Citeren Arnaud Quette <[email protected]>:
the only thing I can see (apart from changing for a more feature full unit) is to lower the trigger level from 30 % to 20 % so that these tests do no result in a shutdown. If the software is still NUT, you can simply change the low battery level using "lowbatt=value" in ups.conf
Note that the above only works if you're using the 'mge-shut' or 'mge-utalk' drivers. If you're using the 'newmge-shut' or 'usbhid-ups' driver, you might try if the UPS allows setting this value by using 'upsrw' to change the value of 'battery.charge.low'.
Having said that, a UPS that triggers a low-battery warning during a weekly test is suspect of having a faulty battery. A weekly test runs the UPS on battery for only a handful seconds (typically 5-10 seconds). If it can't keep up that long without triggering a low-battery warning, it most certainly won't have enough capacity left for a clean shutdown of the attached systems if the power really fails. So either the battery is worn out or the load on the UPS is too high.
Best regards, Arjen -- Please keep list traffic on the list (off-list replies will be rejected) _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

