I'm trying to use a Nas4Free storage system. This same hardware worked
fine on Freenas 0.7.2.
O/S: Nas4Free 9.0.0.1.148 which comes with nut 2.6.4.
UPS is an APC Back UPS RS 800. USB interface.
Driver : usbhid-ups
Port: auto
my NAS is communicating with the UPS, but in testing power failures, I'm
not getting the shutdown to be handled properly.
When I pull the AC plug on the UPS, the NAS recognizes that event, but
doesn't send out the email and doesn't start the shutdown sequence even
though the 30 sec time limit has passed. The log shows errors. I've
posted them below. The restoring of power is also recognized by the NAS.
Jul 14 06:14:41 nas4free upsmon[1813]: UPS Back-UPS-RS-800@localhost on
battery
Jul 14 06:14:42 nas4free upssched[2334]: read confirmation got [ERR
UNKNOWN own" "30"]
Jul 14 06:14:43 nas4free last message repeated 24 times
Jul 14 06:14:43 nas4free upssched[2334]: Unable to connect to daemon and
unable to start daemon
Jul 14 06:17:01 nas4free upsmon[1813]: UPS Back-UPS-RS-800@localhost on
line power
Jul 14 06:17:01 nas4free upssched-cmd: UPS Back-UPS-RS-800@localhost -
Running on line power. Shutdown cancelled.
Jul 14 06:17:03 nas4free msmtp: host=smtp.gmail.com tls=on auth=on
[email protected] <mailto:[email protected]> [email protected]
<mailto:[email protected]> [email protected]
<mailto:[email protected]> mailsize=244 smtpstatus=250
smtpmsg='250 2.0.0 OK 1342261023 y66sm18956640yhi.10' exitcode=EX_OK
more information in the daemon log file:
Jul 14 08:35:17 nas4free upsmon[6990]: UPS ups@localhost on battery
Jul 14 08:35:17 nas4free upssched[7010]: Timer daemon started
Jul 14 08:35:17 nas4free upssched[7010]: Unknown command on socket:
Jul 14 08:35:17 nas4free upssched[7010]: arg 0: 30START
Jul 14 08:35:17 nas4free upssched[7010]: arg 1: shutdown
Jul 14 08:35:17 nas4free upssched[7010]: arg 2: 30
Jul 14 08:35:17 nas4free upssched[7009]: read confirmation got [ERR
UNKNOWN own" "30"]
Jim A
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser