>>> Alternatively, you might use upsrw and experiment with the value of >>> 'ups.delay.shutdown', which changes the same value in the UPS as the >>> 'load.off' command will. Unfortunately, it doesn't have a >>> 'ups.delay.restart', so you will need to press the power button to >>> switch the output back on again. >> Well, using upsrw to set ups.delay.shutdown to various values appears to >> accept the value, but no change is made to the actual value. > See above.
Never mind that remark. Changing variables in nut-2.2.0 is broken for subdrivers that define multiple HID paths for the same NUT variable. It will only use the first HID path it finds, whether or not it is supported on the connected UPS. Since the apc-hid.c subdriver only has one mapping for 'battery.charge.low' this is OK, but it has no less than three for 'ups.delay.restart' and the one you need is the third. So forget about changing 'ups.delay.start', it won't work with nut-2.2.0 (the development version should work however). Best regards, Arjen _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser