There *may* have been a complicating factor. One of our other UPSs (there are three in the set) *might* have been onbatt because it was calibrating at the time. I don't think it was but I can't be sure.
However, that was a different UPS so it *shouldn't* have done anything. nomad On 3/8/21 1:42 PM, Manuel Wolfshant wrote: > On 3/8/21 11:09 PM, Lee Damon via Nut-upsuser wrote: >> Over the weekend one of three UPSs in our server room decided one of >> it's new batteries was bad. I thought maybe the battery wasn't really >> bad since I'd forgotten to tell the UPS to recalibrate. > >> >> I tried to get the UPS to recharge so I could get it to recalibrate >> but at some point it flagged LOWBATT and even though it was on line >> power NUT decided to shut down the world. > > this should not have happened because it's the standard situation when > the battery is depleted and recharging > > >> >> Needless to say, this was undesirable. > > right. it should not have happened > > >> >> Is there any configuration change I can make to say "only shut down if >> the UPS is reporting both ONBATT and LOWBATT"? > > as far as I can tell you have a different issue over there that needs > investigation. as long as the UPS is on line power ( and the input > voltage is within limits ), nut should not trigger a shutdown > > _______________________________________________ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser