Great, it's working fine.
I'm using upssched to shutdown computer after 15mn when on battery.
Should I trigger "upsmon -c fsd" with my script? I mean, is it the normal
way to shutdown both computer and ups.
Best regards,
-----Message d'origine-----
From: Charles Lepple
Sent: Monday, August 26, 2013 3:07 AM
To: James HORLEY
Cc: nut-upsuser list
Subject: Re: [Nut-upsuser] infosec e4
On Aug 26, 2013, at 6:22 AM, James HORLEY wrote:
I've download again nut source today from
"https://github.com/networkupstools/nut/tree/voltronic-driver" and try
compiliing the voltronic-driver.
This branch has been merged in, and will be part of 2.7.1 when it is
released.
The drivers is working fine (ie computer is shutting down) except for the
shutdown of the ups.
I can shutdown the ups by sending the command "shutdown.return" but
standard shutdown doesn't work.
upsmon -K return:
"upsmon -K" is for use inside a shutdown script. (See the man page for
details.)
I think you want "upsmon -c fsd", which triggers the entire shutdown
sequence.
--
Charles Lepple