On 5/7/07, Doug Parsons <[EMAIL PROTECTED]> wrote:
Network UPS Tools upsset 2.0.4

set input.transfer.high to 130 (was 127)
Error: SET failed: Access denied
No settings changed.

What about the webserver error log?

Have you checked the man page for upsset.conf?

Can you try on the command line with upsrw?

I thought that it would use one of the users from the upsd.users file. But
neither one of these nor the nut user will work.

Do those users (in upsd.users) have monitor privileges? I think that's
a step up from just being able to see values with upsc.

----- Original Message -----
From: "Charles Lepple" <[EMAIL PROTECTED]>
To: "Doug Parsons" <[EMAIL PROTECTED]>
Cc: <[email protected]>
Sent: Monday, May 07, 2007 8:03 PM
Subject: Re: [Nut-upsuser] User credential for cgi site


> On 5/5/07, Doug Parsons <[EMAIL PROTECTED]> wrote:
>> Running into a little problem. I have several UPS units connected to one
>> server. Then several servers talk to this server. All of this is working.
>> When I try to set a setting with the setting.cgi page I get an access
>> denied. Which credential does the setting.cgi page authenticate against?
>
> I assume you mean upsset.cgi. I believe the web server needs monitor
> privileges, and the UPS has to be listed in hosts.conf.
>
> Can you cut-and-paste the error message verbatim? That should narrow
> things down. Also, check your web server error log to see if any more
> detailed messages are there.
>
>> I am running 2.0.4 and the particular UPS is a 2200RM APC.
>
> Who built the 2.0.4 package you are using?
>
> --
> - Charles Lepple
>
>





--