> I removed all servers and workstation from the output of the ups.

Servers, workstations? You have multiple devices connected to this system?
See my previous message, your UPS doesn't have the capacity to power more
than a small server or maybe two workstations (if you're lucky).

> I then connected my periphery (monitor, printer, soundsystem...) to the
> battery backed-up output of the ups to have some load.

You should *never* connect a printer to the battery backed up output of a
UPS. Especially laser printers draw huge amounts of power while powering
up. A small SOHO type UPS is not able to cope with that.

> (maybe its only
> 3%, but I it showed the same behaviour as with the servers attached)

I think 3% is the value that would be indicated when the load is
essentially shutdown. Note that 3% is a load of only 33VA.

> After running the command, the ups went off. There was a "klick" :-)
> My monitor went off. My Soundsystem went off. I then had to press the
> ups' power button to turn it back on. The ups has a load of about 55%
> when everything is running under heavy load.

That is too much. Assuming a reasonable power factor which you can expect
nowadays, the real load will be close to

        55% x 1100VA = 605W

As written before, the maximum load on your UPS is just 660W. At startup,
this will more than likely be more than 660W (harddrives spinning up), so
I think you'll need to lower the load on your system. I don't know why the
system shuts down when you fire up the driver, but it could be that the
UPS uses slightly different thresholds depending whether it is running in
managed or unmanaged mode. Unless you run the driver with the '-k' option,
it will not send the UPS a command to shutdown the load.

Best regards, Arjen