Another update:
Did this manually: snmpset -c private -v 1 10.100.200.30 1.3.6.1.4.1.318.1.1.1.5.2.6.0 i 90
And it worked! But using nut it does not work with the error below.
Update: I can set the battery change date. ;-)
But nothing else...
Hi,
we do have APC Smart-UPS each with AP9617 and latest FW.
As we found out we are not able to shutdown the UPS via SNMP - neither immediately nor delayed. And we cannot set values, but we can read them correctly. So it seems as we are not able to write to the UPS and get back strange errors.
root@abex:/etc/nut# upsdrvctl -DDDD shutdown apc10001
Network UPS Tools - UPS driver controller 2.6.4
0.000000
If you're not a NUT core developer, chances are that you're told to enable debugging [...]
0.000280 Shutdown UPS: apc10001
0.000304 exec: /lib/nut/snmp-ups -a apc10001 -k
Network UPS Tools - Generic SNMP UPS driver 0.66 (2.6.4)
Detected Smart-UPS 1000 on host 10.100.200.30 (mib: apcc 1.1)
Initiating UPS shutdown
[apc10001] nut_snmp_set: can't set .1.3.6.1.4.1.318.1.1.1.6.1.1.0: Error in packet: (genError) A general failure occured
Shutdown failed!
0.099067 Driver failed to start (exit status=1)
If I use upscmd for shutdown it says "OK" but does nothing.
I sent an snmp command directly to the ups (1.3.6.1.4.1.318.1.1.1.6.2.1 i 2) and the ups turned off as expected.
I tried to set values via upsset.cgi in the ups and see the following in the logs even if the cgi says "ok":
May 15 09:54:30 abex upsd[7788]: Set variable: admin@10.100.200.1 set battery.charge.restart on apc10001 to 90
May 15 09:54:30 abex snmp-ups[7785]: [apc10001] nut_snmp_set: can't set .1.3.6.1.4.1.318.1.1.1.5.2.6.0: Error in packet: (badValue) The value given has the wrong type or length.
But I can read that value correctly. We cannot set any values but read them all. community is ok as I can see auth messages in the ups if I use the wrong community. When get those errors above, I do not see any errors in the UPS' logs.
I have no clue what's happening here. I can see this on both UPS which have 1kVA and 1.5kVA and AP9617 (that is the same as AP9618 that is supported with the exception of env montoring).
We are using Debain wheezy (not yet the stable) and nut 2.6.4-1 and snmp-stuff 5.4.3-dfsg-2.5.
Is there someone who can help, please?!
Thanks a lot,
-lutzn
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
we do have APC Smart-UPS each with AP9617 and latest FW.
As we found out we are not able to shutdown the UPS via SNMP - neither immediately nor delayed. And we cannot set values, but we can read them correctly. So it seems as we are not able to write to the UPS and get back strange errors.
root@abex:/etc/nut# upsdrvctl -DDDD shutdown apc10001
Network UPS Tools - UPS driver controller 2.6.4
0.000000
If you're not a NUT core developer, chances are that you're told to enable debugging [...]
0.000280 Shutdown UPS: apc10001
0.000304 exec: /lib/nut/snmp-ups -a apc10001 -k
Network UPS Tools - Generic SNMP UPS driver 0.66 (2.6.4)
Detected Smart-UPS 1000 on host 10.100.200.30 (mib: apcc 1.1)
Initiating UPS shutdown
[apc10001] nut_snmp_set: can't set .1.3.6.1.4.1.318.1.1.1.6.1.1.0: Error in packet: (genError) A general failure occured
Shutdown failed!
0.099067 Driver failed to start (exit status=1)
If I use upscmd for shutdown it says "OK" but does nothing.
I sent an snmp command directly to the ups (1.3.6.1.4.1.318.1.1.1.6.2.1 i 2) and the ups turned off as expected.
I tried to set values via upsset.cgi in the ups and see the following in the logs even if the cgi says "ok":
May 15 09:54:30 abex upsd[7788]: Set variable: admin@10.100.200.1 set battery.charge.restart on apc10001 to 90
May 15 09:54:30 abex snmp-ups[7785]: [apc10001] nut_snmp_set: can't set .1.3.6.1.4.1.318.1.1.1.5.2.6.0: Error in packet: (badValue) The value given has the wrong type or length.
But I can read that value correctly. We cannot set any values but read them all. community is ok as I can see auth messages in the ups if I use the wrong community. When get those errors above, I do not see any errors in the UPS' logs.
I have no clue what's happening here. I can see this on both UPS which have 1kVA and 1.5kVA and AP9617 (that is the same as AP9618 that is supported with the exception of env montoring).
We are using Debain wheezy (not yet the stable) and nut 2.6.4-1 and snmp-stuff 5.4.3-dfsg-2.5.
Is there someone who can help, please?!
Thanks a lot,
-lutzn
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
_______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser