Hi!
Using this guide:
http://blog.shadypixel.com/monitoring-a-ups-with-nut-on-debian-or-ubuntu-linux/
and systematically testing the usb capable driver on your site I managed
to get my FSP EP650 (by http://www.fspgroupusa.com/ ) working (after
reboot). Im running Ubuntu 9.10 desktop x64 standard install.
This is the output from running "upsc ups1"
-----
battery.voltage: 13.50
battery.voltage.nominal: 12.0
beeper.status: enabled
driver.name: blazer_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.1
driver.version.internal: 0.03
input.current.nominal: 2.0
input.frequency: 50.1
input.frequency.nominal: 50
input.voltage: 235.1
input.voltage.fault: 235.1
input.voltage.nominal: 220
output.voltage: 235.1
ups.delay.shutdown: 30
ups.delay.start: 180
ups.load: 14
ups.productid: 5161
ups.status: OL
ups.type: offline / line interactive
ups.vendorid: 0665
-----
Question: Should there not be more entries, for example battery time or
similar?
Anyway, if the above looks right, you can add the FSP brand EP 650 to
your list of supported UPSes.
regards,
Jim
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser