I've a Belkin Regulator Pro (F6C1400-EUR) connected via serial to a FreeBSD machine using NUT v.2.4.3

Sometimes I get a series of logged messages saying that the data is switching between stale and valid, this in itself isn't an issue, however occasionally when the communication is re-established, upsmon gets a "On battery" message followed quickly by "Battery low" message, and calls on the system to halt. I know for a fact that the battery isn't low at any stage, as other UPSs have not reported a loss of power. This behaviour has only started occurring since using NUT rather than Belkin Bulldog (not supported on FreeBSD x64).

Dec  1 08:02:46 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:02:47 rack upsmon[957]: Communications with UPS belkin...@localhost established Dec 1 08:02:48 rack upsd[941]: Data for UPS [belkinreg] is stale - check driver Dec 1 08:02:52 rack upsmon[957]: Poll UPS [belkin...@localhost] failed - Data stale Dec 1 08:02:52 rack upsmon[957]: Communications with UPS belkin...@localhost lost Dec 1 08:02:57 rack upsmon[957]: Poll UPS [belkin...@localhost] failed - Data stale
Dec  1 08:02:59 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:03:00 rack upsd[941]: Data for UPS [belkinreg] is stale - check driver Dec 1 08:03:02 rack upsmon[957]: Poll UPS [belkin...@localhost] failed - Data stale
Dec  1 08:03:27 rack last message repeated 5 times
Dec  1 08:03:32 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:03:32 rack upsmon[957]: Communications with UPS belkin...@localhost established Dec 1 08:03:34 rack upsd[941]: Data for UPS [belkinreg] is stale - check driver Dec 1 08:03:37 rack upsmon[957]: Poll UPS [belkin...@localhost] failed - Data stale Dec 1 08:03:37 rack upsmon[957]: Communications with UPS belkin...@localhost lost Dec 1 08:03:42 rack upsmon[957]: Poll UPS [belkin...@localhost] failed - Data stale
...
Dec 1 08:03:52 rack upsmon[957]: Poll UPS [belkin...@localhost] failed - Data stale Dec 1 08:03:52 rack upsmon[957]: Communications with UPS belkin...@localhost lost
Dec  1 08:03:57 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:03:57 rack upsmon[957]: Communications with UPS belkin...@localhost established
Dec  1 08:03:57 rack upsmon[957]: UPS belkin...@localhost on battery
Dec  1 08:03:57 rack upsmon[957]: UPS belkin...@localhost battery is low
Dec  1 08:03:57 rack upsmon[957]: Executing automatic power-fail shutdown
Dec  1 08:03:57 rack upsmon[957]: Auto logout and shutdown proceeding

I can see no reason why the NUT is seeing a battery low message. Unfortunately there is only a 5 minute resolution for the ups log:

20101201 072111 100 238.7 022 [OL] 012 50.1
20101201 072611 NA NA NA [NA] NA NA
20101201 073111 NA NA NA [NA] NA NA
20101201 073611 000 000.0 2400 [OL] 000 0.0
20101201 074111 NA NA NA [NA] NA NA
20101201 074611 NA NA NA [NA] NA NA
20101201 075111 NA NA NA [NA] NA NA
20101201 075611 NA NA NA [NA] NA NA
20101201 080111 NA NA NA [NA] NA NA
20101201 090322 NA NA NA [WAIT] NA NA
20101201 090822 100 234.5 024 [OL] 017 49.9
20101201 091348 NA NA NA [WAIT] NA NA
20101201 091848 100 236.7 022 [OL] 017 50.0
20101201 092348 100 235.7 022 [OL] 017 49.9

Has anyone got any suggestions?