Is NUT using the same SNMP v3 user as your SNMP Set or a different one?

If it is a different one (e.g. an SNMP v1 or v2c string) does that user / 
community string have read/write access?


tcpdump to listen for packets across UDP 161 is one way to check what is 
actually being sent.


Thank you,

David Zomaya
Tripp Lite

________________________________
From: Nut-upsuser 
<nut-upsuser-bounces+david_zomaya=tripplite....@alioth-lists.debian.net> on 
behalf of Lee Damon <no...@ee.washington.edu>
Sent: Wednesday, April 29, 2020 5:00:16 PM
To: nut-upsuser Mailing List
Subject: [EXTERNAL] [Nut-upsuser] SNMP shutdown timing out

This is an EXTERNAL email. Please take a moment and think before clicking any 
links or opening any attachments from this email. If suspicious, please forward 
to ishelpd...@tripplite.com for review.
________________________________
I'm in the process of trying to get NUT to manage an APC SmartUPS.

Monitoring of the UPS is working fine:
$ upsc nutdev1@localhost
Init SSL without certificate database
ambient.1.humidity.alarm.high: 60.00
ambient.1.humidity.alarm.low: 30.00
ambient.1.temperature.alarm.high: 40.00
ambient.1.temperature.alarm.low: 10.00
battery.charge: 94.00
battery.charge.restart: 0
battery.current: 0.00
battery.date: 03/14/20
battery.packs: 0.00
battery.packs.bad: -1.00
battery.runtime: 5160.00
battery.runtime.low: 120
battery.voltage: 27.00
battery.voltage.nominal: -1.00
device.mfr: APC
device.model: SMART-UPS 1400
device.serial: WS9831004667
device.type: ups
driver.name<https://urldefense.proofpoint.com/v2/url?u=http-3A__driver.name&d=DwMFaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=VdKSS_Vk98WT0ADZ-mQe_3zCfrLacAAuMS7JSj5wn1w&s=hM67G_Mcn7oW5yo4o44Na9wyw26mxM8hKXFExeGyhJQ&e=>:
 snmp-ups
driver.parameter.authProtocol: MD5
driver.parameter.mibs: apcc
driver.parameter.pollinterval: 2
driver.parameter.port: 192.5.37.191
driver.parameter.privProtocol: DES
driver.parameter.secLevel: authPriv
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: apcc MIB 1.2
driver.version.internal: 0.97
input.frequency: 60.00
input.sensitivity: high
input.transfer.high: 132
input.transfer.low: 103
input.transfer.reason: selfTest
input.voltage: 120.90
input.voltage.maximum: 122.20
input.voltage.minimum: 120.20
output.current: 0.00
output.frequency: 60.00
output.voltage: 120.90
output.voltage.nominal: 115
ups.delay.shutdown: 20
ups.delay.start: 0
ups.firmware: 70.11.D
ups.id<https://urldefense.proofpoint.com/v2/url?u=http-3A__ups.id&d=DwMFaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=VdKSS_Vk98WT0ADZ-mQe_3zCfrLacAAuMS7JSj5wn1w&s=Cv5z1Xm7dspkGCX9gosuUR3R9b6cDZLJnumKkJ4s1Ms&e=>:
 apcups
ups.load: 14.00
ups.mfr: APC
ups.mfr.date: 07/28/98
ups.model: SMART-UPS 1400
ups.serial: WS9831004667
ups.status: OL
ups.temperature: 24.70
ups.test.date: 04/29/2020
ups.test.result: Ok

I can use snmpset to halt the UPS.
  snmpset -v 3 -a MD5 -A NutScan@Password43LongerWord -l authPriv -u nut -x DES 
-X NutScan@Password43LongerWord apcups 
SNMPv2-SMI::enterprises.318.1.1.1.6.1.1.0 i 2

(Passwords are temporary, I don't care if they leak.)

I am aware of the note in the MIB that states "Setting this variable to 
turnUpsOffToConserveBattery(2) causes a UPS on battery to be put into 'sleep' 
mode.  The UPS will turn back on when utility power is restored.  Attempting to 
turn off a UPS that is not on battery will result in a badValue error." so 
tests are being done with the UPS on battery.

However, when I try to tell it to shut down the UPS it fails with a timeout.

$ sudo snmp-ups -DDDDDDD -a nutdev1 -k
Network UPS Tools - Generic SNMP UPS driver 0.97 (2.7.4)
   0.000000     send_to_all: SETINFO driver.parameter.port "192.5.37.191"
   0.000027     send_to_all: SETINFO driver.parameter.mibs "apcc"
   0.000044     send_to_all: SETINFO driver.parameter.secLevel "authPriv"
   0.000049     send_to_all: SETINFO driver.parameter.authProtocol "MD5"
   0.000067     send_to_all: SETINFO driver.parameter.privProtocol "DES"
   0.000071     debug level is '7'
   0.001365     SNMP UPS driver: entering upsdrv_initups()
   0.001371     SNMP UPS driver: entering nut_snmp_init(snmp-ups)
   0.008570     Setting SNMP retries to 5
   0.008575     Setting SNMP timeout to 1 second(s)
   0.008605     SNMP UPS driver: entering load_mib2nut(apcc)
   0.008610     load_mib2nut: trying classic method with 'apcc' mib
   0.008613     su_find_info: "ups.model" found
   0.008615     Testing ups.model using OID .1.3.6.1.4.1.318.1.1.1.1.1.1.0
   0.008617     Entering nut_snmp_get_str()
   0.008619     nut_snmp_get(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.008637     nut_snmp_walk(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.008640     nut_snmp_walk: max. iteration = 1
   0.027623     load_mib2nut: testOID provided and matches MIB 'apcc'!
   0.027636     load_mib2nut: using apcc mib
   0.027639     su_find_info: "ups.model" found
   0.027641     Entering nut_snmp_get_str()
   0.027642     nut_snmp_get(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.027644     nut_snmp_walk(.1.3.6.1.4.1.318.1.1.1.1.1.1.0)
   0.027646     nut_snmp_walk: max. iteration = 1
   0.051176     Detected SMART-UPS 1400 on host 192.5.37.191 (mib: apcc 1.2)
   0.051192     su_find_info: unknown info type (load.off.delay)
   0.051195     su_find_info: unknown info type (load.on.delay)
   0.051197     su_find_info: unknown info type (load.off.delay)
   0.051199     Initiating UPS shutdown
   0.051201     upsdrv_shutdown...
   0.051203     Unknown template type: shutdown.return
   0.051204     entering su_instcmd(shutdown.return, (null))
   0.051207     su_find_info: "shutdown.return" found
   0.051209     entering nut_snmp_set(.1.3.6.1.4.1.318.1.1.1.6.1.1.0, i, 2)
   6.059576     [nutdev1] nut_snmp_set: can't set 
.1.3.6.1.4.1.318.1.1.1.6.1.1.0: Timeout
   6.059591     su_instcmd: cannot set value for shutdown.return
   6.059593     Unknown template type: shutdown.reboot
   6.059595     entering su_instcmd(shutdown.reboot, (null))
   6.059599     su_find_info: unknown info type (shutdown.reboot)
   6.059601     su_instcmd: shutdown.reboot unavailable
   6.059602     Unknown template type: load.off.delay
   6.059603     entering su_instcmd(load.off.delay, (null))
   6.059606     su_find_info: unknown info type (load.off.delay)
   6.059608     su_instcmd: load.off.delay unavailable
   6.059609     Shutdown failed!

This *might* be related to the question I asked yesterday about nut-scanner but 
given the difference in error reported (nut-scanner was complaining about auth) 
I don't think so.

I'm using nut packages from EPEL 8 for all of this.

I've set SELinux to permissive (even tried 'disabled') and it doesn't appear to 
be blocking anything.

Anyone have any suggestions for what I can try next?

nomad
________________________________
This message is for the addressee's use only. It may contain confidential 
information. If you receive this message in error, please delete it and notify 
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no 
responsibility for viruses which may infect an email sent to you from Tripp 
Lite and which damage your electronic systems or information. It is your 
responsibility to maintain virus detection systems to prevent damage to your 
electronic systems and information.