Arnaud Quette wrote: > 2009/11/30 raf <[email protected]>: > > hi, > > Hi Raf, > > > i've just set up two new computers each with a Powerware 3105 ups. > > they have identical nut configurations and identical upss which > > are both plugged in via usb but only one is being detected by nut. > > the other keeps saying: > > > > Broadcast Message from n...@server-1 > > (somewhere) at 14:52 ... > > UPS u...@localhost is unavailable > > (...) > > everything seems fine there. > I've recently made several changes and improvements on this driver > (the USB one) and would be interested in a driver debug output, ie: > $ /lib/nut/bcmxcp_usb -DDD -a ups > > according to these info, I'll be able to give you a solution. > > cheers, > Arnaud > -- > Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops > Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/ > Debian Developer - http://www.debian.org > Free Software Developer - http://arnaud.quette.free.fr/
hi arnaud, i've attached the output from both hosts. strangely, the output for the one that works is almost identical to the one that doesn't. cheers, raf
Network UPS Tools - BCMXCP UPS driver 0.14 (2.2.2) Warning: This is an experimental driver. Some features may not function correctly. Model = POWERWARE UPS 700VA Firmware = Cont:00.80 Inve:00.60
debug level is '3' Shutdown delay = 120 seconds Index Offset Format NUT Length of alarm map: 22 Index Alarm Supported -001 INVERTER_AC_OVER_VOLTAGE No -001 INVERTER_AC_UNDER_VOLTAGE No -001 INVERTER_OVER_OR_UNDER_FREQ No -001 BYPASS_AC_OVER_VOLTAGE No -001 BYPASS_AC_UNDER_VOLTAGE No -001 BYPASS_OVER_OR_UNDER_FREQ No -001 INPUT_AC_OVER_VOLTAGE No -001 INPUT_AC_UNDER_VOLTAGE No -001 INPUT_UNDER_OR_OVER_FREQ No -001 OUTPUT_OVER_VOLTAGE No -001 OUTPUT_UNDER_VOLTAGE No -001 OUTPUT_UNDER_OR_OVER_FREQ No -001 REMOTE_EMERGENCY_PWR_OFF No -001 REMOTE_GO_TO_BYPASS No -001 BUILDING_ALARM_6 No -001 BUILDING_ALARM_5 No -001 BUILDING_ALARM_4 No -001 BUILDING_ALARM_3 No -001 BUILDING_ALARM_2 No -001 BUILDING_ALARM_1 No -001 STATIC_SWITCH_OVER_TEMP No -001 CHARGER_OVER_TEMP No -001 CHARGER_LOGIC_PWR_FAIL No -001 CHARGER_OVER_VOLTAGE_OR_CURRENT No -001 INVERTER_OVER_TEMP No -001 OUTPUT_OVERLOAD No -001 RECTIFIER_INPUT_OVER_CURRENT No -001 INVERTER_OUTPUT_OVER_CURRENT No -001 DC_LINK_OVER_VOLTAGE No -001 DC_LINK_UNDER_VOLTAGE No -001 RECTIFIER_FAILED No -001 INVERTER_FAULT No -001 BATTERY_CONNECTOR_FAIL No -001 BYPASS_BREAKER_FAIL No -001 CHARGER_FAIL No -001 RAMP_UP_FAILED No -001 STATIC_SWITCH_FAILED No -001 ANALOG_AD_REF_FAIL No -001 BYPASS_UNCALIBRATED