PCMDelayBeforeShutdown", NULL, NULL, HU_TYPE_CMD, powercom_shutdown_info },
+ { "shutdown.stayoff", 0, 0, "UPS.PowerSummary.PCMDelayBeforeShutdown", NULL, NULL, HU_TYPE_CMD, powercom_stayoff_info },
/* end of structure. */
{ NULL, 0, 0, NULL, NULL, NULL, 0, NULL }
_______________________________________________