Arnaud Quette wrote:

> 2009/11/30 raf <[email protected]>:
> > hi,
> 
> Hi Raf,
> 
> > i've just set up two new computers each with a Powerware 3105 ups.
> > they have identical nut configurations and identical upss which
> > are both plugged in via usb but only one is being detected by nut.
> > the other keeps saying:
> >
> >  Broadcast Message from n...@server-1
> >          (somewhere) at 14:52 ...
> >  UPS u...@localhost is unavailable
> > (...)
> 
> everything seems fine there.
> I've recently made several changes and improvements on this driver
> (the USB one) and would be interested in a driver debug output, ie:
> $ /lib/nut/bcmxcp_usb -DDD -a ups
> 
> according to these info, I'll be able to give you a solution.
> 
> cheers,
> Arnaud
> -- 
> Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops
> Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
> Debian Developer - http://www.debian.org
> Free Software Developer - http://arnaud.quette.free.fr/

hi arnaud,

i've attached the output from both hosts. strangely, the output
for the one that works is almost identical to the one that
doesn't.

cheers,
raf


Network UPS Tools - BCMXCP UPS driver 0.14 (2.2.2)

Warning: This is an experimental driver.
Some features may not function correctly.

Model = POWERWARE UPS    700VA
Firmware = Cont:00.80 Inve:00.60
debug level is '3'
Shutdown delay =  120 seconds
Index   Offset  Format  NUT



Length of alarm map: 22

Index   Alarm   Supported

-001    INVERTER_AC_OVER_VOLTAGE        No
-001    INVERTER_AC_UNDER_VOLTAGE       No
-001    INVERTER_OVER_OR_UNDER_FREQ     No
-001    BYPASS_AC_OVER_VOLTAGE  No
-001    BYPASS_AC_UNDER_VOLTAGE No
-001    BYPASS_OVER_OR_UNDER_FREQ       No
-001    INPUT_AC_OVER_VOLTAGE   No
-001    INPUT_AC_UNDER_VOLTAGE  No
-001    INPUT_UNDER_OR_OVER_FREQ        No
-001    OUTPUT_OVER_VOLTAGE     No
-001    OUTPUT_UNDER_VOLTAGE    No
-001    OUTPUT_UNDER_OR_OVER_FREQ       No
-001    REMOTE_EMERGENCY_PWR_OFF        No
-001    REMOTE_GO_TO_BYPASS     No
-001    BUILDING_ALARM_6        No
-001    BUILDING_ALARM_5        No
-001    BUILDING_ALARM_4        No
-001    BUILDING_ALARM_3        No
-001    BUILDING_ALARM_2        No
-001    BUILDING_ALARM_1        No
-001    STATIC_SWITCH_OVER_TEMP No
-001    CHARGER_OVER_TEMP       No
-001    CHARGER_LOGIC_PWR_FAIL  No
-001    CHARGER_OVER_VOLTAGE_OR_CURRENT No
-001    INVERTER_OVER_TEMP      No
-001    OUTPUT_OVERLOAD No
-001    RECTIFIER_INPUT_OVER_CURRENT    No
-001    INVERTER_OUTPUT_OVER_CURRENT    No
-001    DC_LINK_OVER_VOLTAGE    No
-001    DC_LINK_UNDER_VOLTAGE   No
-001    RECTIFIER_FAILED        No
-001    INVERTER_FAULT  No
-001    BATTERY_CONNECTOR_FAIL  No
-001    BYPASS_BREAKER_FAIL     No
-001    CHARGER_FAIL    No
-001    RAMP_UP_FAILED  No
-001    STATIC_SWITCH_FAILED    No
-001    ANALOG_AD_REF_FAIL      No
-001    BYPASS_UNCALIBRATED     No
-001    RECTIFIER_UNCALIBRATED  No
-001    OUTPUT_UNCALIBRATED     No
-001    INVERTER_UNCALIBRATED   No
-001    DC_VOLT_UNCALIBRATED    No
-001    OUTPUT_CURRENT_UNCALIBRATED     No
-001    RECTIFIER_CURRENT_UNCALIBRATED  No
-001    BATTERY_CURRENT_UNCALIBRATED    No
-001    INVERTER_ON_OFF_STAT_FAIL       No
-001    BATTERY_CURRENT_LIMIT   No
-001    INVERTER_STARTUP_FAIL   No
-001    ANALOG_BOARD_AD_STAT_FAIL       No
-001    OUTPUT_CURRENT_OVER_100 No
-001    BATTERY_GROUND_FAULT    No
-001    WAITING_FOR_CHARGER_SYNC        No
-001    NV_RAM_FAIL     No
-001    ANALOG_BOARD_AD_TIMEOUT No
-001    SHUTDOWN_IMMINENT       No
0000    BATTERY_LOW     Yes
0001    UTILITY_FAIL    Yes
-001    OUTPUT_SHORT_CIRCUIT    No
-001    UTILITY_NOT_PRESENT     No
-001    FULL_TIME_CHARGING      No
-001    FAST_BYPASS_COMMAND     No
-001    AD_ERROR        No
-001    INTERNAL_COM_FAIL       No
-001    RECTIFIER_SELFTEST_FAIL No
-001    RECTIFIER_EEPROM_FAIL   No
-001    RECTIFIER_EPROM_FAIL    No
-001    INPUT_LINE_VOLTAGE_LOSS No
-001    BATTERY_DC_OVER_VOLTAGE No
-001    POWER_SUPPLY_OVER_TEMP  No
-001    POWER_SUPPLY_FAIL       No
-001    POWER_SUPPLY_5V_FAIL    No
-001    POWER_SUPPLY_12V_FAIL   No
-001    HEATSINK_OVER_TEMP      No
-001    HEATSINK_TEMP_SENSOR_FAIL       No
-001    RECTIFIER_CURRENT_OVER_125      No
-001    RECTIFIER_FAULT_INTERRUPT_FAIL  No
-001    RECTIFIER_POWER_CAPASITOR_FAIL  No
-001    INVERTER_PROGRAM_STACK_ERROR    No
-001    INVERTER_BOARD_SELFTEST_FAIL    No
-001    INVERTER_AD_SELFTEST_FAIL       No
-001    INVERTER_RAM_SELFTEST_FAIL      No
-001    NV_MEMORY_CHECKSUM_FAIL No
-001    PROGRAM_CHECKSUM_FAIL   No
-001    INVERTER_CPU_SELFTEST_FAIL      No
-001    NETWORK_NOT_RESPONDING  No
-001    FRONT_PANEL_SELFTEST_FAIL       No
-001    NODE_EEPROM_VERIFICATION_ERROR  No
-001    OUTPUT_AC_OVER_VOLT_TEST_FAIL   No
-001    OUTPUT_DC_OVER_VOLTAGE  No
-001    INPUT_PHASE_ROTATION_ERROR      No
-001    INVERTER_RAMP_UP_TEST_FAILED    No
-001    INVERTER_OFF_COMMAND    No
-001    INVERTER_ON_COMMAND     No
-001    TO_BYPASS_COMMAND       No
-001    FROM_BYPASS_COMMAND     No
-001    AUTO_MODE_COMMAND       No
-001    EMERGENCY_SHUTDOWN_COMMAND      No
-001    SETUP_SWITCH_OPEN       No
-001    INVERTER_OVER_VOLT_INT  No
-001    INVERTER_UNDER_VOLT_INT No
-001    ABSOLUTE_DCOV_ACOV      No
-001    PHASE_A_CURRENT_LIMIT   No
-001    PHASE_B_CURRENT_LIMIT   No
-001    PHASE_C_CURRENT_LIMIT   No
-001    BYPASS_NOT_AVAILABLE    No
-001    RECTIFIER_BREAKER_OPEN  No
-001    BATTERY_CONTACTOR_OPEN  No
-001    INVERTER_CONTACTOR_OPEN No
-001    BYPASS_BREAKER_OPEN     No
-001    INV_BOARD_ACOV_INT_TEST_FAIL    No
-001    INVERTER_OVER_TEMP_TRIP No
-001    INV_BOARD_ACUV_INT_TEST_FAIL    No
-001    INVERTER_VOLTAGE_FEEDBACK_ERROR No
-001    DC_UNDER_VOLTAGE_TIMEOUT        No
-001    AC_UNDER_VOLTAGE_TIMEOUT        No
-001    DC_UNDER_VOLTAGE_WHILE_CHARGE   No
-001    INVERTER_VOLTAGE_BIAS_ERROR     No
-001    RECTIFIER_PHASE_ROTATION        No
-001    BYPASS_PHASER_ROTATION  No
-001    SYSTEM_INTERFACE_BOARD_FAIL     No
-001    PARALLEL_BOARD_FAIL     No
-001    LOST_LOAD_SHARING_PHASE_A       No
-001    LOST_LOAD_SHARING_PHASE_B       No
-001    LOST_LOAD_SHARING_PHASE_C       No
-001    DC_OVER_VOLTAGE_TIMEOUT No
-001    BATTERY_TOTALLY_DISCHARGED      No
-001    INVERTER_PHASE_BIAS_ERROR       No
-001    INVERTER_VOLTAGE_BIAS_ERROR_2   No
-001    DC_LINK_BLEED_COMPLETE  No
-001    LARGE_CHARGER_INPUT_CURRENT     No
-001    INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No
-001    LOSS_OF_REDUNDANCY      No
-001    LOSS_OF_SYNC_BUS        No
-001    RECTIFIER_BREAKER_SHUNT_TRIP    No
-001    LOSS_OF_CHARGER_SYNC    No
-001    INVERTER_LOW_LEVEL_TEST_TIMEOUT No
-001    OUTPUT_BREAKER_OPEN     No
-001    CONTROL_POWER_ON        No
-001    INVERTER_ON     No
-001    CHARGER_ON      No
-001    BYPASS_ON       No
-001    BYPASS_POWER_LOSS       No
-001    ON_MANUAL_BYPASS        No
-001    BYPASS_MANUAL_TURN_OFF  No
-001    INVERTER_BLEEDING_DC_LINK_VOLT  No
-001    CPU_ISR_ERROR   No
-001    SYSTEM_ISR_RESTART      No
-001    PARALLEL_DC     No
-001    BATTERY_NEEDS_SERVICE   No
-001    BATTERY_CHARGING        No
-001    BATTERY_NOT_CHARGED     No
-001    DISABLED_BATTERY_TIME   No
-001    SERIES_7000_ENABLE      No
-001    OTHER_UPS_ON    No
-001    PARALLEL_INVERTER       No
-001    UPS_IN_PARALLEL No
-001    OUTPUT_BREAKER_REALY_FAIL       No
-001    CONTROL_POWER_OFF       No
-001    LEVEL_2_OVERLOAD_PHASE_A        No
-001    LEVEL_2_OVERLOAD_PHASE_B        No
-001    LEVEL_2_OVERLOAD_PHASE_C        No
-001    LEVEL_3_OVERLOAD_PHASE_A        No
-001    LEVEL_3_OVERLOAD_PHASE_B        No
-001    LEVEL_3_OVERLOAD_PHASE_C        No
-001    LEVEL_4_OVERLOAD_PHASE_A        No
-001    LEVEL_4_OVERLOAD_PHASE_B        No
-001    LEVEL_4_OVERLOAD_PHASE_C        No
0002    UPS_ON_BATTERY  Yes
-001    UPS_ON_BYPASS   No
-001    LOAD_DUMPED     No
-001    LOAD_ON_INVERTER        No
-001    UPS_ON_COMMAND  No
-001    UPS_OFF_COMMAND No
-001    LOW_BATTERY_SHUTDOWN    No
-001    AUTO_ON_ENABLED No


Shutdown delay longer than battery capacity when Low Battery warning is given. 
(max 60 seconds)
dstate_init: sock /var/run/nut/bcmxcp_usb-ups open on fd 5
new connection on fd 6
Signal 2: exiting
CLOSING

Network UPS Tools - BCMXCP UPS driver 0.14 (2.2.2)

Warning: This is an experimental driver.
Some features may not function correctly.

Model = POWERWARE UPS    700VA
Firmware = Cont:00.80 Inve:00.60
debug level is '3'
Shutdown delay =  120 seconds
Index   Offset  Format  NUT



Length of alarm map: 22

Index   Alarm   Supported

-001    INVERTER_AC_OVER_VOLTAGE        No
-001    INVERTER_AC_UNDER_VOLTAGE       No
-001    INVERTER_OVER_OR_UNDER_FREQ     No
-001    BYPASS_AC_OVER_VOLTAGE  No
-001    BYPASS_AC_UNDER_VOLTAGE No
-001    BYPASS_OVER_OR_UNDER_FREQ       No
-001    INPUT_AC_OVER_VOLTAGE   No
-001    INPUT_AC_UNDER_VOLTAGE  No
-001    INPUT_UNDER_OR_OVER_FREQ        No
-001    OUTPUT_OVER_VOLTAGE     No
-001    OUTPUT_UNDER_VOLTAGE    No
-001    OUTPUT_UNDER_OR_OVER_FREQ       No
-001    REMOTE_EMERGENCY_PWR_OFF        No
-001    REMOTE_GO_TO_BYPASS     No
-001    BUILDING_ALARM_6        No
-001    BUILDING_ALARM_5        No
-001    BUILDING_ALARM_4        No
-001    BUILDING_ALARM_3        No
-001    BUILDING_ALARM_2        No
-001    BUILDING_ALARM_1        No
-001    STATIC_SWITCH_OVER_TEMP No
-001    CHARGER_OVER_TEMP       No
-001    CHARGER_LOGIC_PWR_FAIL  No
-001    CHARGER_OVER_VOLTAGE_OR_CURRENT No
-001    INVERTER_OVER_TEMP      No
-001    OUTPUT_OVERLOAD No
-001    RECTIFIER_INPUT_OVER_CURRENT    No
-001    INVERTER_OUTPUT_OVER_CURRENT    No
-001    DC_LINK_OVER_VOLTAGE    No
-001    DC_LINK_UNDER_VOLTAGE   No
-001    RECTIFIER_FAILED        No
-001    INVERTER_FAULT  No
-001    BATTERY_CONNECTOR_FAIL  No
-001    BYPASS_BREAKER_FAIL     No
-001    CHARGER_FAIL    No
-001    RAMP_UP_FAILED  No
-001    STATIC_SWITCH_FAILED    No
-001    ANALOG_AD_REF_FAIL      No
-001    BYPASS_UNCALIBRATED     No
-001    RECTIFIER_UNCALIBRATED  No
-001    OUTPUT_UNCALIBRATED     No
-001    INVERTER_UNCALIBRATED   No
-001    DC_VOLT_UNCALIBRATED    No
-001    OUTPUT_CURRENT_UNCALIBRATED     No
-001    RECTIFIER_CURRENT_UNCALIBRATED  No
-001    BATTERY_CURRENT_UNCALIBRATED    No
-001    INVERTER_ON_OFF_STAT_FAIL       No
-001    BATTERY_CURRENT_LIMIT   No
-001    INVERTER_STARTUP_FAIL   No
-001    ANALOG_BOARD_AD_STAT_FAIL       No
-001    OUTPUT_CURRENT_OVER_100 No
-001    BATTERY_GROUND_FAULT    No
-001    WAITING_FOR_CHARGER_SYNC        No
-001    NV_RAM_FAIL     No
-001    ANALOG_BOARD_AD_TIMEOUT No
-001    SHUTDOWN_IMMINENT       No
0000    BATTERY_LOW     Yes
0001    UTILITY_FAIL    Yes
-001    OUTPUT_SHORT_CIRCUIT    No
-001    UTILITY_NOT_PRESENT     No
-001    FULL_TIME_CHARGING      No
-001    FAST_BYPASS_COMMAND     No
-001    AD_ERROR        No
-001    INTERNAL_COM_FAIL       No
-001    RECTIFIER_SELFTEST_FAIL No
-001    RECTIFIER_EEPROM_FAIL   No
-001    RECTIFIER_EPROM_FAIL    No
-001    INPUT_LINE_VOLTAGE_LOSS No
-001    BATTERY_DC_OVER_VOLTAGE No
-001    POWER_SUPPLY_OVER_TEMP  No
-001    POWER_SUPPLY_FAIL       No
-001    POWER_SUPPLY_5V_FAIL    No
-001    POWER_SUPPLY_12V_FAIL   No
-001    HEATSINK_OVER_TEMP      No
-001    HEATSINK_TEMP_SENSOR_FAIL       No
-001    RECTIFIER_CURRENT_OVER_125      No
-001    RECTIFIER_FAULT_INTERRUPT_FAIL  No
-001    RECTIFIER_POWER_CAPASITOR_FAIL  No
-001    INVERTER_PROGRAM_STACK_ERROR    No
-001    INVERTER_BOARD_SELFTEST_FAIL    No
-001    INVERTER_AD_SELFTEST_FAIL       No
-001    INVERTER_RAM_SELFTEST_FAIL      No
-001    NV_MEMORY_CHECKSUM_FAIL No
-001    PROGRAM_CHECKSUM_FAIL   No
-001    INVERTER_CPU_SELFTEST_FAIL      No
-001    NETWORK_NOT_RESPONDING  No
-001    FRONT_PANEL_SELFTEST_FAIL       No
-001    NODE_EEPROM_VERIFICATION_ERROR  No
-001    OUTPUT_AC_OVER_VOLT_TEST_FAIL   No
-001    OUTPUT_DC_OVER_VOLTAGE  No
-001    INPUT_PHASE_ROTATION_ERROR      No
-001    INVERTER_RAMP_UP_TEST_FAILED    No
-001    INVERTER_OFF_COMMAND    No
-001    INVERTER_ON_COMMAND     No
-001    TO_BYPASS_COMMAND       No
-001    FROM_BYPASS_COMMAND     No
-001    AUTO_MODE_COMMAND       No
-001    EMERGENCY_SHUTDOWN_COMMAND      No
-001    SETUP_SWITCH_OPEN       No
-001    INVERTER_OVER_VOLT_INT  No
-001    INVERTER_UNDER_VOLT_INT No
-001    ABSOLUTE_DCOV_ACOV      No
-001    PHASE_A_CURRENT_LIMIT   No
-001    PHASE_B_CURRENT_LIMIT   No
-001    PHASE_C_CURRENT_LIMIT   No
-001    BYPASS_NOT_AVAILABLE    No
-001    RECTIFIER_BREAKER_OPEN  No
-001    BATTERY_CONTACTOR_OPEN  No
-001    INVERTER_CONTACTOR_OPEN No
-001    BYPASS_BREAKER_OPEN     No
-001    INV_BOARD_ACOV_INT_TEST_FAIL    No
-001    INVERTER_OVER_TEMP_TRIP No
-001    INV_BOARD_ACUV_INT_TEST_FAIL    No
-001    INVERTER_VOLTAGE_FEEDBACK_ERROR No
-001    DC_UNDER_VOLTAGE_TIMEOUT        No
-001    AC_UNDER_VOLTAGE_TIMEOUT        No
-001    DC_UNDER_VOLTAGE_WHILE_CHARGE   No
-001    INVERTER_VOLTAGE_BIAS_ERROR     No
-001    RECTIFIER_PHASE_ROTATION        No
-001    BYPASS_PHASER_ROTATION  No
-001    SYSTEM_INTERFACE_BOARD_FAIL     No
-001    PARALLEL_BOARD_FAIL     No
-001    LOST_LOAD_SHARING_PHASE_A       No
-001    LOST_LOAD_SHARING_PHASE_B       No
-001    LOST_LOAD_SHARING_PHASE_C       No
-001    DC_OVER_VOLTAGE_TIMEOUT No
-001    BATTERY_TOTALLY_DISCHARGED      No
-001    INVERTER_PHASE_BIAS_ERROR       No
-001    INVERTER_VOLTAGE_BIAS_ERROR_2   No
-001    DC_LINK_BLEED_COMPLETE  No
-001    LARGE_CHARGER_INPUT_CURRENT     No
-001    INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No
-001    LOSS_OF_REDUNDANCY      No
-001    LOSS_OF_SYNC_BUS        No
-001    RECTIFIER_BREAKER_SHUNT_TRIP    No
-001    LOSS_OF_CHARGER_SYNC    No
-001    INVERTER_LOW_LEVEL_TEST_TIMEOUT No
-001    OUTPUT_BREAKER_OPEN     No
-001    CONTROL_POWER_ON        No
-001    INVERTER_ON     No
-001    CHARGER_ON      No
-001    BYPASS_ON       No
-001    BYPASS_POWER_LOSS       No
-001    ON_MANUAL_BYPASS        No
-001    BYPASS_MANUAL_TURN_OFF  No
-001    INVERTER_BLEEDING_DC_LINK_VOLT  No
-001    CPU_ISR_ERROR   No
-001    SYSTEM_ISR_RESTART      No
-001    PARALLEL_DC     No
-001    BATTERY_NEEDS_SERVICE   No
-001    BATTERY_CHARGING        No
-001    BATTERY_NOT_CHARGED     No
-001    DISABLED_BATTERY_TIME   No
-001    SERIES_7000_ENABLE      No
-001    OTHER_UPS_ON    No
-001    PARALLEL_INVERTER       No
-001    UPS_IN_PARALLEL No
-001    OUTPUT_BREAKER_REALY_FAIL       No
-001    CONTROL_POWER_OFF       No
-001    LEVEL_2_OVERLOAD_PHASE_A        No
-001    LEVEL_2_OVERLOAD_PHASE_B        No
-001    LEVEL_2_OVERLOAD_PHASE_C        No
-001    LEVEL_3_OVERLOAD_PHASE_A        No
-001    LEVEL_3_OVERLOAD_PHASE_B        No
-001    LEVEL_3_OVERLOAD_PHASE_C        No
-001    LEVEL_4_OVERLOAD_PHASE_A        No
-001    LEVEL_4_OVERLOAD_PHASE_B        No
-001    LEVEL_4_OVERLOAD_PHASE_C        No
0002    UPS_ON_BATTERY  Yes
-001    UPS_ON_BYPASS   No
-001    LOAD_DUMPED     No
-001    LOAD_ON_INVERTER        No
-001    UPS_ON_COMMAND  No
-001    UPS_OFF_COMMAND No
-001    LOW_BATTERY_SHUTDOWN    No
-001    AUTO_ON_ENABLED No


Shutdown delay longer than battery capacity when Low Battery warning is given. 
(max 60 seconds)
dstate_init: sock /var/run/nut/bcmxcp_usb-ups open on fd 5
Signal 2: exiting
CLOSING