No -001 RECTIFIER_UNCALIBRATED No -001 OUTPUT_UNCALIBRATED No -001 INVERTER_UNCALIBRATED No -001 DC_VOLT_UNCALIBRATED No -001 OUTPUT_CURRENT_UNCALIBRATED No -001 RECTIFIER_CURRENT_UNCALIBRATED No -001 BATTERY_CURRENT_UNCALIBRATED No -001 INVERTER_ON_OFF_STAT_FAIL No -001 BATTERY_CURRENT_LIMIT No -001 INVERTER_STARTUP_FAIL No -001 ANALOG_BOARD_AD_STAT_FAIL No -001 OUTPUT_CURRENT_OVER_100 No -001 BATTERY_GROUND_FAULT No -001 WAITING_FOR_CHARGER_SYNC No -001 NV_RAM_FAIL No -001 ANALOG_BOARD_AD_TIMEOUT No -001 SHUTDOWN_IMMINENT No 0000 BATTERY_LOW Yes 0001 UTILITY_FAIL Yes -001 OUTPUT_SHORT_CIRCUIT No -001 UTILITY_NOT_PRESENT No -001 FULL_TIME_CHARGING No -001 FAST_BYPASS_COMMAND No -001 AD_ERROR No -001 INTERNAL_COM_FAIL No -001 RECTIFIER_SELFTEST_FAIL No -001 RECTIFIER_EEPROM_FAIL No -001 RECTIFIER_EPROM_FAIL No -001 INPUT_LINE_VOLTAGE_LOSS No -001 BATTERY_DC_OVER_VOLTAGE No -001 POWER_SUPPLY_OVER_TEMP No -001 POWER_SUPPLY_FAIL No -001 POWER_SUPPLY_5V_FAIL No -001 POWER_SUPPLY_12V_FAIL No -001 HEATSINK_OVER_TEMP No -001 HEATSINK_TEMP_SENSOR_FAIL No -001 RECTIFIER_CURRENT_OVER_125 No -001 RECTIFIER_FAULT_INTERRUPT_FAIL No -001 RECTIFIER_POWER_CAPASITOR_FAIL No -001 INVERTER_PROGRAM_STACK_ERROR No -001 INVERTER_BOARD_SELFTEST_FAIL No -001 INVERTER_AD_SELFTEST_FAIL No -001 INVERTER_RAM_SELFTEST_FAIL No -001 NV_MEMORY_CHECKSUM_FAIL No -001 PROGRAM_CHECKSUM_FAIL No -001 INVERTER_CPU_SELFTEST_FAIL No -001 NETWORK_NOT_RESPONDING No -001 FRONT_PANEL_SELFTEST_FAIL No -001 NODE_EEPROM_VERIFICATION_ERROR No -001 OUTPUT_AC_OVER_VOLT_TEST_FAIL No -001 OUTPUT_DC_OVER_VOLTAGE No -001 INPUT_PHASE_ROTATION_ERROR No -001 INVERTER_RAMP_UP_TEST_FAILED No -001 INVERTER_OFF_COMMAND No -001 INVERTER_ON_COMMAND No -001 TO_BYPASS_COMMAND No -001 FROM_BYPASS_COMMAND No -001 AUTO_MODE_COMMAND No -001 EMERGENCY_SHUTDOWN_COMMAND No -001 SETUP_SWITCH_OPEN No -001 INVERTER_OVER_VOLT_INT No -001 INVERTER_UNDER_VOLT_INT No -001 ABSOLUTE_DCOV_ACOV No -001 PHASE_A_CURRENT_LIMIT No -001 PHASE_B_CURRENT_LIMIT No -001 PHASE_C_CURRENT_LIMIT No -001 BYPASS_NOT_AVAILABLE No -001 RECTIFIER_BREAKER_OPEN No -001 BATTERY_CONTACTOR_OPEN No -001 INVERTER_CONTACTOR_OPEN No -001 BYPASS_BREAKER_OPEN No -001 INV_BOARD_ACOV_INT_TEST_FAIL No -001 INVERTER_OVER_TEMP_TRIP No -001 INV_BOARD_ACUV_INT_TEST_FAIL No -001 INVERTER_VOLTAGE_FEEDBACK_ERROR No -001 DC_UNDER_VOLTAGE_TIMEOUT No -001 AC_UNDER_VOLTAGE_TIMEOUT No -001 DC_UNDER_VOLTAGE_WHILE_CHARGE No -001 INVERTER_VOLTAGE_BIAS_ERROR No -001 RECTIFIER_PHASE_ROTATION No -001 BYPASS_PHASER_ROTATION No -001 SYSTEM_INTERFACE_BOARD_FAIL No -001 PARALLEL_BOARD_FAIL No -001 LOST_LOAD_SHARING_PHASE_A No -001 LOST_LOAD_SHARING_PHASE_B No -001 LOST_LOAD_SHARING_PHASE_C No -001 DC_OVER_VOLTAGE_TIMEOUT No -001 BATTERY_TOTALLY_DISCHARGED No -001 INVERTER_PHASE_BIAS_ERROR No -001 INVERTER_VOLTAGE_BIAS_ERROR_2 No -001 DC_LINK_BLEED_COMPLETE No -001 LARGE_CHARGER_INPUT_CURRENT No -001 INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No -001 LOSS_OF_REDUNDANCY No -001 LOSS_OF_SYNC_BUS No -001 RECTIFIER_BREAKER_SHUNT_TRIP No -001 LOSS_OF_CHARGER_SYNC No -001 INVERTER_LOW_LEVEL_TEST_TIMEOUT No -001 OUTPUT_BREAKER_OPEN No -001 CONTROL_POWER_ON No -001 INVERTER_ON No -001 CHARGER_ON No -001 BYPASS_ON No -001 BYPASS_POWER_LOSS No -001 ON_MANUAL_BYPASS No -001 BYPASS_MANUAL_TURN_OFF No -001 INVERTER_BLEEDING_DC_LINK_VOLT No -001 CPU_ISR_ERROR No -001 SYSTEM_ISR_RESTART No -001 PARALLEL_DC No -001 BATTERY_NEEDS_SERVICE No -001 BATTERY_CHARGING No -001 BATTERY_NOT_CHARGED No -001 DISABLED_BATTERY_TIME No -001 SERIES_7000_ENABLE No -001 OTHER_UPS_ON No -001 PARALLEL_INVERTER No -001 UPS_IN_PARALLEL No -001 OUTPUT_BREAKER_REALY_FAIL No -001 CONTROL_POWER_OFF No -001 LEVEL_2_OVERLOAD_PHASE_A No -001 LEVEL_2_OVERLOAD_PHASE_B No -001 LEVEL_2_OVERLOAD_PHASE_C No -001 LEVEL_3_OVERLOAD_PHASE_A No -001 LEVEL_3_OVERLOAD_PHASE_B No -001 LEVEL_3_OVERLOAD_PHASE_C No -001 LEVEL_4_OVERLOAD_PHASE_A No -001 LEVEL_4_OVERLOAD_PHASE_B No -001 LEVEL_4_OVERLOAD_PHASE_C No 0002 UPS_ON_BATTERY Yes -001 UPS_ON_BYPASS No -001 LOAD_DUMPED No -001 LOAD_ON_INVERTER No -001 UPS_ON_COMMAND No -001 UPS_OFF_COMMAND No -001 LOW_BATTERY_SHUTDOWN No -001 AUTO_ON_ENABLED No Shutdown delay longer than battery capacity when Low Battery warning is given. (max 60 seconds) dstate_init: sock /var/run/nut/bcmxcp_usb-ups open on fd 5 new connection on fd 6 Signal 2: exiting CLOSING
Network UPS Tools - BCMXCP UPS driver 0.14 (2.2.2) Warning: This is an experimental driver. Some features may not function correctly. Model = POWERWARE UPS 700VA Firmware = Cont:00.80 Inve:00.60
debug level is '3' Shutdown delay = 120 seconds Index Offset Format NUT Length of alarm map: 22 Index Alarm Supported -001 INVERTER_AC_OVER_VOLTAGE No -001 INVERTER_AC_UNDER_VOLTAGE No -001 INVERTER_OVER_OR_UNDER_FREQ No -001 BYPASS_AC_OVER_VOLTAGE No -001 BYPASS_AC_UNDER_VOLTAGE No -001 BYPASS_OVER_OR_UNDER_FREQ No -001 INPUT_AC_OVER_VOLTAGE No -001 INPUT_AC_UNDER_VOLTAGE No -001 INPUT_UNDER_OR_OVER_FREQ No -001 OUTPUT_OVER_VOLTAGE No -001 OUTPUT_UNDER_VOLTAGE No -001 OUTPUT_UNDER_OR_OVER_FREQ No -001 REMOTE_EMERGENCY_PWR_OFF No -001 REMOTE_GO_TO_BYPASS No -001 BUILDING_ALARM_6 No -001 BUILDING_ALARM_5 No -001 BUILDING_ALARM_4 No -001 BUILDING_ALARM_3 No -001 BUILDING_ALARM_2 No -001 BUILDING_ALARM_1 No -001 STATIC_SWITCH_OVER_TEMP No -001 CHARGER_OVER_TEMP No -001 CHARGER_LOGIC_PWR_FAIL No -001 CHARGER_OVER_VOLTAGE_OR_CURRENT No -001 INVERTER_OVER_TEMP No -001 OUTPUT_OVERLOAD No -001 RECTIFIER_INPUT_OVER_CURRENT No -001 INVERTER_OUTPUT_OVER_CURRENT No -001 DC_LINK_OVER_VOLTAGE No -001 DC_LINK_UNDER_VOLTAGE No -001 RECTIFIER_FAILED No -001 INVERTER_FAULT No -001 BATTERY_CONNECTOR_FAIL No -001 BYPASS_BREAKER_FAIL No -001 CHARGER_FAIL No -001 RAMP_UP_FAILED No -001 STATIC_SWITCH_FAILED No -001 ANALOG_AD_REF_FAIL No -001 BYPASS_UNCALIBRATED No -001 RECTIFIER_UNCALIBRATED No -001 OUTPUT_UNCALIBRATED No -001 INVERTER_UNCALIBRATED No -001 DC_VOLT_UNCALIBRATED No -001 OUTPUT_CURRENT_UNCALIBRATED No -001 RECTIFIER_CURRENT_UNCALIBRATED No -001 BATTERY_CURRENT_UNCALIBRATED No -001 INVERTER_ON_OFF_STAT_FAIL No -001 BATTERY_CURRENT_LIMIT No -001 INVERTER_STARTUP_FAIL No -001 ANALOG_BOARD_AD_STAT_FAIL No -001 OUTPUT_CURRENT_OVER_100 No -001 BATTERY_GROUND_FAULT No -001 WAITING_FOR_CHARGER_SYNC No -001 NV_RAM_FAIL No -001 ANALOG_BOARD_AD_TIMEOUT No -001 SHUTDOWN_IMMINENT No 0000 BATTERY_LOW Yes 0001 UTILITY_FAIL Yes -001 OUTPUT_SHORT_CIRCUIT No -001 UTILITY_NOT_PRESENT No -001 FULL_TIME_CHARGING No -001 FAST_BYPASS_COMMAND No -001 AD_ERROR No -001 INTERNAL_COM_FAIL No -001 RECTIFIER_SELFTEST_FAIL No -001 RECTIFIER_EEPROM_FAIL No -001 RECTIFIER_EPROM_FAIL No -001 INPUT_LINE_VOLTAGE_LOSS No -001 BATTERY_DC_OVER_VOLTAGE No -001 POWER_SUPPLY_OVER_TEMP No -001 POWER_SUPPLY_FAIL No -001 POWER_SUPPLY_5V_FAIL No -001 POWER_SUPPLY_12V_FAIL No -001 HEATSINK_OVER_TEMP No -001 HEATSINK_TEMP_SENSOR_FAIL No -001 RECTIFIER_CURRENT_OVER_125 No -001 RECTIFIER_FAULT_INTERRUPT_FAIL No -001 RECTIFIER_POWER_CAPASITOR_FAIL No -001 INVERTER_PROGRAM_STACK_ERROR No -001 INVERTER_BOARD_SELFTEST_FAIL No -001 INVERTER_AD_SELFTEST_FAIL No -001 INVERTER_RAM_SELFTEST_FAIL No -001 NV_MEMORY_CHECKSUM_FAIL No -001 PROGRAM_CHECKSUM_FAIL No -001 INVERTER_CPU_SELFTEST_FAIL No -001 NETWORK_NOT_RESPONDING No -001 FRONT_PANEL_SELFTEST_FAIL No -001 NODE_EEPROM_VERIFICATION_ERROR No -001 OUTPUT_AC_OVER_VOLT_TEST_FAIL No -001 OUTPUT_DC_OVER_VOLTAGE No -001 INPUT_PHASE_ROTATION_ERROR No -001 INVERTER_RAMP_UP_TEST_FAILED No -001 INVERTER_OFF_COMMAND No -001 INVERTER_ON_COMMAND No -001 TO_BYPASS_COMMAND No -001 FROM_BYPASS_COMMAND No -001 AUTO_MODE_COMMAND No -001 EMERGENCY_SHUTDOWN_COMMAND No -001 SETUP_SWITCH_OPEN No -001 INVERTER_OVER_VOLT_INT No -001 INVERTER_UNDER_VOLT_INT No -001 ABSOLUTE_DCOV_ACOV No -001 PHASE_A_CURRENT_LIMIT No -001 PHASE_B_CURRENT_LIMIT No -001 PHASE_C_CURRENT_LIMIT No -001 BYPASS_NOT_AVAILABLE No -001 RECTIFIER_BREAKER_OPEN No -001 BATTERY_CONTACTOR_OPEN No -001 INVERTER_CONTACTOR_OPEN No -001 BYPASS_BREAKER_OPEN No -001 INV_BOARD_ACOV_INT_TEST_FAIL No -001 INVERTER_OVER_TEMP_TRIP No -001 INV_BOARD_ACUV_INT_TEST_FAIL No -001 INVERTER_VOLTAGE_FEEDBACK_ERROR No -001 DC_UNDER_VOLTAGE_TIMEOUT No -001 AC_UNDER_VOLTAGE_TIMEOUT No -001 DC_UNDER_VOLTAGE_WHILE_CHARGE No -001 INVERTER_VOLTAGE_BIAS_ERROR No -001 RECTIFIER_PHASE_ROTATION No -001 BYPASS_PHASER_ROTATION No -001 SYSTEM_INTERFACE_BOARD_FAIL No -001 PARALLEL_BOARD_FAIL No -001 LOST_LOAD_SHARING_PHASE_A No -001 LOST_LOAD_SHARING_PHASE_B No -001 LOST_LOAD_SHARING_PHASE_C No -001 DC_OVER_VOLTAGE_TIMEOUT No -001 BATTERY_TOTALLY_DISCHARGED No -001 INVERTER_PHASE_BIAS_ERROR No -001 INVERTER_VOLTAGE_BIAS_ERROR_2 No -001 DC_LINK_BLEED_COMPLETE No -001 LARGE_CHARGER_INPUT_CURRENT No -001 INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No -001 LOSS_OF_REDUNDANCY No -001 LOSS_OF_SYNC_BUS No -001 RECTIFIER_BREAKER_SHUNT_TRIP No -001 LOSS_OF_CHARGER_SYNC No -001 INVERTER_LOW_LEVEL_TEST_TIMEOUT No -001 OUTPUT_BREAKER_OPEN No -001 CONTROL_POWER_ON No -001 INVERTER_ON No -001 CHARGER_ON No -001 BYPASS_ON No -001 BYPASS_POWER_LOSS No -001 ON_MANUAL_BYPASS No -001 BYPASS_MANUAL_TURN_OFF No -001 INVERTER_BLEEDING_DC_LINK_VOLT No -001 CPU_ISR_ERROR No -001 SYSTEM_ISR_RESTART No -001 PARALLEL_DC No -001 BATTERY_NEEDS_SERVICE No -001 BATTERY_CHARGING No -001 BATTERY_NOT_CHARGED No -001 DISABLED_BATTERY_TIME No -001 SERIES_7000_ENABLE No -001 OTHER_UPS_ON No -001 PARALLEL_INVERTER No -001 UPS_IN_PARALLEL No -001 OUTPUT_BREAKER_REALY_FAIL No -001 CONTROL_POWER_OFF No -001 LEVEL_2_OVERLOAD_PHASE_A No -001 LEVEL_2_OVERLOAD_PHASE_B No -001 LEVEL_2_OVERLOAD_PHASE_C No -001 LEVEL_3_OVERLOAD_PHASE_A No -001 LEVEL_3_OVERLOAD_PHASE_B No -001 LEVEL_3_OVERLOAD_PHASE_C No -001 LEVEL_4_OVERLOAD_PHASE_A No -001 LEVEL_4_OVERLOAD_PHASE_B No -001 LEVEL_4_OVERLOAD_PHASE_C No 0002 UPS_ON_BATTERY Yes -001 UPS_ON_BYPASS No -001 LOAD_DUMPED No -001 LOAD_ON_INVERTER No -001 UPS_ON_COMMAND No -001 UPS_OFF_COMMAND No -001 LOW_BATTERY_SHUTDOWN No -001 AUTO_ON_ENABLED No Shutdown delay longer than battery capacity when Low Battery warning is given. (max 60 seconds) dstate_init: sock /var/run/nut/bcmxcp_usb-ups open on fd 5 Signal 2: exiting CLOSING