Citeren Seann Clark <[EMAIL PROTECTED]>:
> This output is after everything has been shut down and all NUT
> related items killed out of memory after a init script being run to
> stop the main items. The output of the debug is:
> debug level is '3'
> Trying binary protocol...
> read: (20 bytes) => 2e 4f 50 31 35 30 30 20 20 20 20 2e 78 2e 3c 2e 35 31
> 30 30
> CyberPower UPS with binary protocol on /dev/ttyS0 detected
The autodetection for the protocol works at least, it is reporting an
OP1500 model.
> send: (3 bytes) => 52 02 0d
> read: (2 bytes) => 52 00
> send: (3 bytes) => 52 04 0d
> read: (2 bytes) => 52 00
> send: (3 bytes) => 52 08 0d
> read: (2 bytes) => 52 00
> send: (3 bytes) => 52 18 0d
> read: (2 bytes) => 52 00
Here a couple of settings from the UPS are read. It is using the table
for the OP series, so this is correct too.
> send: (2 bytes) => 44 0d
> read: (14 bytes) => 23 7d 00 22 2e d6 80 b1 2e 09 f6 00 ff 0d
> dstate_init: sock /var/run/nut/powerpanel-cyberpower-ups open on fd 6
> send: (2 bytes) => 44 0d
> read: (14 bytes) => 23 7c 00 21 2e d6 7f b1 2e 09 f6 00 ff 0d
> send: (2 bytes) => 44 0d
> read: (14 bytes) => 23 7d 00 22 2e d6 80 b1 2e 09 f6 00 ff 0d
> send: (2 bytes) => 44 0d
> read: (14 bytes) => 23 7d 00 22 2e d6 80 b2 2e 09 f6 00 ff 0d
We succeeded to poll for the status four times in a row (without
retries), so the communication is fine so far.
> send: (2 bytes) => 44 0d
> read: timed out
> Communications with UPS lost: Status read failed!
...but here the problems start.
It looks like we suddenly have developed a communication problem here,
the UPS doesn't want to talk/listen to us anymore. Usually this has to
do with the cable power for the UPS. Currently, the 'powerpanel'
driver clears RTS and sets DTR. I noticed that both the 'cyberpower'
and 'nitram' drivers set both. Could you try if changing line 93 in
powerpanel.c to
ser_set_rts(upsfd, 1);
fixes the problem? I suspect that clearing RTS might be a mistake here.
Best regards, Arjen
--
Please keep list traffic on the list
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser