Steve,
You're welcome.
I forgot to clarify that while you will have two upsmon processes
running (one with root privileges, the other which listens on the
network socket), only one should be logging.
On Aug 22, 2008, at 8:37 AM, Steve T wrote:
Charles,
Thanks for that.
I think the duplicated startup was caused by me also editing /etc/
sysconfig/ups as well as the NUT specific config files. I have
removed the /etc/sysconfig changes and the messages file looks ok
(comparatively!).
On Fri, 2008-08-22 at 08:20 -0400, Charles Lepple wrote:
On Aug 22, 2008, at 7:18 AM, Steve T wrote:
This will sound a bit odd.
I have a current server running with a UPS. I'm in the process of
replacing that server with another and obviously want Nut to
monitor the new server. The new/old servers are in different
locations, so I don't have access to the UPS while configuring
the replacement server.
I think I have the config ok, but what errors would you expect to
see? Typically I'm getting a 'driver not connected' type error in
the /var/log/messages:
"driver not connected" is normal. However...
Aug 19 18:07:16 T300 upsd[1308]: listening on 0.0.0.0 port 3493
Aug 19 18:07:16 T300 upsd[1308]: Can't connect to UPS [belkin]
(belkinunv-belkin): No such file or directory
Aug 19 18:07:16 T300 upsd[1309]: Startup successful
Aug 19 18:07:16 T300 upsmon[1312]: Startup successful
Aug 19 18:07:16 T300 upsd[1309]: Client [EMAIL PROTECTED] logged
into UPS [belkin]
Aug 19 18:07:16 T300 upsmon[1313]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:16 T300 upsmon[1313]: Communications with UPS
[EMAIL PROTECTED] lost
Aug 19 18:07:21 T300 upsmon[1313]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:21 T300 upsmon[1313]: UPS [EMAIL PROTECTED] is
unavailable
Aug 19 18:07:26 T300 upsmon[1313]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:29 T300 upsd[1342]: not listening on 0.0.0.0 port 3493
Aug 19 18:07:29 T300 upsmon[1347]: Startup successful
Aug 19 18:07:29 T300 upsd[1309]: Client [EMAIL PROTECTED] logged
into UPS [belkin]
Aug 19 18:07:29 T300 upsmon[1348]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:29 T300 upsmon[1348]: Communications with UPS
[EMAIL PROTECTED] lost
Aug 19 18:07:31 T300 upsmon[1313]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:34 T300 upsmon[1348]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:34 T300 upsmon[1348]: UPS [EMAIL PROTECTED] is
unavailable
Aug 19 18:07:36 T300 upsmon[1313]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:39 T300 upsmon[1348]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Aug 19 18:07:41 T300 upsmon[1313]: Poll UPS [EMAIL PROTECTED]
failed - Driver not connected
Having two copies of upsmon (1313 and 1348) logging messages about
the same UPS is not expected, though.
Also note:
Aug 19 18:07:16 T300 upsd[1308]: listening on 0.0.0.0 port 3493
[...]
Aug 19 18:07:29 T300 upsd[1342]: not listening on 0.0.0.0 port 3493
The second copy of upsd can't bind to the same port as the first
one, so you get the above error message.
--
Charles Lepple
[EMAIL PROTECTED]
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser