2012/11/26 Franck <fra...@secretfatty.net>

> On 2012-11-26 19:34, Arnaud Quette wrote:
>
>> 2012/11/26 Franck <fra...@secretfatty.net [4]>
>>
>>  On 2012-11-26 18:39, Arnaud Quette wrote:
>>>
>>>  Hi Franck
>>>>
>>>> 2012/11/23 Franck <fra...@secretfatty.net [3] [3]>
>>>>
>>>>  Subject: [Nut-upsuser] CyberPower DX600E wont switch up after
>>>>>>
>>>>>> power
>>>>>>         is back
>>>>>> Message-ID: 
>>>>>> <3c530815d1ea602efdfec0d67eb1e**0...@secretfatty.net<3c530815d1ea602efdfec0d67eb1e...@secretfatty.net>
>>>>>> [1]
>>>>>> [1]>
>>>>>>
>>>>>> Content-Type: text/plain; charset=UTF-8; format=flowed
>>>>>>
>>>>>> Hello
>>>>>> I have an issue with an CyberPower DX600E,
>>>>>> it doesnt switch up when the power is back; after it has been
>>>>>>
>>>>>> unloaded;
>>>>>> is it because of one of those variables ?
>>>>>> regards
>>>>>> Franck
>>>>>>
>>>>>> #upsc myups
>>>>>> battery.charge: 100
>>>>>> battery.charge.low: 10
>>>>>> battery.charge.warning: 20
>>>>>> battery.mfr.date: CPS
>>>>>> battery.runtime: 1380
>>>>>> battery.runtime.low: 300
>>>>>> battery.type: PbAcid
>>>>>> battery.voltage: 4.7
>>>>>> battery.voltage.nominal: 12
>>>>>> device.mfr: CPS
>>>>>> device.model: DX600E
>>>>>> device.type: ups
>>>>>> driver.name [2] [2]: usbhid-ups
>>>>>>
>>>>>>
>>>>>> driver.parameter.pollfreq: 30
>>>>>> driver.parameter.pollinterval: 2
>>>>>> driver.parameter.port: auto
>>>>>> driver.version: 2.4.3
>>>>>> driver.version.data: CyberPower HID 0.3
>>>>>> driver.version.internal: 0.34
>>>>>> input.transfer.high: 0
>>>>>> input.transfer.low: 0
>>>>>> input.voltage: 230.0
>>>>>> input.voltage.nominal: 230
>>>>>> output.voltage: 238.0
>>>>>> ups.beeper.status: enabled
>>>>>> ups.delay.shutdown: 20
>>>>>> ups.delay.start: 30
>>>>>> ups.load: 31
>>>>>> ups.mfr: CPS
>>>>>> ups.model: DX600E
>>>>>> ups.productid: 0501
>>>>>> ups.realpower.nominal: 360
>>>>>> ups.status: OL
>>>>>> ups.timer.shutdown: -60
>>>>>> ups.timer.start: 0
>>>>>> ups.vendorid: 0764
>>>>>>
>>>>>
>>>>> Am i suppose to run a "shutdown.return" command ?
>>>>>
>>>>> Does it make sense to do it in the script triggering (for
>>>>> example
>>>>> when receiving "low battery" ?
>>>>>
>>>>
>>>> depending on your exact OS / distros, this should be handled by
>>>> NUT
>>>> initscripts and probably the halt one.
>>>>  what is yours?
>>>>
>>>
>>> Thanks for your reply Arnaud;
>>> I have a debian squeeze.
>>>
>>
>> looking again at your upsc output, I suspect more an issue with the
>> UPS than with Squeeze.
>>
>> a good test would be to:
>> - remove your PC from the UPS,
>>
>
> Just to check I understood well:
> You mean I would plug the PC directly to the power source, and connect the
> UPS with the PC only using the USB ?


right. we need to monitor the UPS while it's shutting down...


>  - stop NUT after the reboot,
>> - restart the driver in debug more (/lib/nut/usbhid-ups -DDDDD myups)
>> and upsd (simply type "upsd") in another term
>>  - then execute "upscmd -u ... -p ... myups shutdown.return"
>> - leave it half a minute, then Ctrl+C in the driver term.
>> and send back the driver output, in compressed form.
>> you can then restart everything as usual...
>>
>> Id like to see how the data behind "ups.timer.shutdown" and
>> "ups.timer.start" behave.
>>
>>
>
-- Arno
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to