On Fri, 27 Nov 2009, Guillaume Vachon wrote:

Hi all,
I just got myself 2 APC Back-UPS CS 350

I downloaded the stable nut tar.gz installed it.
This is not the first time i install and configure nut so i used the
same configuration as on my other server as i always did. Then i made
the 2 required modification. I changed these 2 thing:
       driver = apcsmart
       port = /dev/hiddev0

# ls -al /dev/hiddev0
crw------- 1 nut nut 180, 96 Nov 27 09:07 /dev/hiddev0

When i try to start nut i get the following :

# upsdrvctl start
Network UPS Tools - UPS driver controller 2.2.0-
Network UPS Tools (version 2.2.0-) - APC Smart protocol driver
        Driver version 1.99.8, command table version 2.0
tcgetattr(/dev/hiddev0): Invalid argument
Driver failed to start (exit status=1)

Thanks in advance if someone can help !

--
Guillaume Vachon (RHCE, CLP10, CTT+, CNI)
Conseiller en TI, Formateur
Infoglobe, http://infoglobe.ca
1963, Frank-Carrel, 201 - Québec, QC G1N 2E6
Téléphone : 418.681.2929 #123




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Try port = auto

In addition, is it a SMART APC?

You may also need
        driver = usbhid-ups

Instead of
       driver = apcsmart

Lastly, lsusb, check the device & bus number, go to dev and find it, make sure its owner is owned by nut and looks like this:

# ls -lR /dev/bus/usb | grep nut
crw-rw-r-- 1 root nut  189, 385 2009-11-27 16:24 002

Justin.