On 26/11/2007, at 12.06, Arjen de Korte wrote:

> Jon Bendtsen wrote:
>
>> I gave up on using the USB converter and used a regular serial
>> cable, it works fine using both the powerpanel and the cpsups
>> driver. I prefer the powerpanel because the name is slightly nicer
>> in the cgi.
>
> Could you post the output of 'upsc <upsname>' here? We're working on
> extending the support for the powerpanel driver, but in order to do
> that, we need some information on what is reported by devices that are
> supported already. Thanks in advance.



powerpanel driver:
---------------------------------------------
[EMAIL PROTECTED]:~# upsc bp500
battery.capacity: 7
battery.charge: 100.0
battery.charge.low: 20
battery.packs: 1
battery.voltage.nominal: 12
driver.name: powerpanel
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.version: 2.2.0-
driver.version.internal: 0.22
input.frequency: 49.9
input.frequency.high: 63
input.frequency.low: 47
input.transfer.high: 272
input.transfer.low: 180
input.voltage: 234
input.voltage.nominal: 230
output.voltage: 234
ups.firmware: 1.704
ups.load: 80
ups.mfr: CYBER POWER
ups.model: 500VA
ups.power.nominal: 500
ups.realpower.nominal: 330
ups.serial: 000000000000
ups.status: OL
ups.temperature: 32


cpsups driver:
--------------------------------------------
[EMAIL PROTECTED]:/etc/nut# upsc bp500
battery.charge: 100.0
battery.runtime:  3:58
driver.name: cpsups
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.version: 2.2.0-
driver.version.internal: .05
input.frequency: 50
input.voltage: 234
output.voltage: 234
ups.load: 82
ups.mfr: CyberPower
ups.model: OP500TE 1.704
ups.power.nominal: 500
ups.runtime: 16.5
ups.status: OL
ups.temperature: 32


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to