On 4/24/12 11:30 AM, Arnaud Quette wrote: > 2012/4/24 ramazan firin <[email protected]> > >> i see that in user-manuel.pdf >> >> "Similarly, if your UPS connects to your computer via an SNMP network >> card, you can probably add support for your device by >> writing a new subdriver to the existing snmp-ups driver." >> >> in this page, http://packages.debian.org/squeeze/nut-snmp >> "This package provides snmp-ups, the SNMP multi-MIB driver for UPS, which >> supports various MIBs including IETF, MGE, and APC. It adds an SNMP Manager >> interface to the core NUT system" >> >> i dont understand clearly, >> >> nut support snmp via network card ? > > we are there talking about NUT that interface with a device (UPS, PDU, > whatever...), as it does with serial and USB devices, to get data, do > settings and issue commands. > > but SNMP has 2 sides, which may be what is puzzling you: > - the agent: which is the UPS card, serving SNMP data, > - the manager, which is the NUT driver (snmp-ups), that consumes data from > the agent. > the snmp-ups driver is a generic driver that supports various MIBs and > types of devices. > > I also once worked on an SNMP agent that provided NUT data through SNMP > (RFC 1628): > https://alioth.debian.org/tracker/index.php?func=detail&aid=312563&group_id=30602&atid=411544 > > For more info on SNMP, see for example: > http://en.wikipedia.org/wiki/Simple_Network_Management_Protocol
It may help if I describe my setup, since in my cluster we only use SNMP
management cards.
All of our UPSes come from APC. If an APC UPS is a Smart-UPS model or better, it
comes with a slot for an SNMP management card. For example, an APC SMART-UPS
3000 uses a model AP9630 management card.
When I configure the management card, I assign it a static IP address; e.g., for
a server named "notredame.nevis.columbia.edu", I create an IP address with the
IP name "notredame-ups.nevis.columbia.edu" (I control the DNS service for my
site).
On notredame, in ups.conf, I include the following:
[notredam-ups]
driver = snmp-ups
port = notredame-ups.nevis.columbia.edu
community = public
mibs=apcc
In upsd.users:
[monuser]
password = XXXX
upsmon master
In upsmon.conf:
MONITOR notredame-ups@localhost 1 monuser XXXX master
This works just fine.
What makes this facility especially nice is that I have servers that depend on
other servers. Suppose I have a server eiffel.nevis.columbia.edu that requires
notredame to be up; if notredame goes down due to its UPS going critical, then I
want eiffel to go down even if its own UPS still has some battery life. Then I
can include the same above statements for notredame in eiffel's configuration
file, in addition to the definitions for eiffel-ups.nevis.columbia.edu.
The lines in upsmon.conf look like this:
MONITOR eiffel-ups@localhost 1 monuser XXXX master
MONITOR notredame-ups@localhost 1 monuser XXXX master
MINSUPPLIES 2
Here's why I need that last line:
<http://www.mail-archive.com/[email protected]/msg06831.html>
The result is that eiffel will shut down if either eiffel-ups or notredame-ups
goes critical.
--
Bill Seligman | Phone: (914) 591-2823