Jim Klimov via Nut-upsuser <nut-upsuser@alioth-lists.debian.net> > > Cheers, > > One PR waiting to get into 2.8.1 release timeframe is > https://github.com/networkupstools/nut/pull/1652 stemming from issue > https://github.com/networkupstools/nut/issues/1279 > > The gist of it is that "battery.voltage" and "battery.charge" were not > always reported correctly with nutdrv-qx driver (might be handled better by > blazer drivers though), and the overrides tried by issue posters did not help > them with original state of NUT codebase.
I tried it on three ups: 10kv online, 3kv online, 2kv offline. all the battery.voltage are fine and the same value as 2.7.4. the battery.charge report of 10kv and 3kv are fine. but 2kv is wrong. with 2.7.4 the 2kv battery.charge is reporting 100. but the new code is reporting 67. details below: 10KV: ./nutdrv_qx -a ftups -d1 Network UPS Tools - Generic Q* USB/Serial driver 0.33 (Windows-v2.8.0-alpha3-1252-g757813e) USB communication driver (libusb 0.1) 0.44 Using protocol: Voltronic 0.07 battery_number: 20 battery_number, settable range: 1..9 bypass_alarm: enabled battery_alarm: enabled bypass_when_off: disabled alarm_control: enabled converter_mode: disabled eco_mode: disabled battery_open_status_check: enabled bypass_forbidding: disabled setvar(bypass_when_off, disabled) bypass_when_off is already disabled setvar: FAILED max_bypass_volt: 264 max_bypass_volt, settable range: 231..276 min_bypass_volt: 110 min_bypass_volt, settable range: 110..209 max_bypass_freq: 64.0 max_bypass_freq, settable range: 61.0..64.0 min_bypass_freq: 56.0 min_bypass_freq, settable range: 56.0..59.0 No values for battery high/low voltages Using 'guesstimation' (low: 208.000000, high: 300.000000)! setvar(ups.delay.start, 60) setvar: SUCCEED setvar(ups.delay.shutdown, 12) setvar: SUCCEED battery.charge: 100 battery.packs: 1 battery.protection: yes battery.runtime: 600 battery.voltage: 272.9 battery.voltage.high: 300.00 battery.voltage.low: 208.00 battery.voltage.nominal: 240.0 device.model: G10K device.type: ups driver.name: nutdrv_qx driver.parameter.bypass_when_off: disabled driver.parameter.offdelay: 12 driver.parameter.ondelay: 60 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 10 driver.parameter.port: auto driver.parameter.synchronous: yes driver.state: dumping driver.version: Windows-v2.8.0-alpha3-1252-g757813e driver.version.data: Voltronic 0.07 driver.version.internal: 0.33 driver.version.usb: libusb-0.1 (or compat) input.current.nominal: 45.0 input.frequency: 59.9 input.frequency.nominal: 60.0 input.phases: 1 input.transfer.high: 231 input.transfer.high.max: 244 input.transfer.high.min: 231 input.transfer.low: 209 input.transfer.low.max: 209 input.transfer.low.min: 196 input.voltage: 218.7 input.voltage.nominal: 230.0 outlet.0.switchable: no output.current: 2.8 output.current.nominal: 45 output.frequency: 59.9 output.frequency.nominal: 60.0 output.phases: 1 output.powerfactor: 0.8 output.voltage: 218.7 output.voltage.nominal: 220.0 ups.beeper.status: enabled ups.delay.shutdown: 12 ups.delay.start: 60 ups.firmware: 00077.13 ups.firmware.aux: P02 ups.load: 7 ups.power.nominal: 10000 ups.productid: 5161 ups.start.auto: yes ups.status: OL ups.temperature: 25.4 ups.type: online ups.vendorid: 0665 3KV: ./nutdrv_qx -a ftups -d1 Network UPS Tools - Generic Q* USB/Serial driver 0.33 (Windows-v2.8.0-alpha3-1252-g757813e) USB communication driver (libusb 0.1) 0.44 Using protocol: Voltronic 0.07 device.serial: UPS reported a non-significant serial [00000000000000] battery_number: 6 battery_number, settable range: 1..9 bypass_alarm: enabled battery_alarm: enabled bypass_when_off: disabled alarm_control: enabled converter_mode: disabled eco_mode: disabled bypass_forbidding: disabled site_fault_detection: disabled setvar(bypass_when_off, disabled) bypass_when_off is already disabled setvar: FAILED max_bypass_volt: 132 max_bypass_volt, settable range: 120..140 min_bypass_volt: 85 min_bypass_volt, settable range: 85..115 max_bypass_freq: 63.0 max_bypass_freq, settable range: 61.0..70.0 min_bypass_freq: 57.0 min_bypass_freq, settable range: 50.0..59.0 No values for battery high/low voltages Using 'guesstimation' (low: 62.400000, high: 90.000000)! setvar(ups.delay.start, 60) setvar: SUCCEED setvar(ups.delay.shutdown, 30) setvar: nothing to do... [ups.delay.shutdown] battery.charge: 100 battery.energysave: no battery.packs: 1 battery.protection: yes battery.runtime: 2820 battery.voltage: 082.0 battery.voltage.high: 90.00 battery.voltage.low: 62.40 battery.voltage.nominal: 72.0 device.model: 3K device.type: ups driver.name: nutdrv_qx driver.parameter.bypass_when_off: disabled driver.parameter.offdelay: 30 driver.parameter.ondelay: 60 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 10 driver.parameter.port: auto driver.parameter.synchronous: yes driver.state: dumping driver.version: Windows-v2.8.0-alpha3-1252-g757813e driver.version.data: Voltronic 0.07 driver.version.internal: 0.33 driver.version.usb: libusb-0.1 (or compat) input.current.nominal: 27.0 input.frequency: 59.9 input.frequency.nominal: 60.0 input.phases: 1 input.transfer.high: 116 input.transfer.high.max: 122 input.transfer.high.min: 113 input.transfer.low: 104 input.transfer.low.max: 107 input.transfer.low.min: 98 input.voltage: 112.2 input.voltage.nominal: 110.0 outlet.0.switchable: no output.current: 5.4 output.current.nominal: 27 output.frequency: 59.9 output.frequency.nominal: 60.0 output.phases: 1 output.power.maximum.percent: 19 output.power.minimum.percent: 18 output.powerfactor: 0.8 output.voltage: 109.8 output.voltage.nominal: 110.0 ups.beeper.status: enabled ups.delay.shutdown: 30 ups.delay.start: 60 ups.firmware: 00204.06 ups.firmware.aux: P01 ups.load: 18 ups.power.nominal: 3000 ups.productid: 5161 ups.start.auto: yes ups.start.battery: yes ups.status: OL ups.temperature: 17.2 ups.type: online ups.vendorid: 0665 2KV: ./nutdrv_qx -a ftups -d1 Network UPS Tools - Generic Q* USB/Serial driver 0.33 (Windows-v2.8.0-alpha3-1252-g757813e) USB communication driver (libusb 0.1) 0.44 Using protocol: Voltronic-QS 0.09 No values for battery high/low voltages Using 'guesstimation' (low: 10.400000, high: 15.000000)! Autodetected 1 as number of battery packs [12/13.50] Battery runtime will not be calculated (runtimecal not set) setvar(ups.delay.start, 60) setvar: SUCCEED setvar(ups.delay.shutdown, 30) setvar: nothing to do... [ups.delay.shutdown] battery.charge: 67 battery.voltage: 13.5 battery.voltage.high: 15.00 battery.voltage.low: 10.40 battery.voltage.nominal: 12.0 device.type: ups driver.name: nutdrv_qx driver.parameter.bypass_when_off: disabled driver.parameter.offdelay: 30 driver.parameter.ondelay: 60 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 10 driver.parameter.port: auto driver.parameter.synchronous: yes driver.state: dumping driver.version: Windows-v2.8.0-alpha3-1252-g757813e driver.version.data: Voltronic-QS 0.09 driver.version.internal: 0.33 driver.version.usb: libusb-0.1 (or compat) input.voltage: 119.5 input.voltage.fault: 119.5 output.current.nominal: 6.0 output.frequency: 60.1 output.frequency.nominal: 60 output.voltage: 119.5 output.voltage.nominal: 110 ups.beeper.status: enabled ups.delay.shutdown: 30 ups.delay.start: 60 ups.firmware.aux: PM-V ups.load: 32 ups.productid: 5161 ups.status: OL ups.type: offline / line interactive ups.vendorid: 0665 _______________________________________________ Nut-upsuser mailing list Nut-upsuser@alioth-lists.debian.net https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser