On 6/28/20 5:54 AM, Scott Colby wrote:
I'm not convinced this is the problem; I think that pfSense has
an alternative way of running the NUT components:
# ps aux | grep ups
root 45456 0.0 0.1 6796 884 - Is 02:22 0:00.01
/usr/local/sbin/upsmon
uucp 45751 0.0 0.1 6796 772 - S 02:22 0:00.10
/usr/local/sbin/upsmon
uucp 46796 0.0 0.1 6888 888 - Ss 02:22 0:00.45
/usr/local/libexec/nut/usbhid-ups -a AVR750U
root 56752 0.0 0.1 6788 832 - Ss 02:22 0:00.13
/usr/local/sbin/upsd -u root
root 39437 0.0 0.2 6828 2464 0 S+ 02:46 0:00.01 grep ups
Is there anything else that should be running?
AFAIK, no, those 3 daemons should do the job. But just for the fun of
it, I would test changing that variable anyway. There is nothing to
lose, after all.
Would you expect `upsmon -c fsd` to not work as I described above
(system halting but UPS not power cycling) if MODE was set to none
but upsmon, the driver, and upsd were running?
If it is running ( i.e. started ) -c fsd should trigger an immediate
shutdown. quote from man upsmon:
*-c* /command/
Send the command /command/ to the existing upsmon process. Valid
commands are:
*fsd*
shutdown all master UPSes (use with caution)
# cat ups.conf
[AVR750U]
driver=usbhid-ups
port=auto
productid=3024
# cat upsmon.conf
MONITOR AVR750U 1 local-monitor <password> master
[...]
driver.version.internal: 0.41
input.frequency: 5990.0
This value is definitely incorrectly reported. Based on the voltages
below I assume you are in USA and the displayed value could be an
incorrectly scaled 59.9 Hz
You are correct about my location and expected voltage. Is there
somewhere that I can change the scaling factor used by NUT?
not that I know of. and
https://networkupstools.org/docs/man/usbhid-ups.html does not show any
either. fortunately the errors are purely cosmetic