On Dec 7, 2012, at 3:01 AM, Dawning Sky wrote: > 1. battery.charge doesn't report correct charge level when the UPS is > On Batter. It just reports 0. Even though it will report 100 when on > line power.
I wonder if this is connected with the following: > ups.debug.S: 31 34 30 00 64 30 0d '140.d0.' As I remember it, '4' is the status character representing "self-test status is unknown". You might need to do a deep discharge test first before the state-of-charge constants are programmed into the UPS. If you can start a deep discharge test from the front panel, I'd try that first. Otherwise, there is a "test.battery.start" command in NUT which might be what you're looking for. However, bear in mind that this driver was written without the benefit of protocol documentation. -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser