Quoting Arnaud Quette <[email protected]>:
battery.charge: 71
What does the above read after 24 hours charging? Is it still below 100%?
No, as seen below - now it correctly shows 100%
@Niels: can you please post an upsc output again.
Sure, here goes:
Linux grisen 2.6.32-25-generic-pae #44-Ubuntu SMP Fri Sep 17 21:57:48
UTC 2010 i686 GNU/Linux
Ubuntu 10.04.1 LTS
(cut)
n...@grisen:~$ sudo upsc [email protected]
[sudo] password for nkj:
battery.capacity: 9.00
battery.charge: 100
battery.charge.low: 20
battery.charge.restart: 0
battery.energysave: no
battery.protection: yes
battery.runtime: 775
battery.type: PbAc
device.mfr: EATON
device.model: 5130 RT 3000
device.serial: NC302C5031
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: MGE HID 1.18
driver.version.internal: 0.34
input.frequency: 50.0
input.frequency.extended: no
input.frequency.nominal: 50
input.sensitivity: normal
input.transfer.boost.low: 184
input.transfer.high: 294
input.transfer.low: 160
input.transfer.trim.high: 265
input.voltage: 229.0
input.voltage.extended: no
input.voltage.nominal: 230
outlet.1.autoswitch.charge.low: 0
outlet.1.delay.shutdown: 65535
outlet.1.delay.start: 3
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 1
outlet.1.status: on
outlet.1.switchable: yes
outlet.2.autoswitch.charge.low: 0
outlet.2.delay.shutdown: 65535
outlet.2.delay.start: 6
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 2
outlet.2.status: on
outlet.2.switchable: yes
outlet.desc: Main Outlet
outlet.id: 0
outlet.switchable: no
output.current: 4.30
output.frequency: 50.0
output.frequency.nominal: 50
output.powerfactor: 0.00
output.voltage: 3946.0
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 6006AC
ups.load: 34
ups.load.high: 105
ups.mfr: EATON
ups.model: 5130 RT 3000
ups.power: 995
ups.power.nominal: 3000
ups.productid: ffff
ups.realpower: 918
ups.realpower.nominal: 2700
ups.serial: NC302C5031
ups.start.auto: yes
ups.start.battery: yes
ups.start.reboot: yes
ups.status: OL CHRG
ups.test.interval: 604800
ups.test.result: Done and passed
ups.timer.shutdown: -1
ups.timer.start: -1
ups.type: offline / line interactive
ups.vendorid: 0463
n...@grisen:~$
@Niels: can you post the first 20 seconds worth of output from
/path/to/usbhid-ups -DDD -a PingvinUPS
I run into some resource allocation problems, I think. Stopping the
NUT service does not help.
Can I provide the info in some other way? Running as single user is
not an option for the next few weeks.
Best regards,
Niels Kristian
Denmark
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser