Hello. I sometimes encountered batteries that were ok, but at times one of the cells would develop a random short/open, therefore reducing the real capacity even if voltage reading was ok. In the absence of a battery load tester i would suggest running multiple tests with a load (car headlight bulb or similar) on the battery outside the ups. This is to eliminate the suspicion of a software or UPS unit fault.
Alex. On Mon, 27 Jan 2020, 02:53 Manuel Wolfshant, <wo...@nobugconsulting.ro> wrote: > On 1/25/20 10:53 AM, Georgi D. Sotirov wrote: > > OK, so yesterday evening I done a real test cutting of the power to the > UPS. And it went good... the UPS supported my server for 28:50 minutes > (i.e. the expected runtime with this load), before forcing shutdown. The > batteries could still hold as charge was 30 % with about 15 minutes run > time. And the UPS did hold for another full 10 minutes before powering off. > These are the relevant lines from /var/log/ups: > > 20200124 201318 32 0.0 12 [OB] NA 0.0 > 20200124 201323 30 0.0 13 [ALARM OB LB] NA 0.0 > 20200124 201328 30 0.0 13 [FSD ALARM OB LB] NA 0.0 > 20200124 201333 30 0.0 13 [FSD ALARM OB LB] NA 0.0 > 20200124 201338 30 0.0 13 [FSD ALARM OB LB] NA 0.0 > 20200124 201340 30 0.0 13 [FSD ALARM OB LB] NA 0.0 > > that looks perfectly fine > > > > The server was shutdown properly, but for some reason it did not power > off. I saw an error from umount about busy file system, but I'm sure this > doesn't always happen. > > the error is related to your linux system, not to nut > > > > With everything powered off, I extracted the original batteries to check > them and measure the voltage. The batteries are Leoch DJW12-9.0 with one of > them at 12.57 V and the other at 12.64 V (measured without load after the > discharge). > > That's... surprisingly well, assuming your multimeter indicates correct > values. I would have expected values well below 12V > > > > > And this morning there was again a short power failure (not more than 30 > minutes, because the router connected to the battery power from the UPS did > hold up). With batteries charged up to 91% the UPS supported the server for > just 07:10 minutes and forced shutdown with 69% battery charge and over 20 > minutes of run time... > > 20200125 021123 70 0.0 16 [OB] NA 0.0 > 20200125 021128 69 0.0 16 [FSD ALARM OB LB] NA 0.0 > 20200125 021133 69 0.0 16 [FSD ALARM OB LB] NA 0.0 > 20200125 021138 69 0.0 16 [FSD ALARM OB LB] NA 0.0 > 20200125 021143 69 0.0 16 [FSD ALARM OB LB] NA 0.0 > 20200125 021148 69 0.0 16 [FSD ALARM OB LB] NA 0.0 > 20200125 021150 69 0.0 16 [FSD ALARM OB LB] NA 0.0 > > So, it seems to me that my UPS forces shutdown pretty randomly. Why the > UPS is not waiting for the preset low battery charge value of 15%? What is > actually driving this FSD ALARM and LB signal when batteries for sure could > hold up more? > > > Can you please show us all the configuration files ? I can only suspect > that there is something wrong there because (from a hardware point of view) > the UPS behaves very very well, according to your tests and logs. > > > _______________________________________________ > Nut-upsuser mailing list > Nut-upsuser@alioth-lists.debian.net > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
_______________________________________________ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser