On Sun, 27 Nov 2022, Simon Wilson via Nut-upsuser wrote:

Per https://networkupstools.org/docs/user-manual.chunked/ar01s06.html 6.3, am I right in thinking, for my single server running NUT (in standalone mode) with connected USB UPS:

- when battery.charge reaches battery.charge.low: ups.status triggers to "LB" and upsmon sets an FSD in motion - upsmon waits FINALDELAY 5 seconds, and calls my shutdown command (which then in sequence does a clean shutdown of my VMs before calling the 'real' shutdown command)
- my server then shuts down and powers off

Main question:

"ups.delay.shutdown" - at what point does this variable kick in? Is ups.delay.shutdown the period in seconds after FSD that the UPS will hard-shutdown, i.e. I need to ensure that my server can complete clean shutdown in that duration?

Yes, you do need to give your server sufficient time.
My understanding is that the ups.delay.shutdown is overwritten by the offdelay option in file ups.conf.

In the machine with which I type this, I have

 rprice@titan ~ upsc Eaton ups.delay.shutdown
 20
 rprice@titan ~ grep offdelay /etc/nut/ups.conf
         offdelay = 30

See https://rogerprice.org/NUT/ConfigExamples.A5.pdf chapter 2.5, and chapter 2.7 line 77.

Roger

_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to