On Tue, Sep 11, 2007 at 09:41:21AM +0200, Arjen de Korte wrote: > > > On Mon, Sep 10, 2007 at 09:12:36PM +0200, Arjen de Korte wrote: > >> > >> > My MGE Pulsar Evolution 800 had some hardware troubles (it may be the > >> > batteries according to the manual). The fault was not detected so the > >> > power was cut to the load and nothing appears in the log files. > >> > >> Please be as specific as possible to describing what kind of problem you > >> had. Which driver (and interface) are you using and which NUT version > >> are > >> we talking about. > > > > I am on Debian unstable and have official Nut 2.2.0 package installed. > > That's useful information.
I agree I should have been more specific on my first try. > > > I use the mge-shut driver (serial as that is what the s in shut means). > > This is historical on my part as I was the original author of the driver > > when it was still called mge-ellipse. > > In that case, you might want to try the newmge-shut driver. Especially if > you use the version from the trunk, you'll find that it supports far more > UPS variables. Since it shares much of the code of the usbhid-ups driver > (except for the low level communications stuff) this will probably replace > the existing mge-shut driver somewhere in the future. > > > When I got home after work, my computer was off and my UPS was beeping > > with the fault led blinking. > > When was the last time you ran a battery test? I believe the UPS does it automatically as I sometimes hear it doing a small bip. > > > I tried to reset the UPS by powering it off and disconnecting it from > > the wall but when I switched it back on and powered up the display it > > would start beeping again and the fault led started to blink again. > > Could you still communicate with it? I don't know the computer where it is connected was off and I didn't think of doing it. > > > That seems likely to be a hardware problem. As the UPS is already 4 > > years old batteries are a likely candidate (and seems to be what the > > beeping and led blinking means according to the manual). > > Batteries are by far the most vulnerable part of a UPS. Some faults will > only show up under load and if you never run battery tests, they may only > surface when the power goes out. So chances are that the UPS itself would > not have noticed something was wrong, before it really became a problem. > In order to prevent this, running a (weekly/monthly) battery test, even if > it is just for a couple of seconds, is absolutely needed. A decent UPS > will notice that the batteries are bad, abort the test and raise an alarm > without interrupting power. > After disconnecting the batteries, the UPS seems to work again somewhat, I'll make a more thorough test as you suggest before ordering a replacement. > > >> Note that the only *automatic* shutdown NUT supports, is for a low > >> battery > >> situation, since that might not need user intervention to clear. Chances > >> are that there are ways to detect the problem you're having (depending > >> on > >> what driver you're using), but I doubt that this will result in NUT > >> initiating a shutdown. It might throw an alarm, but this usually means > >> that it still requires user intervention to deal with/correct the > >> situation. > > Yes I understand only LB condition initiates the shutdown sequence. I > > don't know if the protocol contains any provision to inform the computer > > a hardware problem has occured, that was the meaning of my question > > because if it is available some support for it would be great. > > The HID Power Devices specification provides many ways to inform about > (potential) problems. The nice thing about the newmge-shut driver is that > if you run it in debug mode, it will show all the variables the UPS > supports. You can then lookup the meaning in this specification and see if > that's what you need. I'll give newmge-shut a try, thanks. > > > I would have liked to fine something in my log files. I know the > > problem occured between 14:15 and 14:29 but not much :( > > I guess it was a power outage and the battery failed the moment it really > had to provide power. Regarding the age of the battery, this is quite a > likely failure mode. > I have another UPS which did not record any power failure according to upsmon so it may be during an automatic test of the UPS that the fault occured. Philippe _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser